QFX10002 Power System

QFX10002 AC Power Supply Description

The AC power supplies in QFX10002 models (see Figure 1) are hot-removable, and hot-insertable field-replaceable units (FRUs) that you can install without powering off the switch or disrupting the switching function. The QFX10002-36Q switch has two power supplies; the QFX10002-60C and QFX10002-72Q have four power supplies. All of the power supplies are installed at the factory.

Each of the 1600-W power supplies has a single AC input. A QFX10002 has double the amount of power supplies needed to power all of the components in the switch, which is known as 2N redundancy. When the switch has all of the power supplies installed, the switch has full power redundancy. If a power supply fails or is removed, a second power supply balances the electrical load without interruption. For more on redundancy configuration options, see QFX10002 Component Redundancy. Each power supply provides 12-VDC output with a standby voltage of 12 VDC.

Figure 1: 1600-W AC Power Supply in a QFX10002 Models1600-W AC Power Supply in a QFX10002 Models
  1

Power connector

  3

Ejection lever

  2

Power LED

  4

Handle

The fan in the power supply provides port-to-FRU airflow, which is also known as airflow out (AFO). A power supply with the label AFO or a gold-colored handle denotes port-to-FRU airflow.

Table 1 shows the characteristics of the power supply.

Table 1: QFX10002 AC Power Supply

Wattage

Product Number

Direction of Airflow

Color of Power Supply Handle

1600-W

JPSU-1600W-AC-AFO

Port-to-FRU

Juniper Gold

To avoid electrical injury, carefully follow instructions in Connecting AC Power to a QFX10002 and Removing a Power Supply from a QFX10002.

QFX10002 AC Power Specifications

Table 2 describes the AC power specifications for a QFX10002 switch.

Table 2: AC Power Specifications for a QFX10002 Switch

Item

Specification

AC input voltage

Operating range: 100V-127 VAC and 200V-240 VAC

AC input line frequency

50–60 Hz

AC input current rating

  • 12.9 A at 100–120 VAC for QFX10002-72Q

  • 11.5 A at 100–120 VAC for QFX10002-60C

  • 9.5 A at 100–120 VAC for QFX10002-36Q

Typical power consumption

  • 1050 W for QFX10002-72Q

  • 1728 W for QFX10002-60C

  • 560 W for QFX10002-36Q

Maximum power consumption

  • 1425 W for QFX10002-72Q

  • 1824 W for QFX10002-60C

  • 800 W for QFX10002-36Q

AC Power Cord Specifications for QFX10002 Switches

Detachable AC power cords are shipped with the chassis, if you include them as part of your order. The coupler is type C13 as described by International Electrotechnical Commission (IEC) standard 60320. The plug end of the power cord fits into the power source outlet that is standard for your geographical location.

Note:

In North America, AC power cords must not exceed 14.75 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52, and Canadian Electrical Code (CEC) Section 4-010(3). The cords that can be ordered for the QFX Series switches are in compliance.

The following tables list AC power cord specifications provided for each country or region.

Table 3: AC Power Cord Specifications for QFX10002-60C Switches

Country/Region

Electrical Specifications

Plug Standards

Shipped Juniper Model Number

Spare Juniper Model Number

Graphic

Australia

250 VAC, 10 A, 50 Hz

AS/NZ 3109-1996

CG_CBL-C13-09-AU

CBL-EX-PWR-C13-AU

China

250 VAC, 10 A, 50 Hz

GB 1002-1996

CG_CBL-C13-09-CH

CBL-EX-PWR-C13-CH

Europe (except Italy, Switzerland, and United Kingdom)

250 VAC, 10 A, 50 Hz

CEE (7) VII

CG_CBL-C13-09-EU

CBL-EX-PWR-C13-EU

Italy

250 VAC, 10 A, 50 Hz

CEI 23-16/VII

CG_CBL-C13-09-IT

CBL-EX-PWR-C13-IT

Japan

125 VAC, 12 A, 50 Hz or 60 Hz

JIS C8303

CG_CBL-C13-09-JP

CBL-EX-PWR-C13-JP

North America

(QFX10002-36Q, QFX10002-72Q only) 125 VAC, 13 A, 60 Hz

(all models) 250 VAC, 13 A, 60 Hz

(all models) 250 VAC, 13 A, 60 Hz

CAN/CSA No. 49-92

NEMA L6-15

NEMA 6-15

CG_CBL-C13-09-US

CBL-PW-C13-250L-US (default)

CBL-PWR-C13-250-US

South Korea

250 VAC, 10 A, 60 Hz

250 VAC, 13 A, 60 Hz

KSC 8305; K60884-1

CG_CBL-C13-09-KR

CBL-EX-PWR-C13-KR

Switzerland

250 VAC, 10 A, 50 Hz

SEV 1011 SEV 1991; EN 60320 C13

CG_CBL-C13-09-SZ

CBL-EX-PWR-C13-SZ

United Kingdom

250 VAC, 10 A, 50 Hz

BS 1363/A

CG_CBL-C13-09-UK

CBL-EX-PWR-C13-UK

Table 4: AC Power Cord Specifications for QFX10002-36Q and QFX10002-72Q Switches

Country/Region

Electrical Specifications

Plug Standards

Shipped Juniper Model Number

Spare Juniper Model Number

Graphic

Australia

250 VAC, 10 A, 50 Hz

AS/NZ 3109-1996

CG_CBL-C13-06-AU

CBL-EX-PWR-C13-AU

China

250 VAC, 10 A, 50 Hz

GB 1002-1996

CG_CBL-C13-06-CH

CBL-EX-PWR-C13-CH

Europe (except Italy, Switzerland, and United Kingdom)

250 VAC, 10 A, 50 Hz

CEE (7) VII

CG_CBL-C13-06-EU

CBL-EX-PWR-C13-EU

Italy

250 VAC, 10 A, 50 Hz

CEI 23-16/VII

CG_CBL-C13-06-IT

CBL-EX-PWR-C13-IT

Japan

125 VAC, 12 A, 50 Hz or 60 Hz

JIS C8303

CG_CBL-C13-06-JP

CBL-EX-PWR-C13-JP

North America

(QFX10002-36Q, QFX10002-72Q only) 125 VAC, 13 A, 60 Hz

(all models) 250 VAC, 13 A, 60 Hz

(all models) 250 VAC, 13 A, 60 Hz

CAN/CSA No. 49-92

NEMA L6-15

NEMA 6-15

CG_CBL-C13-06-US

CBL-EX-PWR-C13-US

CBL-PW-C13-250-US

CBL-PWR-C13-250-US

South Korea

250 VAC, 10 A, 60 Hz

250 VAC, 13 A, 60 Hz

KSC 8305; K60884-1

CG_CBL-C13-06-KR

CBL-EX-PWR-C13-KR

Switzerland

250 VAC, 10 A, 50 Hz

SEV 1011 SEV 1991; EN 60320 C13

CG_CBL-C13-06-SZ

CBL-EX-PWR-C13-SZ

United Kingdom

250 VAC, 10 A, 50 Hz

BS 1363/A

CG_CBL-C13-06-UK

CBL-EX-PWR-C13-UK

QFX10002 DC Power Supply Description

The DC power supplies in QFX10002 models (see Figure 2) are hot-removable and hot-insertable field-replaceable units (FRUs) that install without powering off the device or disrupting the switching function. The two 1600-W power supplies in a QFX10002-36Q are installed at the factory and supply 1200 W of power to the chassis. Likewise, the four 1600-W power supplies in a QFX10002-72Q switch are installed at the factory and supply 2400 W of power to the chassis.

A QFX10002 has double the amount of power supplies needed to power all of the components in the switch, which is known as 2N redundancy. When the switch has all of the power supplies installed, the switch has full power redundancy. If a power supply fails or is removed, a second power supply balances the electrical load without interruption. For more on redundancy features, see QFX10002 Component Redundancy. Each power supply provides 12-VDC output with a standby voltage of 12 VDC.

Figure 2: DC Power Supply in QFX10002 ModelsDC Power Supply in QFX10002 Models
  1

Power LED

  3

Handle

  2

Ejector lever

 

The fan in the power supply provides port-to-FRU airflow, which is also known as airflow out (AFO). A power supply with the label AFO or a gold-colored handle denotes port-to-FRU airflow.

Table 5 shows the characteristics of the power supply.

Table 5: QFX10002 DC Power Supply

Wattage

Product Number

Direction of Airflow

Color of Power Supply Handle

1600-W

JPSU-1600W-DC-AFO

Port-to-FRU

Juniper Gold

We recommend that the 48 VDC facility DC source be equipped with a circuit breaker rated at 40 A (–48 VDC) minimum, or as required by local code.

To avoid electrical injury, carefully follow instructions in Maintaining QFX10002 Power Supplies .

QFX10002 DC Power Specifications

Table 6 describes the DC power specifications for the DC version of a QFX10002 switch.

Table 6: DC Power Specifications for a QFX10002

Item

Specifications

DC input voltage

  • Rated operating voltage: VDC -48 VDC to -60 VDC

  • Operating voltage range: –40 VDC through -72 VDC

DC input current rating

40 A maximum for QFX10002-36Q and QFX10002-72Q

57.5 A maximum for QFX10002-60C

Typical power consumption

  • 1050 W for QFX10002-72Q

  • 1642 W for QFX10002-60C

  • 560 W for QFX10002-36Q

Maximum power consumption

  • 1425 W for QFX10002-72Q

  • 1857 W for QFX10002-60C

  • 800 W for QFX10002-36Q

We recommend that the 48 VDC facility DC source be equipped with a circuit breaker rated at 40 A (–48 VDC) minimum, or as required by local code.

QFX10002 DC Power Cable Specifications

QFX10002 DC power supplies require a D-Sub 3W3-type connector. The three pins on the connector provide –48 VDC input (–), return (+), and ground connections to the power supply.

Note:

The optional right-angle DC power cables, CBL-JNP-PWR-DSUB2 and CBL-JNP-PWR-DSUB3, do not include a ground connection wire. See Connecting the QFX10002 to Ground.

DC power cables, each 4 m (approximately 13.1 ft) long, are supplied with the QFX10002. The provided cables include the three-pin connector on one end and three insulated wires at the opposite end, for connection to the site’s DC power distribution system.

Table 7 lists the specifications for the QFX10002 DC power cables.

Table 7: QFX10002 DC Power Cable Specifications

Juniper Model Number

Wire Function

Insulation Color

Wire Size

CBL-JNP-PWR-DSUB

Straight cable

–48 VDC input (–)

Blue

8 AWG (8.4 mm²), 90° C

Return (+)

Black

8 AWG (8.4 mm²), 90° C

Ground

Green and yellow

8 AWG (8.4 mm²), 90° C

CBL-JNP-PWR-DSUB2

(Optional) right-angle cable

–48 VDC input (–)

Blue

8 AWG (8.4 mm²), 90° C

Return (+)

Black

8 AWG (8.4 mm²), 90° C

CBL-JNP-PWR-DSUB3

(Optional) FT4 vertical-flame rated, right-angle cable

–48 VDC input (–)

Gray

8 AWG (8.4 mm²), 90° C

Return (+)

Gray

8 AWG (8.4 mm²), 90° C

Note:

The optional right-angle DC power cables, CBL-JNP-PWR-DSUB2 and CBL-JNP-PWR-DSUB3, do not include a ground connection wire.

Warning:

For field-wiring connections, use copper conductors only.

Warning:

Power cables must not block access to QFX10002 components or drape where people could trip on them.

CAUTION:

You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site might be different from the color coding for the leads on the DC power cable provided with the chassis.

QFX10002 Power Supply LED

Figure 3 shows the location of the status LED on the QFX10002 AC power supply and Figure 4 shows the location of the status LED on the QFX10002 DC power supply.

Figure 3: AC Power Supply LEDAC Power Supply LED
  1

Status LED

 
Figure 4: DC Power Supply LEDDC Power Supply LED
  1

Status LED

 

Table 8 describes the status LED behavior on QFX10002 power supplies.

Table 8: Power Supply LEDs on a QFX10002 Switch

Color

State

Description

Green

Amber

On steadily

Off

The power supply is on and operating correctly.

Green

Amber

Slow blinking (1 Hz)

Off

The power supply is in cold standby mode; only the 12 V DC input is present.

Green

Amber

Blinking (2 Hz)

Off

The power supply is uploading firmware.

Green

Amber

Off

Blinking

Warning events are being detected; the power supply continues to operate. Often these events are because of rising temperatures. Check the fans and ensure there is proper airflow through the chassis.

Green

Amber

Off

On steadily

Either the power cord is unplugged or a major error is detected in the power supply. Examples of a major error are: power supply failure, an over voltage protection error, an over current protection error, or a fan failure.

  • If the power cord is unplugged or missing, reattach the power cord appropriate for your country.

  • If a major error is occurring, Replace the power supply as soon as possible. To maintain proper airflow through the chassis, leave the power supply installed in the chassis until you are ready to replace it.

Green

Amber

Off

Off

There is no AC power to any of the power supplies.

You can get additional information about the status of the power modules using the show chassis environment pem command. For example: