PTX5000 AC Power Electrical Safety Guidelines
The following electrical safety guidelines apply to an AC-powered PTX5000 with three-phase AC power supplies:
AC-powered PTX5000 routers are shipped with three-phase electrical cords with grounding. Do not circumvent this safety feature. Equipment grounding must comply with local and national electrical codes.
For each three-phase delta AC power distribution unit (PDU), you must provide an external listed customer-site circuit breaker rated minimum 60 A (240 VAC) in the building installation, or as required by local code.
For each three-phase wye AC PDU, you must provide an external listed customer-site circuit breaker. See PTX5000 AC and DC PDU Electrical and External Circuit Breaker Specifications for details, or as required by local code.
The delta cores in the mains lead are labeled as follows:
Wire labeled GND—Earth
Wire labeled L1
Wire labeled L2
Wire labeled L3
The wye cores in the mains lead are labeled as follows:
Wire labeled GND—Earth
Wire labeled L1
Wire labeled L2
Wire labeled L3
Wire labeled N