MX10004 Power System

MX10004 routers support AC, DC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) by offering the following power supplies:

  • JNP10K-PWR-AC3

  • JNP10K-PWR-AC2

  • JNP10K-PWR-DC2

You can install up to three power supplies in the slots labeled PSU0 through PSU2 (top to bottom) located in the rear of the chassis.

Note:

The JNP10K-PWR-AC2 and JNP10K-PWR-AC3 can share power proportionally in a mixed configuration, only when you are upgrading to JNP10K-PWR-AC3.

JNP10K-PWR-AC3 Power Supply

The JNP10K-PWR-AC3 power supply is a high-capacity model that is designed to support AC systems in a 15-A and 20-A mode; see Figure 1.

Figure 1: JNP10K-PWR-AC3 Power Supply JNP10K-PWR-AC3 Power Supply

Input—The power supply takes four single-phase AC (180-264 VAC) inputs (A0, A1, B0, and B1) at either 20 A or 15 A and provides a DC output of 12.3V. The input receptacle on the AC power supply unit (PSU) is IEC 320-C22. The mating connector on the power cord is IEC 320-C21.

Output—The power supply provides DC output of 12.3V at:

  • 7800 W (20-A input) with three or four active feeds, or
  • 6000 W (20-A input) with two active feeds (either A0 and A1 or B0 and B1), or
  • 3000 W (20-A input) with single active feed.
  • 7800 W (15-A input) with four active feeds, or

  • 7500 W (15-A input) with three active feeds, or

  • 5000 W (15-A input) with two active feeds, or

  • 2500 W (15-A input) with single active feed.

  • The operating input voltage range is 180 to 264 VAC for AC systems. The DC output is 12.3 VDC.

  • The number of power feeds and whether the power supplies provide high-output (20-A) or low-output (15-A) power are configured using a set of dual inline package (DIP) switches on the faceplate of the power supply. If one power supply in the chassis is set to low power, the power budget for the chassis is reduced to low power, regardless of their DIP switch settings or the output results in the CLI. This design safeguards against accidentally setting the power supply to 20 A in a facility that can provide only 15 A and tripping the facility circuit breaker. We recommend that you don’t mix DIP switch settings in your system. See Table 2 for information about the input and output voltages when you use the DIP switches.

  • The JNP10K-PWR-AC3 power supply has an ENABLE switch on the front panel to enable/disable the main 12.3 VDC output and +5.0 V_BIAS standby output as well. If the switch is in DISABLE position, the front-end PFC will be disabled to minimize power consumption. This switch has the highest priority over any other shutdown method.

  • The Power Factor Correction (PFC) is PF 0.98 kW minimum at full load. The maximum inrush current is 50 A for the active feed.

JNP10K-PWR-BLN3 or Active Blank

Juniper Networks offers an Active Blank Power Module (ABPM), JNP10K-PWR-BLN3. This helps in airflow and cooling in the chassis. You can have the following combination of ABPM, passive blank, and JNP10K-PWR-AC3 power supply units (PSU) in the router chassis:

  • Three PSUs

  • Two PSUs with one ABPM

  • One PSU with one ABPMs and one passive blank

  • One PSU with two ABPMs

  • Table 1: PSU, ABPM, Passive Blank Matrix

    JNP10K-PWR-AC3 PSU(s)

    ABPM (JNP10K-PWR-BLN3)

    Passive Blank

    3

    -

    -

    2

    1

    -

    1

    1

    1

    1

    2

    -

    Note:

    A minimum of one JNP10K-PWR-AC3 power supply unit (PSU) must be present in the router chassis.

The JNP10K-PWR-AC3 power supply has internal fans that contribute to chassis cooling. Three PSUs or two PSUs along with a ABPM must be present in a running chassis to have the adequate airflow. While the minimum power supplies are required to be present in the chassis, they all need not be necessarily connected to power source. If a power supply is installed in a slot but not connected to a power source, it draws power from the chassis to power the internal fans in the power supplies.

Warning:

Extreme burn danger—The JNP10K-PWR-AC3 can reach temperatures in the range of 158°F to 176°F (70°C to 80°C) under running conditions.

Warning:

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be connected to earth ground permanently to ground the chassis adequately and protect the operator from electrical hazards.

CAUTION:

Before you begin installing the router, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the router.

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.

The JNP10K-PWR-AC3 Power Supplies have five dual position DIP switches (INP-A0, INP-A1, INP-B0, INP-B1, and DIP4) that are accessible from the front panel. DIP4 is the fifth DIP switch, which is used to indicate whether 20A or 15A input source is connected. See Figure 2 and Table 2 to know the layout of the DIP switches and the power output when the DIP switches are set in different combinations.

Figure 2: DIP Switches on NP10K-PWR-AC3 Power Supply DIP Switches on NP10K-PWR-AC3 Power Supply

1—LEDs corresponding to the DIP switches above it.

Table 2: DIP Switch Settings for JNP10K-PWR-AC3 Power Supply

INP-A0 (Switch 0)

INP-A1 (Switch 1)

INP-B0 (Switch 2)

INP-B1 (Switch 3)

Switch 4 (High Input 20 A/Low Input 15 A)

Output Power

15-A

Off

Off

Off

On

Off (15 A)

2500 W

Off

Off

On

Off

Off (15 A)

2500 W

Off

Off

On

On

Off (15 A)

5000 W

Off

On

Off

Off

Off (15 A)

2500 W

Off

On

Off

On

Off (15 A)

5000 W

Off

On

On

On

Off (15 A)

7500 W

Off

On

On

Off

Off (15 A)

5000 W

On

Off

Off

Off

Off (15 A)

2500 W

On

Off

Off

On

Off (15 A)

5000 W

On

Off

On

Off

Off (15 A)

5000 W

On

Off

On

On

Off (15 A)

7500 W

On

On

Off

Off

Off (15 A)

5000 W

On

On

Off

On

Off (15 A)

7500 W

On

On

On

Off

Off (15 A)

7500 W

On

On

On

On

Off (15 A)

7800 W

20-A

Off

Off

Off

On

On (20 A)

3000 W

Off

Off

On

Off

On (20 A)

3000 W

Off

Off

On

On

On (20 A)

6000 W

Off

On

Off

Off

On (20 A)

3000 W

Off

On

Off

On

On (20 A)

6000 W

Off

On

On

Off

On (20 A)

6000 W

Off

On

On

On

On (20 A)

7800 W

On

Off

Off

Off

On (20 A)

3000 W

On

Off

Off

On

On (20 A)

6000 W

On

Off

On

Off

On (20 A)

6000 W

On

Off

On

On

On (20 A)

7800 W

On

On

Off

Off

On (20 A)

6000 W

On

On

Off

On

On (20 A)

7800 W

On

On

On

Off

On (20 A)

7800 W

On

On

On

On

On (20 A)

7800 W

CAUTION:

It is important to connect the input feeds of the JNP10K-PWR-AC3 power supply to AC mains before powering-on the router.

JNP10K-PWR-AC3 Power Specifications

The JNP10K-PWR-AC3 power supply supports AC.

Table 3lists the power specifications for the AC power supply (JNP10K-PWR-AC3) used in a MX10004 chassis.

Table 3: Power Specifications for a JNP10K-PWR-AC3 Power Supply

Specification

Value

AC input voltage

180–264 VAC

Input current rating

16 A

DC output power

12.3 V

Table 4 shows the physical specifications for a JNP10K-PWR-AC2 power supply.

Table 4: Physical Specifications for a JNP10K-PWR-AC3 Power Supply

Specification

Value

Height

3.386 in. (8.60 cm)

Width

3.584 in. (9.10 cm)

Depth

17.15 in. (43.57 cm)

Weight

12.8 lbs (5.8 kg)

JNP10K-PWR-AC3 Power Supply LEDs

The JNP10K-PWR-AC3 power supply has six LEDs on its faceplate: !, OK, A0, A1, B0, and B1. The numbered LEDs correspond to the four inputs (INP-A0, INP-A1, INP-B0, and INP-B1). Additionally, there are two more LEDs OK (Power OK) and !(Fault). These LEDs display information about the status of the power supply. See Figure 3.

Figure 3: LEDs on a JNP10K-PWR-AC3 Power Supply LEDs on a JNP10K-PWR-AC3 Power Supply

1—LEDs on the JNP10K-PWR-AC3 Power Supply denoting:

  • ! Fault

  • OK Power OK

  • A0 INP A0–Source input 1

  • A1 INP A1–Source input 2

  • B0 INP B0–Source input 3

  • B1 INP B1–Source input 4

Note:

Physical markings on the power supply are 1, 2, 3, and 4. These markings correspond to INP-A0, INP-A1, INP-B0, and INP-B1 in the show chassis power output (see Table 5).

Table 5: Physical Markings on AC3 Chassis Versus show chassis power Command

Physical Marking on JNP10K-PWR-AC3

show chassis power Command

INP A0

INP-A0

INP A1

INP-A1

INP B0

INP-B0

INP B1

INP-B1

Table 6 describes the LEDs on a JNP10K-PWR-AC3 power supply, color on the LED, state, and its meaning.

Table 6: JNP10K-PWR-AC3 LEDs on a MX10004

LED

Color

State

Description

1 or (AO in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

2 or (A1 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

3 or (B0 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

4 or (B1 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

OK (Power OK)

Green

Solid

The power supply is functioning properly.

Yellow

Blinking

The power supply output has detected a fault.

Unlit

Off

The power supply is switched off.

! (Fault)

Red

Solid

The power supply has failed and must be replaced.

Unlit

Off

The power supply is functioning normally.

JNP10K-PWR-AC2 Power Supply

The JNP10K-PWR-AC2 power supply is a high-capacity model that is designed to support AC, high-voltage AC (HVAC), or high-voltage DC (HVDC) systems in either a 20-A or a 30-A mode; see Figure 4. The power supply feeds AC input and provides DC output of 5000 W with a single feed and 5500 W with a dual feed. The operating input voltage range is 180 to 305 VAC for AC systems and 190 to 410 VDC for DC systems.

You configure the number of power feeds and high or low output using a set of dual inline package (DIP) switches on the faceplate of the power supply. You use the switches to configure whether the power supplies provide high-output (30-A) or low-output (20-A) power. If one power supply in the chassis is set to low power, the power budget for the chassis is reduced to low power, regardless of the DIP switch settings or the output results in the CLI. This design safeguards against accidentally setting the power supply to 30 A in a facility that can provide only 20 A and tripping the facility circuit breaker. We recommend that you not mix DIP switch settings in your system. See Table 7 for information about the input and output voltages when you use the DIP switches.

The JNP10K-PWR-AC2 power supply has internal fans that contribute to chassis cooling. Consequently, all three power supplies must be present in a running chassis to provide adequate airflow. While all power supplies are required to be present in the chassis, they do not all need to be connected to power. If a power supply is installed in a slot but not connected to a power source, it draws power from the chassis to power the internal fans in the power supplies.

Figure 4: JNP10K-PWR-AC2 Power Supply JNP10K-PWR-AC2 Power Supply
Warning:

Extreme burn danger! Do not handle an HVAC or HVDC power supply running in the chassis without heat-protective gloves. The JNP10K-PWR-AC2 can reach temperatures in the range of 158° F to 176° F (70° C to 80° C) under running conditions.

Warning:

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be connected to earth ground permanently to ground the chassis adequately and protect the operator from electrical hazards.

CAUTION:

Before you begin installing the router, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the router.

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or according to the local electrical code.

Table 7: DIP Switch Settings for JNP10K-PWR-AC2 Power Supplies

INP0 (Switch 1)

INP1 (Switch 2)

H/L (High Input 30 A/Low Input 20 A)

Output Power

On

On

On (30 A)

5500 W

On

On

Off (20 A)

3000 W

On

Off

On (30 A)

5000 W

Off

On

On (30 A)

5000 W

On

Off

Off (20 A)

2700 W

Off

On

Off (20 A)

2700 W

CAUTION:

It is important to connect both input feeds of the JNP10K-PWR-AC2 power supply to the main AC power before loading the system with power.

JNP10K-PWR-AC2 Power Specifications

The JNP10K-PWR-AC2 power supply supports AC, high-voltage alternating current (HVAC) and high-voltage direct current (HVDC).

Table 8 lists the power specifications for the AC power supply (JNP10K-PWR-AC2) used in an MX10004 chassis.

Table 8: Power Specifications for a JNP10K-PWR-AC2 Power Supply

Specification

Value

AC input voltage

180–305 VAC

DC input voltage

190–410 VDC

Input current rating

28.5 A

DC output power

12.3 V, 5500 W with dual feed and 5000 W with single feed

Table 9 shows the physical specifications for a JNP10K-PWR-AC2 power supply.

Table 9: Physical Specifications for a JNP10K-PWR-AC2 Power Supply

Specification

Value

Height

3.5 in. (8.89 cm)

Width

3.6 in. (9.14 cm)

Depth

15.1 in. (38.35 cm)

Weight

11.4 lb (5.17 kg)

JNP10K-PWR-AC2 Power Supply LEDs

The JNP10K-PWR-AC2 power supply has four LEDs on its faceplate: !, OK, 2, and 1. These LEDs display information about the status of the power supply. See Figure 5.

Figure 5: LEDs on a JNP10K-PWR-AC2 Power Supply LEDs on a JNP10K-PWR-AC2 Power Supply
  1

! Fault

  3

2 INP2–Source input 2

  2

OK Power OK

  4

1 INP1–Source input 1

Note:

Physical markings on the power supply are 1 and 2. These markings correspond to INP1 and INP2 in the show chassis power output (see Table 10).

You can display the DIP switch settings for input and output power using the show chassis power command.

Table 10: Physical Markings on Chassis Versus show chassis power Command

Physical Marking on JNP10K-PWR-AC2

show chassis power Command

INP1

INP1

INP2

INP2

Table 11 describes the LEDs on a JNP10K-PWR-AC2 power supply.

Table 11: JNP10K-PWR-AC2 LEDs on an MX10004

LED

Color

State

Description

1 or (INP1 in CLI output)

Yellow

Blinking

The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

Unlit

Off

The power supply is switched off; voltage is zero.

2 or (INP2 in CLI output)

Yellow

Blinking

The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

Unlit

Off

The power supply is switched off; voltage is zero.

OK (Power OK)

Green

Solid

The power supply is functioning properly.

Yellow

Blinking

The power supply output has detected a fault.

! (Fault)

Red

Solid

The power supply has failed and must be replaced.

Unlit

Off

The power supply is functioning normally.

MX10004 Power Cable Specifications

Most sites distribute power through a main conduit that leads to frame-mounted power distribution panels, one of which can be located at the top of the rack that houses the router. An AC power cord connects each power supply to the power distribution panel.

Note:

In North America, AC power cords must not exceed 15 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52 and with Canadian Electrical Code (CEC) Section 4-010(3). The cords shipped with the router to North America and Canada are in compliance.

The MX10004 AC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) power supplies have specific cord requirements. Use the following sections to determine the cable requirements based on the model of your power supply and any mode settings:

JNP10K-PWR-AC3 Power Cable Specifications

The JNP10K-PWR-AC3 power supply operates in two modes:

  • 20-A input with 7800 W or 6000 W or 3000 W output

  • 15-A input with 7800 W or 7500 W, or 5000 W, or 2500 W output

Note:

When power cords with right angle plugs at the PSU end are selected, they must be in pairs of Right Angle Left Plugs for inputs A0 or B0 and Extended Right Angle Left Plugs for inputs A1 or B1.

See Table 12 for a list of appropriate cables.

Warning:

Do not run JNP10K-PWR-AC3 power supplies using 16-A or 20-A cables if connected to 15-A input.

CAUTION:

You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.

With right angle power cords and the baffle installed, the power cords will be exposed to hot exhaust air. The IEC C21 plugs have a temperature rating of 155C and the power cord cables have a rating of 90C.

Table 12: JNP10K-PWR-AC3 Power Cable Specifications for 20-A and 15-A Input

Locale

Cord Set Rating

Plug Standard

Spare Juniper Model Number

Graphic

Straight Plug at PSU Input

Australia and New Zealand

15 A, 250 VAC AS/NZS 3112

CBL-PWRC21-AU

Europe (except Italy, Switzerland, and United Kingdom)

16A, 250 VAC CEE 7/7

CBL-PWRC21-EU

Italy

16A, 250 VAC CEI 23-16

CBL-PWRC21-IT

North America

20A, 250 VAC

Locking NEMA L6-20P

CBL-PWRC21-US-L

NEMA 6-20P

CBL-PWRC21-US

International 16A, 250VAC

IEC-309 316P6W

CBL-PWRC21-316P6

 
North America 20A, 250 VAC

IEC-309 320P6W

CBL-PWRC21-320P6

 
Japan 20A, 250 VAC NEMA L6-20P

CBL-PWRC21-JP-L

China 16A, 250 VAC GB2099-1

CBL-PWRC21-CN

North America 20A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-NA

Europe 16A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-EU

Japan 20A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-JP

China 16A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-CN

Switzerland 16A, 250 VAC SEV1011

CBL-PWRC21-SZ

 
South Africa 16A, 250 VAC

RA SANs 164/1

CBL-PWRC21-SA

India 16A, 250VAC RA IS 1293

CBL-PWRC21-IN

United Kingdom 16A, 250 VAC BS 1363

CBL-PWRC21-UK

Israel 16A, 250 VAC

SI 32/1971

Type IL/3G

CBL-PWRC21-IL

Brazil 16A, 250 VAC

NBR 14136

Type BR/3

CBL-PWRC21-BR

Argentina 16A, 250 VAC

IRAM 2073

Type RA/3

CBL-PWRC21-AR

Right Angle Left Plug at PSU Input
USA 20A, 250 VAC NEMA L6-20P CBL-PWRC21R-US-L
USA 20A, 250 VAC NEMA 6-20P CBL-PWRC21R-US
Europe 16A, 250 VAC CEE 7/7 CBL-PWRC21R-EU
Australia 15A, 250 VAC AS/NZ 3112 CBL-PWRC21R-AU
Italy 16A, 250 VAC CEI 23-50 CBL-PWRC21R-IT
International 16A, 250 VAC

IEC 60309

316P6W

CBL-PWRC21R-316P6  
North America 16A, 250VAC

IEC 60309

320P6W

CBL-PWRC21R-320P6  
Japan 20A, 250 VAC NEMA L6-20P CBL-PWRC21R-JP-L
China 16A, 250 VAC GB2099-1 CBL-PWRC21R-CN
North America 16A, 250 VAC

IEC-60320

C20

CBL-PWRC21R-C20-NA
Europe 16A, 250 VAC

IEC 60320

C20

CBL-PWRC21R-C20-EU
Japan 20A, 250 VAC

IEC 60320

C20

CBL-PWRC21R-C20-JP
China 16A, 250 VAC

IEC 60320

C20

CBL-PWRC21R-C20-CN
Switzerland 16A, 250 VAC SEV 1011 CBL-PWRC21R-SZ  
South Africa 16A, 250 VAC SANS 164/1 CBL-PWRC21R-SA
India 16A, 250 VAC IS 1293, RA CBL-PWRC21R-IN
United Kingdom 16A, 250 VAC BS1363 CBL-PWRC21R-UK
Israel 16A, 250 VAC

SI 32/1971

TYPE IL/3G

CBL-PWRC21R-IL
Brazil 16A, 250 VAC

NBR 14136

TYP BR/3

CBL-PWRC21R-BR
Argentina 16A, 250 VAC

IRAM 2073

TYPE RA/3

CBL-PWRC21R-AR
Extended Right Angle Left Plug at PSU Input
USA 20A, 250 VAC NEMA L6-20P CBL-PWRC21RL-US-L
USA 20 A, 250 VAC NEMA 6-20P CBL-PWRC21RL-US
Europe 16A, 250 VAC CEE 7/7 CBL-PWRC21RL-EU
Australia 15A, 250 VAC AS/NZ 3112 CBL-PWRC21RL-AU
Italy 16A, 250 VAC CEI 23-50 CBL-PWRC21RL-IT
International 16A, 250 VAC

IEC-60309

316P6W

CBL-PWRC21RL-316P6  
North America 20A, 250 VAC

IEC-60309

320P6W

CBL-PWRC21RL-320P6  
Japan 20A, 250 VAC NEMA L6-20P CBL-PWRC21RL-JP-L
China 16A, 250 VAC GB2099-1 CBL-PWRC21RL-CN
North America 20A, 250 VAC

IEC-60320

C20

CBL-PWRC21RL-C20NA
Europe 16A, 250 VAC

IEC-60320

C20

CBL-PWRC21RL-C20EU
Japan 20A, 250 VAC

ICE-60320

C20

CBL-PWRC21RL-C20JP
China 16A, 250 VAC

IEC-60320

C20

CBL-PWRC21RL-C20CN
Switzerland 16A, 250 VAC SEV 1011 CBL-PWRC21RL-SZ  
South Africa 16A, 250 VAC SANS 164/1 CBL-PWRC21RL-SA
India 16A, 250 VAC IS1293, RA CBL-PWRC21RL-IN
United Kingdom 16A, 250 VAC BS 1363 CBL-PWRC21RL-UK
Israel 16A, 250 VAC

SI 32/1971

Type IL/3G

CBL-PWRC21RL-IL
Brazil 16A, 250 VAC

NBR 14136

Type BR/3

CBL-PWRC21RL-BR
Argentina 16A, 250 VAC

IRAM 2073

Type RA/3

CBL-PWRC21RL-AR

JNP10K-PWR-AC2 Power Cable Specifications

The JNP10K-PWR-AC2 power supply operates in two modes:

Warning:

Do not run JNP10K-PWR-AC2 power supplies using 16-A or 20-A cables if connected to 30-A input.

CAUTION:

You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.

Table 13: JNP10K-PWR-AC2 Power Cable Specifications for 20-A Input

Locale

Cord Set Rating

Plug Standard

Spare Juniper Model Number

Graphic

Argentina

16 A, 250 VAC

IRAM 2073 Type RA/3

CBL-JNP-SG4-AR

Australia and New Zealand

15 A, 250  VAC

AS/NZS 3112

CBL-JNP-SG4-AU

Brazil

16 A, 250 VAC

NBR 14136 Type BR/3

CBL-JNP-SG4-BR

China

16 A, 250 VAC

GB2099

CBL-JNP-SG4-CH

Europe (except Italy, Switzerland, and the United Kingdom)

20 A, 250 VAC

CEE 7/7

CBL-JNP-SG4-EU

Great Britain

13 A, 250 VAC

BS1363

CBL-JNP-SG4-UK

India

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Israel

16 A, RA, 250 VAC

SI 32/1971 Type IL/3C

CBL-JNP-SG4-IL

Italy

16 A, 250 VAC

CEI 23-16

CBL-JNP-SG4-IT

North America

20 A, 250 VAC

3-5958P4 to IEC 60320 C20

CBL-JNP-SG4-C20

16 A, 250 VAC

Locking NEMA L6-20P

CBL-JNP-SG4-US-L

NEMA 6-20P

CBL-JNP-SG4-US

15 A, 277 V

NEMA I7-20P

CBL-JNP-SG4-HVAC

South Africa

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Switzerland

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-SZ

JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input

The JNP10K-PWR-AC2 HVAC or HVDC power supplies require a high-current cable assembly when set for 30-A input. One end of the cable has an Anderson APP-400 connector, while the other end of the cable is bare wire. See Figure 6 and Table 14. These cables are separately orderable and are not shipped automatically with JNP10K-PWR-AC2 orders. An example of the right-angle cable and connector is shown in Figure 8.

For connection to AC systems, Juniper Networks provides a cable with either a NEMA 30-A connector (Figure 6) or an IEC 330P6W connector (Figure 7).

Figure 6: NEMA 30-A Locking Connector NEMA 30-A Locking Connector
Figure 7: IEC 330P6W Connector IEC 330P6W Connector
Table 14: 30-A Cabling Options

Option

Locale

Cord Set Rating

Plug Standards

Connector

Spare Juniper Model Number

HVAC/HVDC power cord

Any

30 A 400 VAC

UL 950 and IEC 60950

Anderson/straight to bare wire

CBL-PWR2-BARE

Any

30 A 400 VAC

UL 950 and IEC 60950

Anderson/right-angle to bare wire

CBL-PWR2-BARE-RA

AC power cord

Continental Europe

30 A 250 VAC

UL 950 and IEC332P6

Anderson/right-angle to IEC 332P6

CBL-PWR2-332P6W-RA

Continental Europe

30 A 250 VAC

UL 950 and IEC332P6

Anderson/straight to IEC332P6

CBL-PWR2-332P6W

Continental Europe

30 A 240 VAC

IEC330P6

Anderson/right-angle to IEC 330P6

CBL-PWR2-330P6W-RA

Continental Europe

30 A 240 VAC

IEC330P6

Anderson/straight to IEC 330P6

CBL-PWR2-330P6W

North America

30 A 250 VAC

UL 498 and CSA

Anderson/right-angle to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P-RA

North America

30 A 250 VAC

UL 498 and IEC5958P4

Anderson/straight to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P

AC jumper power cord

Any

30 A 400 VAC

UL and CSA

Anderson/straight to Anderson

CG-CBL-APP-400-02

Figure 8: Right-Angle, Bare Cable with Anderson Connector Right-Angle, Bare Cable with Anderson Connector
  1

Black wire –“+” or “-” for HVDC and “Hot or neutral” for AC

  3

White wire – “+” or “-” for HVDC and “Hot or neutral” for AC

  2

Green wire - Ground

 

JNP10K-PWR-DC2 Power Supply

The JNP10K-PWR-DC2 power supply provides two power supplies in a single housing that accepts either 60 A or 80 A using four redundant input power feeds. The two internal power supplies (PS_0 and PS_1) each have redundant input feeds: A0 and/or B0 for PS_0 and A1 and/or B1 for PS_1. You configure the input using a set of three DIP switches on the power supply faceplate that sets the combined output power for both internal power supplies. The output depends on the settings of these DIP switches. See Table 15 and Figure 9.

Table 15: DIP Switch Settings for JNP10K-PWR-DC2 Power Supplies

INP0(Switch 1)

INP1(Switch 2)

H/L (High Input 80 A/Low Input 60 A)

Output Power

On

On

On (80 A)

5500 W

On

On

Off (60 A)

4400 W

On

Off

On (80 A)

2750 W

Off

On

On (80 A)

2750 W

On

Off

Off (60 A)

2200 W

Off

On

Off (60 A)

2200 W

The JNP10K-PWR-DC2 power supply requires a dedicated circuit breaker for each input DC feed. The DC breaker shall be rated for 80A DC with medium delay.

Figure 9: JNP10K-PWR-DC2 Power Supply JNP10K-PWR-DC2 Power Supply

The JNP10K-PWR-DC2 power supply has internal fans that contribute to chassis cooling. Consequently, all three power supplies must be present in a running chassis to have adequate airflow. While all power supplies are required to be present in the chassis, they do not all need to be connected to power. If a power supply is installed in a slot but not connected to a power source, it draws power from the chassis to power the internal fans in the power supplies.

Warning:

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be connected to earth ground permanently to ground the chassis adequately and protect the operator from electrical hazards.

CAUTION:

Before you begin installing the router, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the router.

JNP10K-PWR-DC2 Power Specifications

Table 16 lists the power specifications for the high-voltage direct current (HVDC) power supply used in MX10004 routers.

Table 16: Power Specifications for the JNP10K-PWR-DC2 Power Supply

Item

Specifications

DC input voltage

  • Minimum operating voltage: –40 VDC

  • Nominal operating voltage: –48 VDC

  • Operating voltage range: –40 VDC through –72 VDC

DC input current rating

  • 76-A maximum at minimum operating voltage (-40 VDC) with 80-A DIP switch setting and 5500-W output load

  • 64-A maximum at nominal operating voltage (–48 VDC) with 80-A DIP switch setting and 5500-W output load

  • 60-A maximum at minimum operating voltage (-40 VDC) with 60-A DIP switch setting and 4400-W output load

  • 50-A maximum at nominal operating voltage (-48 VDC) with 60-A DIP switch setting and 4400-W output load

Output power

  • 2200 W for low-input (60-A) single feed

  • 4400 W for low-input (60-A) dual feed

  • 2750 W for high-input (80-A) single feed

  • 5500 W for high-input (80-A) dual feed

Table 17 shows the physical specifications for a JNP10K-PWR-DC2 power supply.

Table 17: Physical Specifications of a JNP10K-PWR-DC2 Power Supply

Specification

Value

Height

3.5 in. (8.89 cm)

Width

3.6 in. (9.14 cm)

Depth

16.05 in. (40.77 cm)

Weight

8.1 lb (3.67 kg)

JNP10K-PWR-DC2 Power Supply LEDs

A JNP10K-PWR-DC2 power supply has four LEDs on its faceplate: 1, 2, OK, and the symbol indicating a fault, !. These LEDs display information about the status of the power supply. See Figure 10.

Figure 10: LEDs on a JNP10K-PWR-DC2 Power Supply LEDs on a JNP10K-PWR-DC2 Power Supply
  1

! Fault

  3

2 Power source input 1

  2

OK Power OK

  4

1 Power source input 0

You can find out the version of the firmware installed in the power supply from the output of show system firmware command. Table 18 describes the LEDs on a JNP10K-PWR-DC2 power supply if the firmware installed in the power supply is 300.300.208.208.304 or higher. Table 19 describes the LEDs on a JNP10K-PWR-DC2 power supply if the firmware installed in the power supply is lower than 300.300.208.208.304.

Table 18: LEDs on a JNP10K-PWR-DC2 Power Supply (with 300.300.208.208.304 or higher firmware installed in it)

Feed 0

Feed 1

State of the Power Supply Switch

LED 1

LED 2

OK LED

! LED

Off

Off

Off

Orange

Orange

Off

Red

A or B

Off

Off

Green—Blinking

Orange

Off

Red

A and B

Off

Off

Green

Orange

Off

Red

Off

A or B

Off

Orange

Green—Blinking

Off

Red

A or B

A or B

Off

Green—Blinking

Green—Blinking

Off

Red—Blinking

A and B

A or B

Off

Green

Green—Blinking

Off

Red—Blinking

Off

A and B

Off

Orange

Green

Off

Red

A or B

A and B

Off

Green—Blinking

Green

Off

Red—Blinking

A and B

A and B

Off

Green

Green

Off

Off

Off

Off

On

Orange

Orange

Off

Red

A or B

Off

On

Green—Blinking

Orange

Green

Red

A and B

Off

On

Green

Orange

Green

Red

Off

A or B

On

Orange

Green—Blinking

Green

Red

A or B

A or B

On

Green—Blinking

Green—Blinking

Green

Red—Blinking

A and B

A or B

On

Green

Green—Blinking

Green

Red—Blinking

Off

A and B

On

Orange

Green

Green

Red

A or B

A and B

On

Green—Blinking

Green

Green

Red—Blinking

A and B

A and B

On

Green

Green

Green

Off

Table 19: LEDs on a JNP10K-PWR-DC2 Power Supply (with firmware lower than 300.300.208.208.304 installed in it)

LED

Color

State

Description

1 (INP0 in CLI output) or 2 (INP1 in CLI output)

Green

Solid

The DC power is within normal operating range (-40 VDC to -72 VDC).

Orange

Solid

The DC power input voltage is not within normal operating range.

Unlit

Off

The power supply is switched off.

OK (Power OK)

Green

Solid

The DC power output is within normal operating range.

Orange

Blinking

The power supply output is out of the power limits.

! (Fault)

Red

Solid

The power supply has failed and must be replaced.

Unlit

Off

The power supply is functioning normally. Or, only one input is powered and the enable switch for the input that is not powered is set to ON. See Install a JNP10K-PWR-DC2 Power Supply for more information about the enable switches.

Note:

If the 1 or 2 and the OK LED are unlit, the power cables are not installed properly or the power supply has failed.

If the 1 or 2 LED is lit green and the OK LED is unlit, the power supply is not installed properly or the power supply has an internal failure.

If the ! LED is blinking, add a power supply to balance the power demand and supply.

MX10004 Grounding Cable and Lug Specifications

The router must be adequately grounded before power is connected to ensure proper operation and to meet safety and electromagnetic interference (EMI) requirements. To ground an MX10004 chassis, connect a grounding cable to earth ground and then attach it to the chassis grounding point on the rear of the chassis beneath.

You must install the MX10004 in a restricted-access location and ensure that the chassis is always properly grounded. The MX10004 has a two-hole protective grounding terminal provided on the chassis. Under all circumstances, use this grounding connection to ground the chassis. For AC-powered systems, you must also use the grounding wire in the AC power cord along with the two-hole grounding lug connection. This tested system meets or exceeds all applicable EMC regulatory requirements with the two-hole protective grounding terminal.

Warning:

To comply with GR-1089 requirements, all intrabuilding copper cabling used for SFP+, QSFP+, and higher must be shielded and grounded at both ends.

CAUTION:

Before router installation begins, a licensed electrician must attach a cable lug to the grounding cables that you supply. See Connect the MX10004 Router to Earth Ground. A cable with an incorrectly attached lug can damage the router.

Before you connect the router to earth ground, review the following information:

  • Two threaded inserts (PEM nuts) are provided on the lower rear of the chassis to connect the router to earth ground. The protective earthing terminals are spaced at 0.63 in. (16 mm) centers.

  • The grounding lug required is a Panduit LCD6-10A-L or equivalent (provided). The grounding lug accommodates 6 AWG (13.3 mm²) stranded wire. If one or more JNP10K-PWR-DC2 power supplies are installed in the chassis and set for high input (80 A), use the Panduit LCD4-14A-L or equivalent (provided). This lug accommodates 4 AWG (21.1 mm²) stranded wire. The 4 AWG (21.1 mm²) stranded wire should be rated 90° C or as specified by the local electrical code.

  • The grounding cable that you provide for an MX10004 must be the same size as, or heavier than, the input wire of each power supply. Minimum recommendations are 6 AWG (13.3 mm²) stranded copper wire, Class B; 90° C wire, or as specified by local code.