Maintaining the PTX5000 AC Power System

Maintaining the PTX5000 AC Power System

Purpose

For optimum performance, verify the condition of the power distribution units (PDUs), power supply modules (PSMs), AC power cords, and grounding cables.

Action

On a regular basis:

  • Periodically inspect the site to ensure that the grounding and AC power cords connected to the PTX5000 are securely in place and that no moisture is accumulating near the PTX5000. To review grounding and site wiring requirements for the PTX5000, see PTX5000 Chassis Grounding Cable and Lug Specifications and Site Electrical Wiring Guidelines.

  • Check the status of the PDUs by issuing the show chassis environment pdu command.

  • Make sure that the AC power cords are arranged so that they do not obstruct access to other router components.

  • Routinely check the status LEDs on the PDU and PSM faceplates and the craft interface to verify that the power system is functioning normally.

    For more information about the PDU and PSM LEDs, see PTX5000 AC Power Distribution Unit LEDs and PTX5000 AC Power Supply Module LEDs.

  • Check the red and yellow alarm LEDs and the LCD display on the craft interface. PDU and PSM failure or removal triggers an alarm that causes one or both of the LEDs to light and an error message to appear on the LCD display. You can display the associated error messages by issuing the following CLI command:

    For a list of possible alarm messages, see Troubleshooting the PTX5000 Power System.

  • The power system requires an unobstructed airflow at both the front and rear of the chassis. Periodically check the site to ensure that both the air intake at the bottom front of the chassis and the exhaust from the PSM faceplates are unobstructed.

  • To check the power usage in watts for all PDUs and PSMs, issue the show chassis power command .

    Issue the show chassis power detail command to check the power usage in watts for hardware components such as FPCs, fan trays, Routing Engine and Control Board, and SIB, CCG, and craft interface.

Replacing a PTX5000 Three-Phase Delta AC PDU

Removing a PTX5000 Three-Phase Delta AC PDU

The PTX5000 has two redundant, load-sharing PDUs. Each PDU is hot-insertable and hot-removable. The PDU weighs 51.2 lb (23.2 kg).

To remove a three-phase delta PDU:

  1. Switch off the customer-site circuit breakers to the PDU being removed.
  2. Switch the circuit breaker and the power OUTPUT switch located on the faceplate of the PDU to the off (O) position.
  3. Disconnect the AC power cord from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process. Verify that the 200-240 V ~ 60 A 50-60 Hz LED on the PDU faceplate is off.
  5. Remove the power supply modules (PSMs) in the front of the chassis from the PDU to be removed (see Figure 1).
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Loosen the captive screw on the PSM ejector handle.
    3. Grasp the ejector handle and pull to eject the PSM.
    4. Slide the PSM halfway out of the chassis. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    5. Repeat these steps for the remaining PSMs in the PDU.
    Figure 1: Removing the AC Power Supply ModulesRemoving the AC Power Supply Modules
  6. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis at the back of the PTX5000.
  7. Open the door of the metal wiring compartment.
  8. Disconnect the wires from the AC terminal block on the three-phase delta AC power supply (Figure 2). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal or grounding point screw, and remove each wire from the input terminal or grounding point.
    1. Remove the wire labeled L3 from the L3 input terminal.
    2. Remove the wire labeled L2 from the L2 input terminal.
    3. Remove the wire labeled L1 from the L1 input terminal.
    4. Remove the wire labeled GND from the grounding point.
    Figure 2: Disconnecting AC Power Wires from a Three-Phase Delta AC Power SupplyDisconnecting AC Power Wires from a Three-Phase Delta AC Power Supply
  9. Using a number 2 Phillips (+) screwdriver, loosen the captive screws that secure the metal retaining bracket and AC power cord to the PDU. While gently removing the wires of the AC power cord from the wiring compartment, remove the metal retaining bracket and AC power cord from the PDU. See Figure 3.
    Figure 3: Removing the Metal Retaining Bracket and AC Power CordRemoving the Metal Retaining Bracket and AC Power Cord
  10. Loosen the four captive screws attaching the front PDU handle to the PDU and chassis.
  11. Grasp the front PDU handle on the PDU faceplate and pull firmly down toward you. Slide the PDU halfway out of the chassis until you can reach the installation handle located on top of the PDU. (See Figure 5).
    CAUTION:

    Each PDU weighs approximately 63.3 lb (28.7 kg). Be prepared to support the full weight of the PDU as you remove it from the PTX5000.

  12. Use the installation handle to slide the PDU completely out of the chassis.
  13. Use the captive screws on the metal retaining bracket to reattach it to the PDU being removed.
Warning:

Do not touch the power connectors on the rear of the PDU. They can contain dangerous voltages.

CAUTION:

Do not leave a PDU slot empty for more than a short time while the PTX5000 is operational. For proper airflow, the PDU must remain in the chassis or a blank panel must be used in an empty slot.

Figure 4: Three-Phase Delta AC Power SupplyThree-Phase Delta AC Power Supply
  1

Top installation handle

  5

Circuit breaker

  2

Front installation handle

  6

Metal wiring compartment

  3

Output power switch

  7

Metal wiring compartment door

  4

Air exhaust ventilation

  8

Metal retaining bracket

Figure 5: Removing a Three-Phase Delta AC PDURemoving a Three-Phase Delta AC PDU

Installing a PTX5000 Three-Phase Delta AC PDU

To install a three-phase delta AC PDU:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Switch the circuit breaker and the power OUTPUT switch located on the faceplate of the PDU to the off (O) position.
  3. Grasp the front installation handle and top installation handle, and insert the PDU into the PDU slot.
  4. Using both hands, slide the PDU into the chassis until you feel resistance.
  5. Push the front installation handle up toward the PDU, and secure the handle with the captive screws.
  6. Using a number 2 Phillips (+) screwdriver, loosen the four captive screws that secure the metal retaining bracket to the newly installed PDU. Remove the metal retaining bracket from the PDU.
  7. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws on the metal AC wiring compartment of the replacement PDU. Open the metal door of the metal AC wiring compartment.
  8. Using a number 2 Phillips (+) screwdriver, use the four captive screws on the metal retaining bracket to secure the AC power cord to the PDU.
    Figure 6: Connecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Delta PDUConnecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Delta PDU
  9. Connect the wires to the AC terminal block on the three-phase delta AC PDU (Figure 7). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal or grounding point screw, insert each wire into the grounding point or input terminal, and tighten the screw.
    1. Insert the wire labeled GND into the grounding point.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    Figure 7: Connecting Grounding and AC Power Wires to a Three-Phase Delta AC Power SupplyConnecting Grounding and AC Power Wires to a Three-Phase Delta AC Power Supply
  10. Verify that the AC power and grounding wiring connections are correct.
  11. Using a number 2 Phillips (+) screwdriver, tighten the two captive screws on the metal AC wiring compartment.
  12. Verify that the AC power cord is not touching or blocking access to PTX5000 components, and that it does not drape where people could trip on it.
  13. Reconnect the AC power cord to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  14. Switch on the customer-site circuit breaker to the PDU.
  15. Verify that the 200-240 V ~ 60 A 50-60 Hz LED on the PDU faceplate is lit steadily, indicating that the PDU is receiving voltage.
  16. Reinstall the PSMs into the PDU.
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Place one hand underneath the PSM to support it and slide it into the PSM slot.
    3. Push the ejector handle toward the PSM, and tighten the captive screw on the ejector handle to secure it to the PSM.
    4. Repeat these steps for the other PSMs in the PDU.
  17. Move the circuit breaker on the PDU to the on (|) position.
  18. Verify that the CB ON LED on the PDU faceplate is lit steadily.
  19. Move the power OUTPUT switch on the PDU to the on (|) position.
  20. Verify that the AC IN LED and DC IN LED on the faceplate of each PSM in the PDU are lit steadily, indicating that each PSM is receiving power. Verify that the FAULT LED is off.
  21. Verify that the PDU OK LED on the PDU faceplate is lit steadily, indicating that the PDU is functioning normally.
Figure 8: Installing a Three-Phase Delta AC PDUInstalling a Three-Phase Delta AC PDU

Replacing a PTX5000 Three-Phase Delta AC PDU Power Cord

Removing a PTX5000 Three-Phase Delta AC PDU Power Cord

To remove a three-phase delta PDU power cord:

  1. Switch off the customer-site circuit breakers to the PDU being removed.
  2. Move the circuit breaker and power OUTPUT switch located on the faceplate of the PDU to the off (O) position.
  3. Disconnect the AC power cord from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process. Verify that the 200-240 V ~ 60 A 50-60 Hz LED on the PDU faceplate is off.
  5. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis at the back of the PTX5000.
  6. Open the door of the metal wiring compartment. Disconnect the wires from the AC terminal block on the three-phase delta AC power supply (Figure 9). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal or grounding point screw, and remove each wire from the input terminal or grounding point.
    1. Remove the wire labeled L3 from the L3 input terminal.
    2. Remove the wire labeled L2 from the L2 input terminal.
    3. Remove the wire labeled L1 from the L1 input terminal.
    4. Remove the wire labeled GND into the grounding point.
    Figure 9: Disconnecting AC Power Wires from a Three-Phase Delta AC PDUDisconnecting AC Power Wires from a Three-Phase Delta AC PDU
  7. Using a number 2 Phillips (+) screwdriver, loosen the captive screws that secure the metal retaining bracket and AC power cord to the PDU. While gently removing the wires of the AC power cord from the wiring compartment, remove the metal retaining bracket and AC power cord from the PDU. See Figure 10.
    Figure 10: Removing the Metal Retaining Bracket and AC Power CordRemoving the Metal Retaining Bracket and AC Power Cord
  8. Unscrew the retaining nut from the AC power cord, and detach the AC power cord from the metal retaining bracket.
    Note:

    Reserve the retaining nut to attach the metal retaining bracket to the replacement AC power cord.

    Figure 11: Removing the Metal Retaining Bracket from the AC Power Cord Removing the Metal Retaining Bracket from the AC Power Cord
      1

    Retaining nut

      3

    Three-phase delta AC power cord

      2

    Metal retaining bracket

     

Installing a PTX5000 Three-Phase Delta AC PDU Power Cord

To install a three-phase delta AC power cord:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Switch the circuit breaker and power OUTPUT switch on the PDU to the off (O)position.
  3. Gently push the AC power cord wires through the hole in the metal retaining bracket. Screw the retaining nut onto the AC power cord to secure the metal retaining bracket to the replacement AC power cord.
    Figure 12: Attaching the Metal Retaining Bracket to the Three-Phase Delta AC Power Cord Attaching the Metal Retaining Bracket to the Three-Phase Delta AC Power Cord
      1

    Retaining nut

      3

    Three-phase delta AC power cord

      2

    Metal retaining bracket

     
  4. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws on the metal AC wiring compartment. Open the metal door of the metal AC wiring compartment.
  5. Gently push the wires of the AC power cord into the area for the metal retaining bracket, and pull the wires to the left toward the metal AC wiring compartment.
  6. Using a number 2 Phillips (+) screwdriver, use the four screws on the metal retaining bracket to secure the AC power cord to the PDU.
    Figure 13: Connecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Delta PDUConnecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Delta PDU
  7. Connect the wires to the AC terminal block on the three-phase delta AC PDU (Figure 14). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal or grounding point screw, insert each wire into the grounding point or input terminal, and tighten the screw.
    1. Insert the wire labeled GND into the grounding point.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    Figure 14: Connecting Grounding and AC Power Wires to a Three-Phase Delta AC Power SupplyConnecting Grounding and AC Power Wires to a Three-Phase Delta AC Power Supply
  8. Verify that the AC power and grounding wiring connections are correct.
  9. Using a number 2 Phillips (+) screwdriver, tighten the two captive screws on the metal AC wiring compartment.
  10. Verify that the AC power cord is not touching or blocking access to PTX5000 components, and that it does not drape where people could trip on it.
  11. Reconnect the AC power cord to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  12. Switch on the customer-site circuit breaker to the PDU.
  13. Verify that the 200-240 V ~ 60 A 50-60 Hz LED on the PDU faceplate is lit steadily, indicating that the PDU is receiving voltage.
  14. Move the circuit breaker on the PDU to the on (|) position.
  15. Verify that the CB ON LED on the PDU faceplate is lit steadily.
  16. Move the power OUTPUT switch on the PDU to the on (|) position.
  17. Verify that the AC IN LED and DC IN LED on the faceplate of each PSM in the PDU are lit steadily, indicating that each PSM is receiving power. Verify that the FAULT LED is off.
  18. Verify that the PDU OK LED on the PDU faceplate is lit steadily, indicating that the PDU is functioning normally.

Replacing a PTX5000 Three-Phase Wye AC PDU

Removing a PTX5000 Three-Phase Wye AC PDU

The PTX5000 has two redundant, load-sharing PDUs. Each PDU is hot-insertable and hot-removable. The PDU weighs 51.2 lb (23.2 kg).

To remove a three-phase wye PDU:

  1. Switch off the customer-site circuit breakers to the PDU being removed.
  2. Move the circuit breaker and power OUTPUT switch located on the faceplate of the PDU to the off (O) position.
  3. Disconnect the AC power cord from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process. Verify that the 200-240 V/346-415 ~ 30 A 50-60 Hz LED on the PDU faceplate is off.
  5. Remove the power supply modules (PSMs) in the front of the chassis from the PDU to be removed (see Figure 15).
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Loosen the captive screw on the PSM ejector handle.
    3. Grasp the ejector handle and pull to eject the PSM. Slide the PSM halfway out of the chassis. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    4. Repeat these steps for the remaining PSMs in the PDU.
    Figure 15: Removing the AC Power Supply ModulesRemoving the AC Power Supply Modules
  6. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis at the back of the PTX5000.
  7. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws to the metal wiring compartment door. Open the door of the metal wiring compartment. Disconnect the wires from the AC terminal block on the three-phase wye AC PDU (Figure 16). Using 1/5-in. (5.5-mm) slotted screw, loosen the input terminal or grounding point screw, and remove each wire from the input terminal or grounding point.
    1. Remove the wire labeled L3 from the L3 input terminal.
    2. Remove the wire labeled L2 from the L2 input terminal.
    3. Remove the wire labeled L1 from the L1 input terminal.
    4. Remove the wire labeled GND into the grounding point.
    Figure 16: Disconnecting AC Power Wires from a Three-Phase Wye AC PDUDisconnecting AC Power Wires from a Three-Phase Wye AC PDU
  8. Using a number 2 Phillips (+) screwdriver, loosen the screws that secure the metal retaining bracket and AC power cord to the PDU. While gently removing the wires of the AC power cord from the wiring compartment, remove the metal retaining bracket and AC power cord from the PDU. See Figure 17.
    Figure 17: Removing the Metal Retaining Bracket and AC Power CordRemoving the Metal Retaining Bracket and AC Power Cord
  9. Loosen the four captive screws attaching the front PDU handle to the PDU and chassis.
  10. Grasp the front installation handle on the PDU faceplate and pull the handle firmly down toward you. Slide the PDU halfway out of the chassis until you can reach the top installation handle. (See Figure 19.)
  11. Use the top and front installation handle to slide the PDU completely out of the chassis.
    CAUTION:

    Each PDU weighs approximately 51.2 lb (23.2 kg). Be prepared to support the full weight of the PDU as you remove it from the PTX5000.

Warning:

Do not touch the power connectors on the rear of the PDU. They can contain dangerous voltages.

CAUTION:

Do not leave a PDU slot empty for more than a short time while the PTX5000 is operational. For proper airflow, the PDU must remain in the chassis or a blank panel must be used in an empty slot.

Figure 18: Three-Phase Wye AC PDUThree-Phase Wye AC PDU
  1

Top installation handle

  5

Circuit breaker

  2

Front installation handle

  6

Metal wiring compartment

  3

Power OUTPUT switch

  7

Metal wiring compartment door

  4

Air exhaust ventilation

  8

Metal retaining bracket

Figure 19: Removing a Three-Phase Wye AC PDURemoving a Three-Phase Wye AC PDU

Installing a PTX5000 Three-Phase Wye AC PDU

To install a three-phase wye AC PDU:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Switch the circuit breaker on the PDU to the off (O) position.
  3. Grasping both the front and top installation handle, insert the replacement PDU into the PDU slot.
  4. Using both hands, slide the PDU into the chassis until you feel resistance.
  5. Push the front installation handle up toward the PDU. Using a number 2 Phillips (+) screwdriver, tighten the captive screws on the handle.
  6. Using a number 2 Phillips (+) screwdriver, loosen the four captive screws on the metal retaining bracket located on the lower right of the newly installed PDU. Remove the metal retaining bracket from the PDU.
    Figure 20: Removing the Metal Retaining Bracket from the Three-Phase Wye PDURemoving the Metal Retaining Bracket from the Three-Phase Wye PDU
  7. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws on the metal AC wiring compartment of the replacement PDU. Open the metal door of the metal AC wiring compartment.
  8. Gently push the wires of the AC power cord into the area for the metal retaining bracket, and pull the wires to the left toward the metal AC wiring compartment.
  9. Using a number 2 Phillips (+) screwdriver, tighten the four captive screws on the metal retaining bracket to secure the AC power cord to the PDU.
    Figure 21: Connecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Wye PDUConnecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Wye PDU
  10. Connect the wires to the AC terminal block on the three-phase wye AC PDU (Figure 22). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal or grounding point screw, and insert each wire into the grounding point or input terminal, and tighten the screw.
    1. Insert the wire labeled GND into the grounding point.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    5. Insert the wire labeled N into the N input terminal.
    Figure 22: Connecting Grounding and AC Power Wires to a Three-Phase Wye AC PDUConnecting Grounding and AC Power Wires to a Three-Phase Wye AC PDU
  11. Verify that the AC power and grounding wire connections are correct.
  12. Using a number 2 Phillips (+) screwdriver, tighten the two captive screws on the metal AC wiring compartment.
  13. Verify that the AC power cord is not touching or blocking access to chassis components, and that it does not drape where people could trip on it.
  14. Reconnect the AC power cord to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  15. Switch on the customer-site circuit breaker to the PDU.
  16. Verify that the AC input (~) LED on the PDU faceplate is lit steadily, indicating that the PDU is receiving voltage.
  17. Reinstall the PSMs into the PDU.
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Place one hand underneath the PSM to support it and slide it into the PSM slot.
    3. Push the ejector handle toward the PSM, and tighten the captive screw on the ejector handle to secure it to the PSM.
    4. Repeat these step for the other PSMs in the PDU.
  18. Move the circuit breaker on the PDU to the on (|) position.
  19. Verify that the CB ON LED on the PDU faceplate is lit steadily.
  20. Move the power OUTPUT switch on the PDU to the on (|) position.
  21. Verify that the AC IN LED and DC IN LED on the faceplate of each PSM in the PDU are lit steadily, indicating that each PSM is receiving power. Verify that the FAULT LED is off.
  22. Verify that the PDU OK LED on the PDU faceplate is lit steadily, indicating that the PDU is functioning normally.
Figure 23: Installing a Three-Phase Wye AC PDUInstalling a Three-Phase Wye AC PDU

Replacing a PTX5000 Three-Phase Wye AC PDU Power Cord

Removing a PTX5000 Three-Phase Wye AC PDU Power Cord

To remove a three-phase wye PDU power cord:

  1. Switch off the customer-site circuit breakers to the PDU for the AC power cord being removed.
  2. Move the circuit breaker and output power switch located on the faceplate of the PDU to the off (O) position.
  3. Disconnect the AC power cord from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process. Verify that the 200-240 V/346-415 ~ 30 A 50-60 Hz LED on the PDU faceplate is off.
  5. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis at the back of the PTX5000.
  6. Open the door of the metal wiring compartment.
  7. Disconnect the wires from the AC terminal block on the three-phase delta AC power supply (Figure 24). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal or grounding point screw, and remove each wire from the input terminal or grounding point.
    1. Remove the wire labeled N from the N input terminal.
    2. Remove the wire labeled L3 from the L3 input terminal.
    3. Remove the wire labeled L2 from the L2 input terminal.
    4. Remove the wire labeled L1 from the L1 input terminal.
    5. Remove the wire labeled GND into the grounding point.
    Figure 24: Disconnecting AC Power Wires from a Three-Phase Wye AC Power SupplyDisconnecting AC Power Wires from a Three-Phase Wye AC Power Supply
  8. Using a number 2 Phillips (+) screwdriver, loosen the captive screws that secure the metal retaining bracket and AC power cord to the PDU. While gently removing the wires of the AC power cord from the wiring compartment, remove the metal retaining bracket and AC power cord from the PDU. See Figure 25.
    Figure 25: Removing the Metal Retaining Bracket and AC Power CordRemoving the Metal Retaining Bracket and AC Power Cord

Installing a PTX5000 Three-Phase Wye AC PDU Power Cord

To install a three-phase wye AC power cord:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Switch the circuit breaker and power OUTPUT switch on the PDU to the off (O) position.
  3. Gently push the AC power cord wires through the hole in the metal retaining bracket. Screw the retaining nut onto the AC power cord to secure the metal retaining bracket to the replacement AC power cord (see Figure 26).
    Figure 26: Attaching the Metal Retaining Bracket to the AC Power Cord Attaching the Metal Retaining Bracket to the AC Power Cord
      1

    Retaining nut

      3

    Three-phase wye AC power cord

      2

    Metal retaining bracket

     
  4. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws on the metal AC wiring compartment. Open the metal door of the metal AC wiring compartment.
  5. Gently push the wires of the AC power cord into the area for the metal retaining bracket, and pull the wires to the left toward the metal AC wiring compartment. Using a number 2 Phillips (+) screwdriver, use the four screws on the metal retaining bracket to secure the AC power cord to the PDU (see Figure 27).
    Figure 27: Connecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Wye PDUConnecting the Metal Retaining Bracket and AC Power Cord to the Three-Phase Wye PDU
  6. Connect the wires to the AC terminal block on the three-wye AC PDU (Figure 28). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen each of the input terminals or grounding point screws, insert each wire into the grounding point or input terminal, and tighten the screw.
    1. Insert the wire labeled GND into the grounding point.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    5. Insert the wire labeled N into the N input terminal.
    Figure 28: Connecting Grounding and AC Power Wires to a Three-Phase Wye AC Power SupplyConnecting Grounding and AC Power Wires to a Three-Phase Wye AC Power Supply
  7. Verify that the AC power and grounding wiring connections are correct.
  8. Using a number 2 Phillips (+) screwdriver, tighten the two captive screws on the metal AC wiring compartment.
  9. Verify that the AC power cord is not touching or blocking access to PTX5000 components, and that it does not drape where people could trip on it.
  10. Reconnect the AC power cord to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  11. Switch on the customer-site circuit breaker to the PDU.
  12. Verify that the 200-240 V/346-415 ~ 30 A 50-60 Hz LED on the PDU faceplate is lit steadily, indicating that the PDU is receiving voltage.
  13. Move the circuit breaker on the PDU to the on (|) position.
  14. Verify that the CB ON LED on the PDU faceplate is lit steadily.
  15. Move the power OUTPUT switch on the PDU to the on (|) position.
  16. Verify that the AC IN LED and DC IN LED on the faceplate of each PSM in the PDU are lit steadily, indicating that each PSM is receiving power. Verify that the FAULT LED is off.
  17. Verify that the PDU OK LED on the PDU faceplate is lit steadily, indicating that the PDU is functioning normally.

Replacing a PTX5000 Normal-Capacity AC PSM

Removing a PTX5000 AC PSM

To remove an AC PSM:

  1. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis.
  2. Loosen the captive screws on the door covering the PSM and open the door.
  3. Loosen the captive screw on the PSM ejector handle.
  4. Grasp the ejector handle and pull to eject the PSM. Slide it halfway out of the chassis (see Figure 29).
    CAUTION:

    Each AC PSM weighs approximately 10.5 lb (4.8 kg). Be prepared to support the full weight of the PSM as you remove it from the PTX5000.

  5. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    Figure 29: Removing a PSMRemoving a PSM

Installing a PTX5000 AC PSM

To install an AC PSM:

  1. Using both hands, slide the PSM into the chassis until you feel resistance . Each AC PSM weighs approximately 10.5 lb (4.8 kg).
  2. Push the ejector handle toward the PSM, and tighten the captive screw on the PSM.
  3. Verify that the AC IN OK LED on the PSM faceplate is lit steadily, indicating that the PSM is receiving power.
  4. Verify that the DC IN OK LED on the PSM faceplate is lit steadily.
Figure 30: Installing a PSMInstalling a PSM

Replacing a PTX5000 High Capacity Delta AC PDU

Removing a PTX5000 High Capacity Delta AC PDU

The PTX5000 has two redundant, load-sharing PDUs. Each PDU is hot-insertable and hot-removable. The High Capacity Delta AC PDU weighs 63.3 lb (28.7 kg).

To remove a High Capacity Delta AC PDU:

  1. Switch off the customer-site circuit breakers to the PDU that is being removed.
  2. Move the power switch located on the faceplate of the PDU to the standby () position.
  3. Disconnect the AC power cord from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process. Verify that the AC input LED on the PDU faceplate is off.
  5. Remove the power supply modules (PSMs) in the front of the chassis from the PDU to be removed (see Figure 31).
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Press down the locking tab and then pull out the PSM by using the ejector handle. Grasp the ejector handle and pull to eject the PSM.
    3. Slide the PSM halfway out of the chassis. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    4. Repeat these steps for the remaining PSMs in the PDU.
    Figure 31: Removing the High Capacity AC Power Supply ModulesRemoving the High Capacity AC Power Supply Modules
    Warning:

    Each High Capacity AC PSM weighs approximately 9.8 lb (4.5 kg). Be prepared to support the full weight of the PSM as you remove it from the PTX5000.

  6. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis.
  7. Open the door of the metal wiring compartment.
  8. Disconnect the wires from the AC terminal block on the High Capacity Delta AC PDU (Figure 32). Using a 5/16-in. (8-mm) slotted screwdriver, loosen the input terminal screws and the grounding point screw, and remove each wire from the input terminal and the grounding point.
    1. Remove the wire labeled L3 from the L3 input terminal.
    2. Remove the wire labeled L2 from the L2 input terminal.
    3. Remove the wire labeled L1 from the L1 input terminal.
    4. Remove the wire labeled GND from the grounding point.
    Figure 32: Disconnecting AC Power Wires from a High Capacity Delta AC PDUDisconnecting AC Power Wires from a High Capacity Delta AC PDU
  9. Using a number 2 Phillips (+) screwdriver, loosen the captive screws that secure the metal retaining bracket and AC power cord to the PDU. While gently removing the wires of the AC power cord from the wiring compartment, remove the metal retaining bracket and AC power cord from the PDU. See Figure 33.
    Figure 33: Removing the Metal Retaining Bracket and AC Power CordRemoving the Metal Retaining Bracket and AC Power Cord
  10. Loosen the four captive screws attaching the front PDU handle to the PDU and chassis.
  11. Grasp the front PDU handle on the PDU faceplate and pull firmly down toward you. Slide the PDU halfway out of the chassis until you can reach the installation handle located on top of the PDU. (See Figure 34).
    Warning:

    Each PDU weighs approximately 63.3 lb (28.7 kg). Be prepared to support the full weight of the PDU as you remove it from the PTX5000.

  12. Use the installation handle to slide the PDU completely out of the chassis.
    Figure 34: Removing a High Capacity Delta AC PDURemoving a High Capacity Delta AC PDU
  13. Use the captive screws on the metal retaining bracket to reattach it to the PDU being removed.
Warning:

Do not touch the power connectors on the rear of the PDU. They can contain dangerous voltages.

CAUTION:

Do not leave a PDU slot empty for more than a short time while the PTX5000 is operational. For proper airflow, the PDU must remain in the chassis or a blank panel must be used in an empty slot.

Installing a PTX5000 High Capacity Delta AC PDU

To install a High Capacity Delta AC PDU:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Move the power switch located on the faceplate of the PDU to the standby () position.
  3. Grasp the front installation handle and top installation handle, and insert the PDU into the PDU slot. See Figure 35.
    Figure 35: Installing a High Capacity Delta AC PDUInstalling a High Capacity Delta AC PDU
  4. Using both hands, slide the PDU into the chassis until you feel resistance.
  5. Push the front installation handle up toward the PDU, and secure the handle with the captive screws.
  6. Using a number 2 Phillips (+) screwdriver, loosen the four captive screws that secure the metal retaining bracket to the newly installed PDU. Remove the metal retaining bracket from the PDU.
  7. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws on the metal AC wiring compartment of the replacement PDU. Open the metal door of the metal AC wiring compartment.
  8. Gently push the wires of the AC power cord into the area for the metal retaining bracket, and pull the wires to the left toward the metal AC wiring compartment.
  9. Using a number 2 Phillips (+) screwdriver, use the four captive screws on the metal retaining bracket to secure the AC power cord to the PDU. See Figure 36.
    Figure 36: Connecting the Metal Retaining Bracket and AC Power Cord to the High Capacity Delta PDUConnecting the Metal Retaining Bracket and AC Power Cord to the High Capacity Delta PDU
  10. Connect the wires to the AC terminal block on the High Capacity Delta AC PDU (Figure 37). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal screws and the grounding point screw, insert each wire into the grounding point or input terminal, and tighten the screws.
    1. Insert the wire labeled GND into the grounding point.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    Figure 37: Connecting Grounding and AC Power Wires to a High Capacity Delta AC Power SupplyConnecting Grounding and AC Power Wires to a High Capacity Delta AC Power Supply
  11. Verify that the AC power and grounding wiring connections are correct.
  12. Using a number 2 Phillips (+) screwdriver, tighten the two captive screws on the metal AC wiring compartment.
  13. Verify that the AC power cord does not touch or block access to chassis components, and that it does not drape where people could trip on it.
  14. Reconnect the AC power cord to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  15. Switch on the customer-site circuit breaker to the PDU.
  16. Verify that the AC input LED on the PDU faceplate is lit steadily, indicating that the PDU is receiving voltage.
  17. Reinstall the PSMs into the PDU.
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Place one hand underneath the PSM to support it and slide it into the PSM slot.
    3. Push the ejector handle toward the PSM, and tighten the captive screw on the ejector handle to secure it to the PSM.
    4. Repeat these steps for the other PSMs in the PDU.
  18. Move the power switch on the PDU to the on (|) position.
  19. Verify that the input OK LED on the faceplate of each PSM in the PDU is lit steadily, which indicates that each PSM is receiving power. Verify that the fault () LED is off.
  20. Verify that the PDU OK LED on the PDU faceplate is lit steadily, which indicates that the PDU is functioning normally.

Replacing a PTX5000 High Capacity Wye AC PDU

Removing a PTX5000 High Capacity Wye AC PDU

The PTX5000 has two redundant, load-sharing PDUs. Each PDU is hot-insertable and hot-removable. The High Capacity Wye AC PDU weighs 63.3 lb (28.7 kg).

To remove a High Capacity Wye AC PDU:

  1. Switch off the customer-site circuit breakers to the PDU that is being removed.
  2. Move the power switch located on the faceplate of the PDU to the standby () position.
  3. Disconnect the AC power cord from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process. Verify that the AC In (~) LED on the PDU faceplate is off.
  5. Remove the power supply modules (PSMs) in the front of the chassis from the PDU to be removed (see Figure 38).
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Press down the locking tab and then pull out the PSM by using the ejector handle.
    3. Grasp the ejector handle and pull to eject the PSM. Slide the PSM halfway out of the chassis.
    4. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    5. Repeat these steps for the remaining PSMs in the PDU.
    Figure 38: Removing the High Capacity AC Power Supply ModulesRemoving the High Capacity AC Power Supply Modules
    Warning:

    Each High Capacity AC PSM weighs approximately 9.8 lb (4.5 kg). Be prepared to support the full weight of the PSM as you remove it from the PTX5000.

  6. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis at the back of the PTX5000.
  7. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws to the metal wiring compartment door. Open the door of the metal wiring compartment. Disconnect the wires from the AC terminal block on the High Capacity Wye AC PDU (Figure 39). Using 7/32-in. (5.5-mm) slotted screwdriver, loosen the input terminal screws and the grounding point screw, and remove each wire from the input terminal points and the grounding point.
    1. Remove the wire labeled L3 from the L3 input terminal.
    2. Remove the wire labeled L2 from the L2 input terminal.
    3. Remove the wire labeled L1 from the L1 input terminal.
    4. Remove the wire labeled GND into the grounding point.
    Figure 39: Disconnecting AC Power Wires from a High Capacity Wye AC PDUDisconnecting AC Power Wires from a High Capacity Wye AC PDU
  8. Using a number 2 Phillips (+) screwdriver, loosen the screws that secure the metal retaining bracket and AC power cord to the PDU. While gently removing the wires of the AC power cord from the wiring compartment, remove the metal retaining bracket and AC power cord from the PDU. See Figure 40.
    Figure 40: Removing the Metal Retaining Bracket and AC Power CordRemoving the Metal Retaining Bracket and AC Power Cord
  9. Loosen the four captive screws attaching the front PDU handle to the PDU and chassis.
  10. Grasp the front installation handle on the PDU faceplate and pull the handle firmly down toward you. Slide the PDU halfway out of the chassis until you can reach the top installation handle. (See Figure 41.)
  11. Use the top and front installation handle to slide the PDU completely out of the chassis.
    CAUTION:

    Each PDU weighs approximately 63.3 lb (28.7 kg). Be prepared to support the full weight of the PDU as you remove it from the PTX5000.

Warning:

Do not touch the power connectors on the rear of the PDU. They can contain dangerous voltages.

CAUTION:

Do not leave a PDU slot empty for more than a short time while the PTX5000 is operational. For proper airflow, the PDU must remain in the chassis or a blank panel must be used in an empty slot.

Figure 41: Removing a High Capacity Wye AC PDURemoving a High Capacity Wye AC PDU

Installing a PTX5000 High Capacity Wye AC PDU

To install a High Capacity Wye AC PDU:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Move the power switch located on the faceplate of the PDU to the standby () position.
  3. Grasping both the front and top installation handles, insert the replacement PDU into the PDU slot. See Figure 42.
    Figure 42: Installing a High Capacity Wye AC PDUInstalling a High Capacity Wye AC PDU
  4. Using both hands, slide the PDU into the chassis until you feel resistance.
  5. Push the front installation handle up toward the PDU. Using a number 2 Phillips (+) screwdriver, tighten the captive screws on the handle.
  6. Using a number 2 Phillips (+) screwdriver, loosen the four captive screws on the metal retaining bracket located on the lower right of the newly installed PDU. Remove the metal retaining bracket from the PDU. See Figure 43.
    Figure 43: Removing the Metal Retaining Bracket from the High Capacity Wye PDURemoving the Metal Retaining Bracket from the High Capacity Wye PDU
  7. Using a number 2 Phillips (+) screwdriver, loosen the two captive screws on the metal AC wiring compartment of the replacement PDU. Open the metal door of the metal AC wiring compartment.
  8. Gently push the wires of the AC power cord into the area for the metal retaining bracket, and pull the wires to the left toward the metal AC wiring compartment.
  9. Using a number 2 Phillips (+) screwdriver, tighten the four captive screws on the metal retaining bracket to secure the AC power cord to the PDU. See Figure 44.
    Figure 44: Connecting the Metal Retaining Bracket and AC Power Cord to the High Capacity Wye PDUConnecting the Metal Retaining Bracket and AC Power Cord to the High Capacity Wye PDU
  10. Connect the wires to the AC terminal block on the High Capacity Wye AC PDU (Figure 45). Using a 1/5-in. (5.5-mm) slotted screwdriver, loosen the input terminal screws and the grounding point screw, and insert each wire into the grounding point or input terminal, and tighten the screw.
    1. Insert the wire labeled GND into the grounding point.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    5. Insert the wire labeled N into the N input terminal.
    Figure 45: Connecting Grounding and AC Power Wires to a High Capacity Wye AC PDUConnecting Grounding and AC Power Wires to a High Capacity Wye AC PDU
  11. Verify that the AC power and grounding wire connections are correct.
  12. Using a number 2 Phillips (+) screwdriver, tighten the two captive screws on the metal AC wiring compartment.
  13. Verify that the AC power cord is does not touch or block access to chassis components, and that it does not drape where people could trip on it.
  14. Reconnect the AC power cord to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  15. Switch on the customer-site circuit breaker to the PDU.
  16. Verify that the AC input (~) LED on the PDU faceplate is lit steadily, indicating that the PDU is receiving voltage.
  17. Reinstall the PSMs into the PDU.
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Place one hand underneath the PSM to support it and slide it into the PSM slot.
    3. Push the ejector handle toward the PSM, and tighten the captive screw on the ejector handle to secure it to the PSM.
    4. Repeat these steps for all the other PSMs in the PDU.
  18. Move the circuit breaker on the PDU to the on (|) position.
  19. Verify that the CB OK LED on the PDU faceplate is lit steadily.
  20. Move the power switch on the PDU to the on (|) position.
  21. Verify that the input OK LED on the faceplate of each PSM in the PDU is lit steadily, which indicates that each PSM is receiving power. Verify that the fault () LED is off.
  22. Verify that the PDU OK LED on the PDU faceplate is lit steadily, indicating that the PDU is functioning normally.

Replacing a PTX5000 High Capacity Single-Phase AC PDU

Removing a PTX5000 Single-Phase AC PDU

The PTX5000 has two redundant, load-sharing PDUs. Each PDU is hot-insertable and hot-removable. The Single-Phase AC PDU weighs 60.5 lb (27.4 kg).

To remove a Single-Phase AC PDU:

  1. Switch off the customer-site circuit breakers to the PDU that is being removed.
  2. Move the power switch located on the faceplate of the PDU to the standby () position.
  3. Disconnect the AC power cords from the power source.
    Note:

    After powering off a PDU, you must wait at least 60 seconds before turning it back on.

  4. Make sure that the voltage across the AC power cord is 0 V and that there is no chance that the AC power cord might become active during the removal process.
  5. If 20-A input cord is used, then use a number 2 Phillips (+) screwdriver to loosen the screw on the 20-A input terminal and plug in the connector (see Figure 46). Tighten the screw after plugging in the connector.
    Note:

    The 30-A connector does not have a clamp, it has its own integral clip for locking the connector.

    Figure 46: Disconnecting 20-A inputs to High Capacity Single-Phase AC PDUDisconnecting 20-A inputs to High Capacity Single-Phase AC PDU
  6. Remove the power supply modules (PSMs) in the front of the chassis from the PDU to be removed (see Figure 47).
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Press down the locking tab and then pull out the PSM by using the ejector handle.
    3. Grasp the ejector handle and pull to eject the PSM. Slide the PSM halfway out of the chassis.
    4. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    5. Repeat these steps for the remaining PSMs in the PDU.
    Figure 47: Removing the High Capacity AC Power Supply ModulesRemoving the High Capacity AC Power Supply Modules
    Warning:

    Each High Capacity AC PSM weighs approximately 14.3 lb (6.5 kg). Be prepared to support the full weight of the PSM as you remove it from the PTX5000.

  7. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis at the back of the PTX5000.
  8. Loosen the four captive screws attaching the front PDU handle to the PDU and chassis.
  9. Grasp the front installation handle on the PDU faceplate and pull the handle firmly down toward you. Slide the PDU halfway out of the chassis until you can reach the top installation handle. (See Figure 48.)
  10. Use the top and front installation handle to slide the PDU completely out of the chassis.
    CAUTION:

    Each PDU weighs approximately 60.5 lb (27.4 kg). Be prepared to support the full weight of the PDU as you remove it from the PTX5000.

Warning:

Do not touch the power connectors on the rear of the PDU. They can contain dangerous voltages.

CAUTION:

Do not leave a PDU slot empty for more than a short time while the PTX5000 is operational. For proper airflow, the PDU must remain in the chassis or a blank panel must be used in an empty slot.

Figure 48: Removing a High Capacity Single-Phase AC PDURemoving a High Capacity Single-Phase AC PDU

Installing a PTX5000 High Capacity Single-Phase AC PDU

To install a Single-Phase AC PDU:

  1. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  2. Move the power switch located on the faceplate of the PDU to the standby () position.
  3. Grasping both the front and top installation handles, insert the replacement PDU into the PDU slot. See Figure 49.
    Figure 49: Installing a Single-Phase AC PDUInstalling a Single-Phase AC PDU
  4. Using both hands, slide the PDU into the chassis until you feel resistance.
  5. Push the front installation handle up toward the PDU. Using a number 2 Phillips (+) screwdriver, tighten the captive screws on the handle.
  6. Reinstall the PSMs into the PDU.
    1. Loosen the captive screws on the door covering the PSMs and open the door.
    2. Place one hand underneath the PSM to support it and slide it into the PSM slot.
    3. Push the ejector handle toward the PSM, and tighten the captive screw on the ejector handle to secure it to the PSM.
    4. Repeat these steps for all the other PSMs in the PDU.
  7. Using a number 2 Phillips (+) screwdriver, loosen the two screws from the metal door of the metal AC wiring compartment located in the middle of the PDU for 20-A inputs and lower part of the PDU for the 30-A inputs.
  8. Using a number 2 Phillips (+) screwdriver, loosen the screw on the 20-A input terminal and plug in the connector.(see Figure 51). Tighten the screw after plugging in the connector.
    Note:

    The 30 A connector does not have a clamp, it has its own integral clip for locking the connector.

    Figure 50: 20-A Plug Type (North America)20-A Plug Type (North America)
    Figure 51: Connecting 20-A Inputs to High Capacity Single-Phase AC PDUConnecting 20-A Inputs to High Capacity Single-Phase AC PDUConnecting 20-A Inputs to High Capacity Single-Phase AC PDU
    Figure 52: Connecting 30 A inputs to High Capacity Single-Phase AC PDUConnecting 30 A inputs to High Capacity Single-Phase AC PDU
  9. Connect up to eight inputs (20-A or 30-A) to the PDU. See Figure 53.
    Figure 53: 30-A Plug Types (North America)30-A Plug Types (North America)
    Figure 54: Connecting 30 A Inputs to High Capacity Single-Phase AC PDUConnecting 30 A Inputs to High Capacity Single-Phase AC PDUConnecting 30 A Inputs to High Capacity Single-Phase AC PDU
  10. Verify that the AC power wiring connections are correct.
  11. Verify that the AC power cord does not touch or block access to PTX5000 components, and that it does not drape where people could trip on it.
  12. Repeat the procedure for the other single-phase AC PDU.
  13. Verify that the AC power cord does not touch or block access to chassis components, and that it does not drape where people could trip on it.
  14. Reconnect the all the AC power cords to the power source.
    Note:

    After powering on a PDU, you must wait at least 60 seconds before turning it off.

  15. Switch on the customer-site circuit breakers to the PDU.
  16. Move the power switch on the PDU to the on (|) position.
  17. Verify that the input PSM LEDs on the faceplate of the PDU is lit steadily, which indicates that each PSM is receiving power.
  18. Verify that the PDU OK LED on the PDU faceplate is lit steadily, indicating that the PDU is functioning normally.

Replacing a PTX5000 High Capacity AC PSM

Removing a PTX5000 High Capacity AC PSM

To remove a High Capacity AC PSM:

  1. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis.
  2. Loosen the captive screws on the door covering the PSMs and open the door.
  3. Press down the locking tab and then pull out the PSM by using the ejector handle.
    CAUTION:

    Each High Capacity AC PSM weighs approximately 9.8 lb (4.5 kg). Be prepared to support the full weight of the PSM as you remove it from the PTX5000.

  4. Place one hand underneath the PSM to support it and slide it completely out of the chassis.
    Figure 55: Removing a High Capacity AC PSMRemoving a High Capacity AC PSM

Installing a PTX5000 High Capacity AC PSM

The High Capacity DC PSMs are smaller in dimensions compared to the first-generation PSMs. So, you must install the PSM sleeves to install the High Capacity DC PSMs in the chassis. See Installing the High Capacity PSM Sleeves for details. Each High Capacity AC PSM weighs approximately 9.8 lb (4.5 kg).

To install a High Capacity AC PSM:

  1. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis.
  2. Using both hands, slide the PSM into the chassis until the locking tab is engaged.
    Figure 56: Installing a High Capacity AC PSMInstalling a High Capacity AC PSM
  3. Close the ejector handle so that it is flush with the PSM faceplate.
  4. Verify that the AC input OK LED on the PSM faceplate is lit steadily, indicating that the PSM is receiving voltage.
  5. Verify that the AC output OK LED on the PSM faceplate is lit steadily, indicating the output is functioning normally, and the input voltage is within the supported range.