MX10004 Site Preparation Overview
The following topics describe general site planning and preparation for sites with MX10004 routers. Specific topics include site specifications, environmental requirements, electrical and wiring requirements, rack requirements, and airflow requirements for optimal MX10004 router performance.
MX10004 General Site Guidelines
Efficient router operation requires proper site planning and maintenance. It also requires proper layout of the router, the rack or cabinet (if used) and the wiring closet.
To plan and create an acceptable operating environment for your router and prevent environmentally caused equipment failures:
-
Keep the area around the chassis free from dust and conductive material, such as metal flakes.
-
Follow prescribed airflow guidelines to ensure that the cooling system functions properly and that exhaust from other equipment doesn’t blow into the intake vents of the router.
-
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent damage to the equipment. Static discharge can cause components to fail completely or intermittently over time.
-
Install the router in a secure area so that only authorized personnel can access the router.
MX10004 Site Preparation Checklist
The checklist in Table 1 summarizes the tasks you must perform to prepare a site for the MX10004 router.
✓ |
Item or Task |
For More Information |
---|---|---|
Environment | ||
□ |
Verify that environmental factors such as temperature and humidity are within router tolerances. |
|
Power | ||
□ |
Measure the distance between external power sources and the router installation site. |
|
□ |
Calculate the power consumption and requirements. |
|
Rack | ||
□ |
Verify that your rack meets the minimum requirements for router installation. |
|
□ |
Plan rack location, including required space clearances for optimal airflow. |
See MX10004 Clearance Requirements for Airflow and Hardware Maintenance. |
□ |
Secure the rack to the floor and the building structure. |
|
Cables | ||
□ |
Acquire cables and connectors:
|
The list of supported transceivers for the MX10004 line cards is located at https://apps.juniper.net/hct/product/#prd=MX10004. |
□ |
Plan the cable routing and management. |
MX10004 Environmental Requirements and Specifications
You must install the MX10004 router in a four-post rack. The router requires housing in a dry, clean, well-ventilated, and temperature-controlled environment.
Follow these environmental guidelines:
-
Ensure that the site is as dust free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the router cooling system.
-
Maintain ambient airflow for normal router operation. If the airflow is blocked or restricted, or if the intake air is too warm, the router might overheat. If the router overheats, the router temperature monitor might shut down the router to protect the hardware components.
Environmental tolerances for altitude and operating temperature depend on:
-
The type of ESD front door installed—either the standard JNP10004-FRNT-PNL without an air filter or the JNP10004-FPNL1 with air filter that is available as a spare.
-
The wattage of the type of optics being used—either 14 W or 21 W optics.
-
The line card slot. Slot 0 has slightly different airflow and cooling.
Description |
Tolerance |
---|---|
Altitude |
No performance degradation up to 6000 feet (1829 meters). |
Relative humidity |
|
Temperature |
|
Seismic zone |
Designed to comply with Zone 4 earthquake requirements according to NEBS GR-63-CORE, Issue 3. |
Install MX10004 routers only in restricted-access areas, such as dedicated equipment rooms and equipment closets. Install routers in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.
MX10004 Site Electrical Wiring Guidelines
MX10004 Environmental Requirements and Specifications describes the factors you must consider while you plan the electrical wiring at your site.
It is particularly important to provide a properly grounded and shielded environment and to use electrical surge-suppression devices.
Site Wiring Factor |
Guidelines |
---|---|
Signaling limitations |
To ensure that signaling functions optimally:
|
Radio frequency interference (RFI) |
To reduce or eliminate the emission of RFI from your site wiring:
|
Electromagnetic compatibility (EMC) |
Provide a properly grounded and shielded environment and use electrical surge-suppression devices. Strong sources of electromagnetic interference (EMI) can cause the following damage:
Tip:
If your site is susceptible to problems with EMC, particularly from lightning or radio transmitters, you might want to seek expert advice. |
The intrabuilding port or ports of the equipment or subassembly are suitable for connection to intrabuilding or unexposed wiring or cabling only. The intrabuilding port or ports of the equipment or subassembly MUST NOT be metallically connected to interfaces that connect to the OSP or its wiring. These interfaces are designed for use as intrabuilding interfaces only (Type 2 or Type 4 ports as described in GR-1089-CORE). The interfaces require isolation from the exposed OSP cabling. The addition of primary protectors is not sufficient protection to connect these interfaces metallically to OSP wiring.
MX10004 Rack Requirements
The MX10004 router chassis is designed to be installed in four-post racks.
Rack requirements consist of:
-
Rack type.
-
Rack mount kit hole spacing.
-
Rack size and strength.
-
Rack connection to the building structure.
Table 4 provides the rack requirements and specifications for the MX10004.
Rack Requirement |
Guidelines |
---|---|
Rack type: four-post |
Use a four-post rack that provides bracket holes or hole patterns spaced at 1-U (1.75 in. or 4.45 cm) increments and that meets the size and strength requirements to support the weight and seismic requirements. We recommend that you use a Telect DR1250-84436 rack or an equivalent rack. A U is the standard rack unit defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310–D) published by the Electronics Industries Association (EIA). You can mount up to six MX10004 routers in a four-post rack if:
Tip:
Always mount devices starting at the bottom of the rack. |
Rack-mount kit hole spacing |
The holes in the rack-mount kit are spaced at 1 U (1.75 in. or 4.45 cm) so that the router can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
|
Rack connection to building structure |
|
MX10004 Clearance Requirements for Airflow and Hardware Maintenance
When you plan the site for an MX10004 router installation, you must allow sufficient clearance around the installed chassis for cooling and maintenance. See Figure 1 for a top view of clearance for the MX10004.
For JNP10K-PWR-AC3 power supply, the overall depth is 36 in. (91.44 cm) instead of 34.2 in. and the power cable depth is 6 in. (15.24 cm) instead of 7 in.
Follow these guidelines:
-
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See MX10004 Cooling System for more information about the airflow through the chassis.
-
If you plan to mount an MX10004 in a rack with other equipment, ensure that the exhaust from other equipment doesn’t blow into the intake vents of the chassis.
-
Leave at least 30 in. (76.2 cm) in front of the chassis and at least 24 in. (61 cm) behind the MX10004 so that service personnel can remove and install hardware components. To be NEBS GR-63 compliant, allow at least 30 in. (76.2 cm) in front of the rack and 24 in. (61 cm) behind the rack.