ON THIS PAGE
EX9214 Site Guidelines and Requirements
Environmental Requirements and Specifications for EX Series Switches
The switch must be installed in a rack or cabinet housed in a dry, clean, well-ventilated, and temperature-controlled environment.
Ensure that these environmental guidelines are followed:
The site must be as dust-free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the switch cooling system.
Maintain ambient airflow for normal switch operation. If the airflow is blocked or restricted, or if the intake air is too warm, the switch might overheat, leading to the switch temperature monitor shutting down the switch to protect the hardware components.
Table 1 provides the required environmental conditions for normal switch operation.
Switch or device |
Environment Tolerance |
|||
---|---|---|---|---|
Altitude |
Relative Humidity |
Temperature |
Seismic |
|
EX2200-C |
No performance degradation up to 5,000 feet (1524 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 104° F (40° C) at altitudes up to 5,000 ft (1,524 m). For information about extended temperature SFP transceivers supported on EX2200 switches, see Pluggable Transceivers Supported on EX2200 Switches. |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX2200 (except EX2200-C switches) |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX2300-C |
No performance degradation up to 5,000 feet (1524 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 104° F (40° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX2300 (except EX2300-C switches) |
No performance degradation up to 13,000 feet (3962 meters) at 104° F (40° C) as per GR-63 |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX3200 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX3300 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX3400 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4100 |
No performance degradation up to 5,000 feet (1524 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4200 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4300 |
EX4300 switches except the EX4300-48MP model— No performance degradation up to 10,000 feet (3048 meters) EX4300-48MP model— No performance degradation up to 6,000 feet (1829 meters) |
EX4300 switches except the EX4300-48MP model— Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) EX4300-48MP model— Normal operation ensured in the relative humidity range 5% through 90% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4400 |
No performance degradation up to 6,000 feet (1829 meters) |
Normal operation ensured in the relative humidity range 10% through 90% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4500 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 32° F (0° C) through 113° F (45° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4550 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
|
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX4600 |
No performance degradation to 6,562 feet (2000 meters) |
Normal operation ensured in the relative humidity range 5% through 90%, noncondensing
|
|
Complies with Zone 4 earthquake requirements per NEBS GR-63-CORE, Issue 4. |
EX4650 |
No performance degradation to 6,000 feet (1829 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (condensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX6210 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX8208 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX8216 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
EX9204 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 5% through 90% (noncondensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) Nonoperating storage temperature in shipping container: – 40° F (–40° C) to 158° F (70° C) |
Complies with Zone 4 earthquake requirements as per GR-63. |
EX9208 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 5% through 90% (noncondensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) Nonoperating storage temperature in shipping container: – 40° F (–40° C) to 158° F (70° C) |
Complies with Zone 4 earthquake requirements as per GR-63. |
EX9214 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 5% through 90% (noncondensing) |
Normal operation is ensured in the temperature range 32° F (0° C) through 104° F (40° C) Nonoperating storage temperature in shipping container: – 40° F (–40° C) through 158° F (70° C) |
Complies with Zone 4 earthquake requirements as per GR-63. |
EX9251 |
No performance degradation up to 10,000 ft (3048 m) |
Normal operation ensured in relative humidity range of 5% to 90%, noncondensing |
Normal operation ensured in temperature range of 32° F (0° C) to 104° F (40° C) Nonoperating storage temperature in shipping container: – 40° F (–40° C) to 158° F (70° C) |
Complies with Telcordia Technologies Zone 4 earthquake requirements |
XRE200 |
No performance degradation up to 10,000 feet (3048 meters) |
Normal operation ensured in the relative humidity range 10% through 85% (noncondensing) |
Normal operation ensured in the temperature range 41° F (5° C) through 104° F (40° C) |
Complies with Zone 4 earthquake requirements as per GR-63, Issue 4. |
Install EX Series switches only in restricted areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110– 16, 110– 17, and 110– 18 of the National Electrical Code, ANSI/NFPA 70.
General Site Guidelines
Efficient device operation requires proper site planning and maintenance. It also requires proper layout of the equipment, rack or cabinet, and wiring closet.
To plan and create an acceptable operating environment for your device and prevent environmentally caused equipment failures:
Keep the area around the chassis free from dust and conductive material, such as metal flakes.
Follow the prescribed airflow guidelines to ensure that the cooling system functions properly. Ensure that exhaust from other equipment does not blow into the intake vents of the device.
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent damaging the equipment. Static discharge can cause components to fail completely or intermittently over time.
Install the device in a secure area, so that only authorized personnel can access the device.
Site Electrical Wiring Guidelines
Table 2 describes the factors you must consider while planning the electrical wiring at your site.
You must provide a properly grounded and shielded environment and use electrical surge-suppression devices.
Avertissement Vous devez établir un environnement protégé et convenablement mis à la terre et utiliser des dispositifs de parasurtension.
Site Wiring Factor |
Guidelines |
---|---|
Signaling limitations |
If your site experiences any of the following problems, consult experts in electrical surge suppression and shielding:
|
Radio frequency interference |
To reduce or eliminate RFI from your site wiring, do the following:
|
Electromagnetic compatibility |
If your site is susceptible to problems with electromagnetic compatibility (EMC), particularly from lightning or radio transmitters, seek expert advice. Strong sources of electromagnetic interference (EMI) can cause:
|
Clearance Requirements for Airflow and Hardware Maintenance for an EX9214 Switch
When planning the site for installing an EX9214 switch, you must allow sufficient clearance around the switch.
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See Figure 1.
For switches with AC power supplies, allow at least 24 in. (61 cm) of clearance in front of the switch and at least 26.85 in. (68.2 cm) of clearance behind the switch. Allow 2.8 in. (7.1 cm) between the side of the chassis and any non-heat-producing surface such as a wall. See Figure 2.
Figure 2: Clearance Requirements for Airflow and Hardware Maintenance for an EX9214 Switch with AC Power SuppliesFor switches with DC power supplies, allow at least 24 in. (61 cm) of clearance in front of the switch and at least 29.05 in. (73.8 cm) of clearance behind the switch. Allow 2.8 in. (7.1 cm) between the side of the chassis and any non-heat-producing surface such as a wall. See Figure 3.
Figure 3: Clearance Requirements for Airflow and Hardware Maintenance for an EX9214 Switch with DC Power SuppliesIf you are mounting the switch on a rack or cabinet along with other equipment, ensure that the exhaust from other equipment does not blow into the intake vents of the chassis.
Airflow must always be from front to back with respect to the rack. If the device has side to rear airflow, then provisions must be made to ensure that fresh air from the front of the rack is supplied to the inlets, and the exhaust exits at the rear of the rack. The device must not interfere with the cooling of other systems in the rack. Fillers must be used as appropriate in the rack to ensure there is no recirculation of heated exhaust air back to the front of the rack. You must also ensure that hot air does not flow around the cables.
For service personnel to remove and install hardware components, there must be adequate space at the front and back of the switch. At least 24 in. (61 cm) is required both in front of and behind the switch. NEBS GR-63 recommends that you allow at least 30 in. (72.6 cm) in front of the rack and 24 in. (61.0 cm) behind the rack.
Rack Requirements
You can mount the device on two-post racks or four-post racks.
Rack requirements consist of:
Rack type.
Mounting bracket hole spacing.
Rack size and strength.
Rack connection to the building structure.
Table 3 provides the rack requirements and specifications.
Rack Requirement |
Guidelines |
---|---|
Rack type |
A U is the standard rack unit defined by the Electronic Components Industry Association (http://www.ecianow.org). You can mount the device on a rack that provides bracket holes or hole patterns spaced at 1U (1.75 in. or 4.45 cm) increments and meets the size and strength requirements to support the weight. |
Mounting bracket hole spacing |
The holes in the mounting brackets are spaced at 1U (1.75 in. or 4.45 cm) so that the device can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
Ensure that the:
|
Rack connection to building structure |
Secure the rack as follows:
|
See Also
Cabinet Requirements
You can mount the device in a cabinet that contains a 19-in. rack.
Cabinet requirements consist of:
Cabinet size.
Clearance requirements.
Cabinet airflow requirements.
Table 4 provides the cabinet requirements and specifications.
Cabinet Requirement |
Guidelines |
---|---|
Cabinet size |
|
Cabinet clearance |
|
Cabinet airflow requirements |
When you mount the device in a cabinet, ensure that ventilation through the cabinet is sufficient to prevent overheating, as follows:
|
Grounding Cable and Lug Specifications for EX9200 Switches
To ensure proper operation and to meet safety and electromagnetic interference (EMI) requirements, you must connect an EX9200 switch to earth ground before you connect power to the switch. You must use the protective earthing terminal on the switch chassis to connect the switch to earth ground.
The switch is installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be permanently connected to earth ground to adequately ground the chassis and protect the operator from electrical hazards.
Before switch installation begins, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the switch.
- Grounding Points Specifications for an EX9200 Switch
- Grounding Cable Lug Specifications for an EX9200 Switch
- Grounding Cable Specifications for an EX9200 Switch
Grounding Points Specifications for an EX9200 Switch
To meet safety and electromagnetic interference (EMI) requirements and to ensure proper operation, the switch must be adequately grounded before power is connected. To ground AC-powered and DC-powered switches, you must connect a grounding cable to earth ground and then attach it to the chassis grounding points using the two screws provided.
Two threaded inserts (PEM nuts) are provided on the upper rear of the chassis for connecting the switch to earth ground. The grounding points fit UNC 1/4–20 screws (American). The grounding points are spaced at 0.625 in. (15.86 mm) centers.
Additional grounding is provided to an AC-powered switch when you plug its power supplies into grounded AC power receptacles.
Grounding Cable Lug Specifications for an EX9200 Switch
The accessory box shipped with the switch includes one cable lug that attaches to the grounding cable (see Figure 4) and two UNC 1/4–20 screws used to secure the grounding cable to the grounding points.
Before switch installation begins, a licensed electrician must attach a cable lug to the grounding and power cables that you supply. A cable with an incorrectly attached lug can damage the switch.
The same cable lug is used for the DC power cables.
Grounding Cable Specifications for an EX9200 Switch
The grounding cable that you provide must meet the specifications in Table 5.
Cable Type |
Quantity and Specification |
---|---|
Grounding |
One 6 AWG (13.3 mm2), minimum 60 °C wire, or one that complies with the by the local code For DC-powered EX9214 switches, the 48 VDC facility must be equipped with a circuit breaker rated 40 A (–48 VDC), or 60 A (–48 VDC), and the grounding cable must be minimum 10 AWG, or one that complies with the by the local code. |