PTX10001-36MR Site Guidelines and Requirements
PTX10001-36MR Environmental Requirements and Specifications
The PTX10001-36MR must be installed in a rack or cabinet. It must be housed in a dry, clean, well-ventilated, and temperature-controlled environment.
Follow these environmental guidelines:
The site must be as dust-free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the PTX10001-36MR cooling system.
Maintain ambient airflow for normal PTX10001-36MR operation. If the airflow is blocked or restricted, or if the intake air is too warm, the chassis might overheat, leading to the PTX10001-36MR temperature monitor shutting down the router to protect the hardware components.
Table 1 provides the required environmental conditions for normal PTX10001-36MR operation.
Description |
Tolerance |
---|---|
Altitude |
No performance degradation up to 6,562 feet (2000 meters). |
Relative humidity |
|
Temperature |
|
Seismic |
Designed to comply with Zone 4 earthquake requirements per NEBS GR-63-CORE, Issue 3. |
Install the PTX10001-36MR only in restricted areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.
General Site Guidelines
Efficient device operation requires proper site planning and maintenance. It also requires proper layout of the equipment, rack or cabinet, and wiring closet.
To plan and create an acceptable operating environment for your device and prevent environmentally caused equipment failures:
Keep the area around the chassis free from dust and conductive material, such as metal flakes.
Follow the prescribed airflow guidelines to ensure that the cooling system functions properly. Ensure that the exhaust from other equipment does not blow into the intake vents of the device.
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent damaging the equipment. Static discharge can cause components to fail completely or intermittently over time.
Install the device in a secure area, so that only authorized personnel can access the device.
PTX10001-36MR Chassis Grounding Cable and Lug Specifications
For installations that require a separate grounding conductor to the chassis, the PTX10001-36MR must be adequately grounded before power is connected to ensure proper operation and to meet safety and electromagnetic interference (EMI) requirements. To ground a PTX10001-36MR, connect a grounding cable to earth ground and then attach it to the chassis grounding points.
The device is a pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal provided on the chassis in addition to the grounding pin of the power supply cord. This separate protective earthing terminal must be permanently connected to earth ground for installations that require a separate grounding conductor to the chassis.
To comply with GR-1089 requirements, all intrabuilding copper cabling used for transceiver ports must be shielded and grounded at both ends.
Before device installation begins, a licensed electrician must attach a cable lug to the grounding cables that you supply. See Connect the PTX10001-36MR to Ground. A cable with an incorrectly attached lug can damage the PTX10001-36MR.
Before connecting the PTX10001-36MR to earth ground, review the following information:
The grounding lug required is a Panduit LCD6-14AH-L or equivalent (not provided).
The grounding cable that you provide for a PTX10001-36MR must be the same size or heavier than the input wire of each power supply. Minimum recommendations are 8 AWG (8.4 mm²) stranded wire, 90° C wire, or as permitted by local code.
PTX10001-36MR Clearance Requirements for Airflow and Hardware Maintenance
When planning the site for a PTX10001-36MR installation, you must allow sufficient clearance around the installed chassis (see Figure 1).
Follow these guidelines:
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See PTX10001-36MR Cooling System for more information about the airflow through the chassis.
If you are mounting a PTX10001-36MR in a rack with other equipment, ensure that the exhaust from other equipment does not blow into the intake vents of the chassis.
You must leave at least 24 in. (61 cm) both in front of and behind the PTX10001-36MR for service personnel to remove and install hardware components. You must leave adequate space at the front and back of the PTX10001-36MR. NEBS GR-63 recommends that you allow at least 30 in. (76.2 cm) in front of the rack or cabinet and 24 in. (61 cm) behind the rack.
PTX10001-36MR Physical Specifications
Table 2 lists the physical specifications for the PTX10001-36MR chassis.
Product SKU |
Weight |
Height |
Width |
Depth |
---|---|---|---|---|
PTX10001-36MR |
With all power supplies and fans installed: 39.7 lb (18.0 kg) |
1.72 in. (4.3 cm) |
17.36 in. (44.09 cm) |
25.89 in. (65.76 cm) |
Site Electrical Wiring Guidelines
Table 3 describes the factors you must consider while planning the electrical wiring at your site.
You must provide a properly grounded and shielded environment and use electrical surge-suppression devices.
Avertissement Vous devez établir un environnement protégé et convenablement mis à la terre et utiliser des dispositifs de parasurtension.
Site Wiring Factor |
Guidelines |
---|---|
Signaling limitations |
If your site experiences any of the following problems, consult experts in electrical surge suppression and shielding:
|
Radio frequency interference |
To reduce or eliminate RFI from your site wiring, do the following:
|
Electromagnetic compatibility |
If your site is susceptible to problems with electromagnetic compatibility (EMC), particularly from lightning or radio transmitters, seek expert advice. Strong sources of electromagnetic interference (EMI) can cause:
|
PTX10001-36MR Rack Requirements
The PTX10001-36MR chassis is designed to be installed in two-post or four-post racks.
Rack requirements consist of:
Rack type
Mounting bracket hole spacing
Rack size and strength
Table 4 provides the rack requirements and specifications for the PTX10001-36MR.
Rack Requirement |
Guidelines |
---|---|
Rack type |
Use a two-post or a four-post rack. You can mount the device on any two-post or four-post rack that provides bracket holes or hole patterns spaced at 1-U (1.75 in. or 4.45 cm) increments and that meets the size and strength requirements to support the weight. A U is the standard rack unit defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310–D) published by the Electronics Components Industry Association (http://www.ecianow.org/). |
Mounting bracket hole spacing |
The holes in the mounting brackets are spaced at 1-U (1.75 in. or 4.45 cm) increments, so that the PTX10001-36MR can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
|
Rack connection to building structure |
|
PTX10001-36MR Cabinet Requirements
You can mount the PTX10001-36MR in an enclosure or cabinet that contains a four-post 19-in. open rack as defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310-D) published by the Electronics Industry Association.
Cabinet requirements consist of:
Cabinet size and clearance
Cabinet airflow requirements
Table 5 provides the cabinet requirements and specifications for the PTX10001-36MR.
Cabinet Requirement |
Guidelines |
---|---|
Cabinet size and clearance |
The minimum cabinet size for accommodating a PTX10001-36MR device is 36 in. (91.4 cm) deep. Large cabinets improve airflow and reduce the chance of overheating. |
Cabinet airflow requirements |
When you mount the device in a cabinet, ensure that ventilation through the cabinet is sufficient to prevent overheating.
|