PTX10016 Site Preparation Overview
The following sections describe the guidelines, the specifications, and the requirements to prepare the site for installing a PTX10016 router.
PTX10016 Site Preparation Checklist
The checklist in Table 1 summarizes the tasks you need to perform when preparing a site for a PTX10016 installation.
✓ |
Item or Task |
For More Information |
---|---|---|
Environment | ||
□ |
Verify that environmental factors such as temperature and humidity do not exceed router tolerances. |
|
Power | ||
□ |
Measure the distance between external power sources and the router installation site. |
— |
□ |
Calculate the power consumption and requirements. |
|
Rack | ||
□ |
Verify that your rack meets the minimum requirements for the installation of the router. |
|
□ |
Plan rack location, including required space clearances. |
PTX10016 Clearance Requirements for Airflow and Hardware Maintenance |
□ |
Secure the rack to the floor and building structure. |
— |
Cables | ||
□ |
Acquire cables and connectors:
|
The list of supported transceivers for the PTX10016 line cards is located at https://apps.juniper.net/hct/product/#prd=PTX10016. |
□ |
Plan the cable routing and management. |
— |
PTX10016 Environmental Requirements and Specifications
You must install the PTX10016 router in a four-post rack. You must house it in a dry, clean, well-ventilated, and temperature-controlled environment.
Follow these environmental guidelines:
The site must be as dust-free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the router cooling system.
Maintain ambient airflow for normal router operation. If the airflow is blocked or restricted, or if the intake air is too warm, the router might overheat, leading to the router temperature monitor shutting down the device to protect the hardware components.
Table 2 provides the required environmental conditions for normal router operation.
Description |
Tolerance |
---|---|
Altitude |
No performance degradation up to 6000 feet (1800 meters). |
Relative humidity |
Normal operation ensured in relative humidity range of 5% through 90%, noncondensing.
|
Temperature |
|
Seismic |
Designed to comply with Zone 4 earthquake requirements per NEBS GR-63-CORE, Issue 3. |
Install the PTX10016 router only in restricted-access areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.
General Site Guidelines
Efficient device operation requires proper site planning and maintenance and proper layout of the equipment, rack or cabinet (if used), and wiring closet.
To plan and create an acceptable operating environment for your device and prevent environmentally caused equipment failures:
Keep the area around the chassis free from dust and conductive material, such as metal flakes.
Follow prescribed airflow guidelines to ensure that the cooling system functions properly and that exhaust from other equipment does not blow into the intake vents of the device.
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent damaging the equipment. Static discharge can cause components to fail completely or intermittently over time.
Install the device in a secure area, so that only authorized personnel can access the device.
See Also
PTX10016 Site Electrical Wiring Guidelines
Table 3 describes the factors you must consider while planning the electrical wiring at your site.
It is particularly important to provide a properly grounded and shielded environment and to use electrical surge-suppression devices.
Site Wiring Factor |
Guideline |
---|---|
Signaling limitations |
To ensure that signaling functions optimally:
|
Radio frequency interference (RFI) |
To reduce or eliminate the emission of RFI from your site wiring:
|
Electromagnetic compatibility (EMC) |
Provide a properly grounded and shielded environment and use electrical surge-suppression devices. Strong sources of electromagnetic interference (EMI) can cause the following damage:
Tip:
If your site is susceptible to problems with EMC, particularly from lightning or radio transmitters, you might want to seek expert advice. |
The intrabuilding port(s) of the equipment or subassembly is suitable for connection to intrabuilding or unexposed wiring or cabling only. The intrabuilding port(s) of the equipment or subassembly must not be metallically connected to interfaces that connect to the outside plant (OSP) or its wiring. These interfaces are designed for use as intrabuilding interfaces only (Type 2 or Type 4 ports as described in GR-1089-CORE), and require isolation from the exposed OSP cabling. The addition of primary protectors is not sufficient protection to connect these interfaces metallically to OSP wiring.
PTX10016 Rack Requirements
The PTX10016 router chassis are designed to be installed in four-post racks.
Rack requirements consist of:
Rack type
Rack mount kit hole spacing
Rack size and strength
Rack connection to the building structure
Table 4 provides the rack requirements and specifications for the PTX10016 router.
Rack Requirement |
Guidelines |
---|---|
Rack type: four-post |
Use a four-post rack that provides bracket holes or hole patterns spaced at 1-U (1.75 in. or 4.45 cm) increments and that meets the size and strength requirements to support the weight. Note:
A U is the standard rack unit defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310–D) published by the Electronics Industry Association. You can stack two PTX10016 routers at the bottom of the four-post rack if:
|
Rack mount kit hole spacing |
The holes in the rack mount kit are spaced at 1 U (1.75 in. or 4.45 cm), so that the router can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
|
Rack connection to building structure |
|
PTX10016 Clearance Requirements for Airflow and Hardware Maintenance
When planning the site for a PTX10016 router installation, you must allow sufficient clearance around the installed chassis for cooling and maintenance. See Figure 1 and Figure 2 for the top view of the clearance for the PTX10016.
For JNP10K-PWR-AC3 power supply, the overall depth is 36 in. (91.44 cm) instead of 34.2 in. and the power cable depth is 6 in. (15.24 cm) instead of 7 in.
Follow these guidelines:
-
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See PTX10016 Cooling System and Airflow for more information about the airflow through the chassis.
-
If you are mounting a PTX10016 in a rack with other equipment, ensure that the exhaust from other equipment does not blow into the intake vents of the chassis.
-
Leave at least 24 in. (61 cm) both in front of and behind the PTX10016 for service personnel to remove and install hardware components. To be NEBS GR-63 compliant, allow at least 30 in. (76.2 cm) in front of the rack and 24 in. (61 cm) behind the rack.
See Also
PTX10016 Chassis Physical Specifications
The PTX10016 modular chassis is a rigid sheet-metal structure that houses the field-replaceable units (FRUs). The maximum weight of a fully populated chassis, without line cards installed in it, is 706.2 lb (320.33 kg). You can mount up to two PTX10016 routers in a standard 19-in. 4-post rack (42 U) rack, provided the rack can handle the combined weight and there is adequate power and cooling. Table 5 summarizes the physical specifications of the chassis. See Figure 3.
The specifications of the line cards are without optics or the cable management system.
Description |
Net Weight |
Height |
Width |
Depth |
---|---|---|---|---|
Chassis, spare |
220 lb (99.79 kg) |
36.65 in. (93.09 cm) |
17.4 in. (44.2 cm) Note:
The outer edges of the chassis flange extend the width to 19 in. (48.3 cm). |
35 in. (88.9 cm) 42.4 in. (107.7 cm) with EMI door |
Routing and Control Board (RCB) | 12.2 lb (5.5 kg) |
1.3 in. (3.3 cm) |
15.1 in. (38.35 cm) |
20.3 in. (51.56 cm) |
JNP10016-FAN |
19.8 lb (8.98 kg) |
36.6 in. (92.97 cm) |
6.6 in. (16.8 cm) |
4.0 in. (10.2 cm) without handles, 5.2 in. (13.2 cm) with handles |
JNP10016-FAN2 |
34 lb (15.42 kg) |
36.5 in. (92.97 cm) |
6.6 in. (16.8 cm) |
5.5 in. (13.97 cm) without handles, 6.7 in. (17.01 cm) with handles |
JNP10016-FAN-CTRL |
1.5 lb (0.68 kg) |
1.5 in. (3.81 cm) |
6.5 in. (15.24 cm) |
12.4 in. (31.5 cm) |
JNP10016-FTC2 |
2.2 lb (1 kg) |
1.5 in. (3.81 cm) |
6.5 in. (15.24 cm) |
12.4 in. (31.5 cm) |
JNP10K-PWR-AC power supply |
6.8 lb (3.08 kg) |
3.4 in. (8.64 cm) |
3.6 in. (9.14 cm) |
14.4 in. (36.58 cm) |
JNP10K-PWR-AC2 power supply |
11.4 lb (5.17 kg) |
3.4 in. (8.64 cm) |
3.6 in. (9.14 cm) |
16.6 in. (42.16 cm) |
JNP10K-PWR-DC power supply |
6 lb (2.72 kg) |
3.4 in. (8.64 cm) |
3.6 in. (9.14 cm) |
14.4 in. (36.58 cm) |
JNP10K-PWR-DC2 power supply |
8.6 lb (3.9 kg) |
3.4 in. (8.64 cm) |
3.6 in. (9.14 cm) |
16.05 in. (40.77 cm) |
JNP10016-SF SIB switch fabric |
39.4 lb (17.88 kg) |
34.6 in. (87.88 cm) |
1.8 in. (4.57 cm) |
13.4 in. (34.04 cm) |
JNP10016-SF3 SIB switch fabric |
42.7 lb (19.37 kg) |
34.5 in. (87.6 cm) |
1.8 in. (4.57 cm) |
13.3 in. (33.8 cm) |
Switch fabric slot cover panel (Part number: JNP10016-SF-BLNK2) |
8.2 lb (3.72 kg) |
33.85 in. (85.98) |
1.8 in. (4.57 cm) |
12.77 in. (32.44 cm) |
PTX10K-LC1101 line card |
27 lb (12.2 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
20.54 in. (52.2 cm) |
PTX10K-LC1102 line card |
22.6 lb (10.2 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
20.54 in. (52.2 cm) |
PTX10K-LC1104 line card |
32 lb (14.5 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
20.54 in. (52.2 cm) |
PTX10K-LC1105 line card |
28.5 lb (12.9 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
20.54 in. (52.2 cm) |
PTX10K-LC1201-36CD line card |
35 lb (15.88 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
21.3 in. (54.1 cm) |
PTX10K-LC1202-36MR line card |
21 lb (9.5 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
21.3 in. (54.1 cm) |
QFX10000-60S-6Q line card |
21.4 lb (9.7 kg) |
1.9 in. (4.8 cm) |
17.2 in. (43.7 cm) |
20.54 in. (52.2 cm) |
Line card slot cover panel | 1.2 lb (0.54 kg) |
2.1 in. (5.33 cm) |
17.4 in. (44.2 cm) |
3.4 in. (8.64 cm) |
1 — RCBs | 4 — Mounting holes for front panel |
2 — Status panel | 5 — Line cards |
3 — Handles |
The handles on each side of the chassis facilitate the fine-tune positioning of the chassis on the base brackets. Do not use the handles to lift the chassis, even when the chassis is empty. See Mount the PTX10016 by Using the EX-MOD-RMK-4POST Rack Mount Kit for instructions for properly moving a loaded chassis.