PTX5000 Power Planning
Calculating PTX5000 Power Consumption
Use the information in this topic to determine the power consumption for your router.
Starting in Junos OS Release 14.1, new power management features in Junos OS for PTX5000 ensure that the chassis power requirements do not exceed the power available to the PTX5000.
Power management ensures that high-priority FPCs continue to receive power when the system does not have sufficient power to keep all the FPCs online.
If a power supply fails, Junos OS can bring low-priority FPCs offline to allow high-priority FPCs to remain online.
For more information about configuring power management on the PTX5000, see Understanding Power Management on the PTX5000 in the Chassis-Level User Guide.
- Power Requirements for PTX5000 Components
- Calculating Power Consumption for your Configuration
- Calculating System Thermal Output
Power Requirements for PTX5000 Components
Table 1 describes the output power requirements for the required and optional FRUs for the PTX5000. The power requirements vary depending on the ambient air temperature for your installation.
The power requirements listed below are accurate for estimating typical power consumption at different ambient temperatures. However, Junos OS reserves additional power in the power budget for base system components—the host subsystem, the fan trays, and the SIBs. When planning for the minimum required PSMs, this power reserve must be included.
You can use the interactive Power Calculator application at https://pathfinder.juniper.net/power-calculator/ to determine the number of PSMs required to support your system configuration. The Power Calculator application requires Juniper.net login credentials.
Component |
25° C (77° F) Ambient Temperature |
40° C (104° F) Ambient Temperature |
---|---|---|
Host subsystem with RE-DUO-C2600-16G Routing Engine, CB-PTX Control Board, and CCG |
130 W |
150 W |
Host subsystem with RE-PTX-X8-64G Routing Engine, CB2-PTX Control Board, and CCG |
182 W |
187 W |
FAN-PTX-V vertical fan tray |
80 W |
370 W |
FAN-PTX-H horizontal fan tray |
240 W |
950 W |
FAN3-PTX-H horizontal fan tray |
330 W |
900 W |
SIB-I-PTX5008 SIBs (total power requirements for 9 SIBs) |
380 W |
450 W |
SIB2-I-PTX5K SIBs (total power requirements for 9 SIBs) |
450 W |
510 W |
SIB3-PTX5K SIBs (total power requirements for 9 SIBs) |
1170 W |
1170 W |
FPCs | ||
FPC-PTX-P1-A |
420 W |
500 W |
FPC2-PTX-P1A |
820 W |
900 W |
FPC3-PTX-U2 |
494 W |
511 W |
FPC3-PTX-U3 |
754 W |
777 W |
PICs | ||
P1-PTX-24-10GE-SFPP |
60 W |
66 W |
P1-PTX-24-10G-W-SFPP |
82 W |
100 W |
P2-10G-40G-QSFPP |
100 W |
115 W |
P3-24-U-QSFP28 |
131 W |
134 W |
P1-PTX-2-40GE-CFP |
27 W |
32 W |
P3-15-U-QSFP28 |
119 W |
123 W |
P1-PTX-2-100GE-CFP |
70 W |
73 W |
P2-100GE-CFP2 |
60 W |
70 W |
P2-100GE-OTN |
135 W |
160 W |
P1-PTX-2-100G-WDM |
250 W |
264 W |
Calculating Power Consumption for your Configuration
By using the information provided in Table 1, you can calculate the power consumption for your configuration.
The examples below show the power requirement calculations for different types of configurations:
All the examples below use RE-PTX-X8-64G Routing Engines, CB2-PTX Control Boards, FAN3-PTX-H horizontal fan trays, and SIB3-PTX5K SIBs.
This example shows the calculation for a non-redundant base configuration with no FPCs or PICs at 25° C (77° F) ambient temperature:
1 host subsystem + 1 vertical fan tray + 2 horizontal fan trays + SIBs = output power in watts 182 W + 80 W + 2(330 W) + 1170 W = 2092 W Output power in watts / power supply efficiency = power consumption in watts 2092 W / 0.9 = 2324.4 W
This example shows the calculation for a redundant base configuration with four FPC3-PTX-U3 FPCs and eight P3-15-U-QSFP28 PICs at 25° C (77° F) ambient temperature:
2 host subsystems + 1 vertical fan tray + 2 horizontal fan trays + SIBs + 4 FPC3-PTX-U3 FPCs + 8 P3-15-U-QSFP28 PICs = output power in watts 2(182 W) + 80 W + 2(330 W) + 1170 W + 4(754 W) + 8(119 W) = 6242 W Output power in watts / power supply efficiency = power consumption in watts 6242 W / 0.9 = 6935.6 W
This example shows the calculation for a redundant base configuration with eight FPC3-PTX-U3 FPCs and sixteen P3-15-U-QSFP28 PICs at 40° C (104° F) ambient temperature:
2 host subsystems + 1 vertical fan tray + 2 horizontal fan trays + SIBs + 8 FPC3-PTX-U3 FPCs + 16 P3-15-U-QSFP28 PICs = output power in watts 2(187 W) + 370 W + 2(900 W) + 1170 W + 8(777 W) + 16(123 W) = 11898 W Output power in watts / power supply efficiency = power consumption in watts 11898 W / 0.9 = 13,220 W
Calculating System Thermal Output
After you have calculated the power consumption for your configuration, you can use that information to determine the system thermal output (BTUs per hour). To do so, multiply the power consumption in watts by 3.41.
For example, above we calculated the power consumption for a redundant base configuration with eight FPC3-PTX-U3 FPCs and sixteen P3-15-U-QSFP28 PICs at 40° C (104° F) ambient temperature to be 13,220 W. Using that information we can calculate the system thermal output for the configuration:
Power consumption in watts * 3.41 = system thermal output in BTU/hr 13220 W * 3.41 = 45080.2 BTU/hr
Understanding Normal-Capacity Power System Power Zones
PSM Slots
There is no power zoning in the High Capacity power system.
The PTX5000 normal-capacity power system has up to eight power supply modules (PSMs), located in the lower front of the chassis below the FPC card cage. The PSMs insert into one of four slots—labeled 0 through 3—located in the rear of each PDU labeled PDU0 and PDU1. For full power redundancy, a minimum number of PSMs must be installed and fully operational:
For full power redundancy, six PSMs are required to support up to four FPCs.
Zone 0—One PSM0 in each PDU
Zone 1—One PSM1 in each PDU
Zone 2—One PSM2 or PSM3 in each PDU
For full power redundancy, all eight PSMs are required to support five or more FPCs:
Zone 0—One PSM0 in each PDU
Zone 1—One PSM1 in each PDU
Zone 2—Both PSM2 and PSM3 in each PDU
Normal-Capacity Power Zones and PSM Fault Tolerance
The normal-capacity power system contains three power zones. Table 2 describes which components are powered by each zone and PSM. Table 3, Table 4, and Table 5 describe the fault tolerance for each zone.
Zone |
PSM |
Component |
---|---|---|
0 |
0 |
Fan trays |
1 |
1 |
The craft interface and the following components installed in the rear card cage: Routing Engines, Control Boards, CCGs, and SIBs.
|
2 |
2 |
Any four FPCs in slots FPC0 through FPC7 |
3 |
Any four FPCs in slots FPC0 through FPC7 |
Nonredundant Configuration |
Redundant Configuration |
|
---|---|---|
PDU0 |
PDU1 |
|
One PSM0 in either PDU can provide power to all fan trays. |
PSM0 is required for full power redundancy. If PSM0 in PDU0 is powered off or fails, the configuration becomes nonredundant. |
PSM0 is required for full power redundancy. If PSM0 in PDU1 is powered off or fails, the configuration becomes nonredundant. |
If the nonredundant PSM in this zone is not powered on, the fan trays are not powered on, and the PTX5000 will not be powered on. |
If neither PSM in this zone is powered on, the fan trays are not powered on, and the PTX5000 will not be powered on. |
|
If the nonredundant PSM in this zone fails, the fan trays are not powered on, which will cause the PTX5000 to be powered off. |
If both PSMs in this zone fail, the fan trays are not powered on, which will cause the PTX5000 to be powered off. |
Nonredundant Configuration |
Redundant Configuration |
|
---|---|---|
PDU0 |
PDU1 |
|
One PSM1 in either PDU can provide power to the craft interface, both host subsystems, both CCGs, and all nine SIBs. |
PSM1 in PDU0 is required for full power redundancy. If PSM1 in PDU0 is powered off or fails, the configuration becomes nonredundant. |
PSM1 in PDU1 is required for full power redundancy. If PSM1 in PDU1 is powered off or fails, the configuration becomes nonredundant. |
If the nonredundant PSM in this zone is not powered on, the craft interface, host subsystems. CCGs, and SIBs are not powered on. |
If PSM1 in PDU0 and PSM1 in PDU1 are not online, the craft interface, host subsystems, CCGs, and SIBs are not powered on. |
|
If the nonredundant PSM in this zone fails, the craft interface, host subsystems. CCGs, and SIBs are powered off. |
If PSM1 in PDU0 and PSM1 in PDU1 both fail, the craft interface, host subsystems, CCGs, and SIBs are powered off. |
Number of FPCs |
Nonredundant Configuration |
Redundant Configuration |
|
---|---|---|---|
PDU0 |
PDU1 |
||
Up to four FPCs The PSMs must be in different PDUs for full power redundancy. |
One PSM2 or PSM3 in either PDU can provide nonredundant power. PSM2 and PSM3 in the same PDU are nonredundant. |
Two PSMs in this zone are required for full power redundancy. One PSM2 or PSM3 must be installed in PDU0 and fully functional. If PSM2 or PSM3 in PDU0 is powered off or fails, the configuration becomes nonredundant. |
Two PSMs in this zone are required for full power redundancy. One PSM2 or PSM3 must be installed in PDU1 and fully functional. If PSM2 or PSM3 in PDU1 is powered off or fails, the configuration becomes nonredundant. |
Five to eight FPCs |
Two PSMs, one in each PDU can provide nonredundant power. PSM2 and PSM3 in the same PDU is nonredundant. CAUTION: Three PSMs are nonredundant. |
All four PSMs in this zone are required for full power redundancy. PSM2 and PSM3 in PDU0 must be present and fully functional. If PSM2 or PSM3 in PDU0 is powered off or fails, the configuration becomes nonredundant. |
All four PSMs in this zone are required for full power redundancy. PSM2 and PSM3 in PDU1 must also be present and fully functional. If PSM2 or PSM3 in PDU0 is powered off or fails, the configuration becomes nonredundant. |
If all four PSMs in this zone fail, all FPCs are powered off. |