QFX10016 Power Planning
Use the information to calculate the power consumption for the QFX10016 and plan your system’s power requirements.
Power Requirements for QFX10000 Components
Table 1 lists the power requirements for different hardware components of a QFX10008 and QFX10016 under typical voltage conditions. For power requirements for chassis configurations, see Calculating Power Requirements for a QFX10008 and Calculating Power Requirements for a QFX10016.
Components |
Description |
Power Requirements (Watts) |
|
---|---|---|---|
Typical Power |
Maximum Power |
||
QFX10008-SF |
QFX10008 SIB |
170 W |
225 W |
QFX10016-SF |
QFX10016 SIB |
510 W |
675 W |
QFX10008-FAN |
QFX10008 standard fan tray |
225 W at 77° F (25° C) |
475 W at maximum fan speed |
QFX10016-FAN |
QFX10016 fan tray |
475 W at 77° F (25° C) |
975 W at maximum fan speed |
QFX10000-RE |
QFX10000 Routing and Control Board |
50 W |
125 W |
QFX10000-30C |
QFX10000 30-port QSFP28 line card |
890 W |
1150 W |
QFX10000-30C-M |
QFX10000 30-port MACsec QSSP28 line card |
950 W |
1250 W |
QFX10000-36Q |
QFX10000 36-port QSFP+ line card |
520 W |
675 W |
QFX10000-60S-6Q |
QFX10000 60-port SFP+ and 6-port QSFP+ line card |
365 W |
455 W |
QFX10K-12C-DWDM |
QFX10000 Coherent line card |
900 W |
1050 W |
Calculating Power Requirements for a QFX10016
Use the information in this topic to calculate power requirements of your QFX10016 configuration and the number of power supplies required for different QFX10016 switch configurations.
To ensure adequate power and to avoid raising a power alarm, you must maintain a redundant power supply in your device at all times. This additional power supply provides for the recommended n +1 redundancy.
Replace failed power supplies immediately to prevent unexpected failures.
If a new line card is installed in an operational switch, power management does not power on the line card if the increased power demand exceeds the total available power, including redundant power. If redundant power is used to power on the line card, a minor alarm is raised, which becomes a major alarm in five minutes if the condition is not corrected.
The calculations in this topic represent the maximum power requirements that you need to budget for your QFX10016 modular switch configuration. The actual power consumption of your switch will be less than the calculated results shown here and will vary based on the hardware and software configuration of your switch, the amount of traffic passing through the line cards, and environmental variables such as room temperature.
Before you begin these calculations:
Ensure you understand the different switch configurations. See QFX10016 Components and Configurations.
Ensure that you know the power requirements of different switch components. See Power Requirements for QFX10000 Components.
This topic describes these tasks:
- How to Calculate the Power Consumption of Your QFX10016
- How to Calculate the Number of Power Supplies Required for Your QFX10016 Configuration
How to Calculate the Power Consumption of Your QFX10016
Use the following procedure to determine the maximum power you need to supply to the switch. To calculate system power consumption, you first determine the combined internal power requirements of all the switch components and then divide this result by the power supply output power.
To calculate maximum system power consumption:
How to Calculate the Number of Power Supplies Required for Your QFX10016 Configuration
Use this procedure to calculate the number of power supplies required by your switch configuration. The minimum power configuration for QFX10016 switches is three power supplies. However, using the calculated minimum power configuration does not prevent the system from raising a power alarm. To ensure do you not log power alarms, you must configure your switch for n+1 power supplies.
To calculate the number of power supplies required for your minimum switch configuration:
QFX10008 and QFX100016 Grounding Cable and Lug Specifications
You must install the switch in a restricted-access location and ensure it is adequately grounded at all times. Proper grounding ensures your switch is operating correctly and that it meets safety and electromagnetic interference (EMI) requirements. A QFX modular chassis, has a 2-hole protective grounding terminal on the rear of the chassis beneath the power supplies for grounding.
For AC powered systems, you must also use the grounding wire in the AC power cord along with the 2-hole lug ground connection. This tested system meets or exceeds all applicable EMC regulatory requirements with the 2-hole protective grounding terminal.
To comply with GR-1089 requirements, all intra-building copper cabling used for SFP+, QSFP+, and QSFP28 ports must be shielded and grounded at both ends.
Before switch installation begins, a licensed electrician must attach a cable lug to the grounding cable that you supply. See Connect the QFX10008 or QFX10016 to Earth Ground. A cable with an incorrectly attached lug can damage the switch.
Before connecting the switch to earth ground, review the following information:
Two threaded inserts (PEM nuts) are provided on the lower rear of the chassis for connecting the switch to earth ground. The grounding points are spaced at 0.63 in. (16 mm) centers.
The grounding lug required is a Panduit LCD6-10A-L or equivalent (provided). The grounding lug accommodates 6 AWG (13.3 mm²) stranded wire. If one or more JNP10K-PWR-DC2 power supplies are installed in the chassis and set for high input (80-A), use the Panduit LCD4-14A-L or equivalent (provided). This lug accommodates 4 AWG (21.1mm²) stranded wire.
The grounding cable that you provide for a QFX10016 must be the same size or heavier than the input wire of each power supply. Minimum recommendations are 6 AWG (13.3 mm²) stranded copper wire, Class B; 90° C wire, or as permitted by local code.