ON THIS PAGE
QFX5110 Site Guidelines and Requirements
QFX5110 Environmental Requirements and Specifications
The switch must be installed in a rack or cabinet. It must be housed in a dry, clean, well-ventilated, and temperature-controlled environment.
Follow these environmental guidelines:
The site must be as dust-free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the switch cooling system.
Maintain ambient airflow for normal switch operation. If the airflow is blocked or restricted, or if the intake air is too warm, the switch might overheat, leading to the switch temperature monitor shutting down the device to protect the hardware components.
Table 1 provides the required environmental conditions for normal switch operation for all QFX5110 models.
Description |
Tolerance |
---|---|
Altitude |
No performance degradation to 6562 feet (2000 meters) |
Relative humidity |
Normal operation ensured in relative humidity range of 5% through 90%, noncondensing
|
Temperature |
|
Seismic |
Designed to comply with Zone 4 earthquake requirements per NEBS GR-63-CORE, Issue 3. |
Install QFX Series devices only in restricted areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.
See Also
General Site Guidelines
Efficient device operation requires proper site planning and maintenance. It also requires proper layout of the equipment, rack or cabinet, and wiring closet.
To plan and create an acceptable operating environment for your device and prevent environmentally caused equipment failures:
Keep the area around the chassis free from dust and conductive material, such as metal flakes.
Follow the prescribed airflow guidelines to ensure that the cooling system functions properly. Ensure that exhaust from other equipment does not blow into the intake vents of the device.
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent damaging the equipment. Static discharge can cause components to fail completely or intermittently over time.
Install the device in a secure area, so that only authorized personnel can access the device.
Site Electrical Wiring Guidelines
Table 2 describes the factors you must consider while planning the electrical wiring at your site.
You must provide a properly grounded and shielded environment and use electrical surge-suppression devices.
Avertissement Vous devez établir un environnement protégé et convenablement mis à la terre et utiliser des dispositifs de parasurtension.
Site Wiring Factor |
Guidelines |
---|---|
Signaling limitations |
If your site experiences any of the following problems, consult experts in electrical surge suppression and shielding:
|
Radio frequency interference |
To reduce or eliminate RFI from your site wiring, do the following:
|
Electromagnetic compatibility |
If your site is susceptible to problems with electromagnetic compatibility (EMC), particularly from lightning or radio transmitters, seek expert advice. Strong sources of electromagnetic interference (EMI) can cause:
|
QFX5110 Chassis Grounding Cable and Lug Specifications
To ground a QFX5110, connect a grounding cable to earth ground and attach it to the chassis grounding points. See Connect the QFX5110 to Earth Ground. However if you are unable to access the chassis grounding point on a DC system by using the two-holed grounding lug, you can ground the chassis using the DC protective earthing terminal on the DC power supply, see Alternate Method to Ground QFX5110-48S-DC and QFX5110-32Q-DC Systems.
To comply with GR-1089 requirements, all intra-building copper cabling used for SFP+ and QSFP+ ports must be shielded and grounded at both ends.
Before switch installation begins, a licensed electrician must attach a cable lug to the grounding cables that you supply. See Connect the QFX5110 to Earth Ground. A cable with an incorrectly attached lug can damage the switch.
Before connecting the switch to earth ground, review the following information:
The grounding lug required is a Panduit LCD10-10A-L or equivalent (not provided). The recommended grounding lug accommodates 14–10 AWG (2–5.3 mm²) stranded wire. If you are using the alternate method of grounding the chassis on a QFX5110-48S or QFX5110-32Q DC system, the recommended grounding cable is 12 AWG (2.5 mm²) standard wire, 90° C wire or heavier.
The grounding cable must be 14 AWG (2 mm²), minimum 60° C wire, or as permitted by the local code (not provided).
See Also
QFX5110 Clearance Requirements for Airflow and Hardware Maintenance
When planning the site for installing a QFX5110, you must allow sufficient clearance around the installed chassis (see Figure 1).
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See QFX5110 Cooling System and Airflow Description for more information about the airflow through the chassis.
If you are mounting a QFX5110 in a rack with other equipment, ensure that the exhaust from other equipment does not blow into the intake vents of the chassis.
Leave at least 24 in. (61 cm) both in front of and behind the QFX5110. For service personnel to remove and install hardware components, you must leave adequate space at the front and back of the switch. NEBS GR-63 recommends that you allow at least 30 in. (76.2 cm) in front of the rack or cabinet and 24 in. (61 cm) behind the rack or cabinet.
See Also
QFX5110 Chassis Physical Specifications
The QFX5110 models are rigid sheet-metal structures that houses the hardware components. Table 3 summarizes the physical specifications of the QFX5110.
Product SKU |
Height |
Width |
Depth |
Weight |
---|---|---|---|---|
QFX5110-48S |
1.72 in. (4.3 cm) |
17.36 in. (44.1 cm) |
20.48 in. (52.02 cm) excluding fan and power supply handles |
23 lbs (10.43 kg) with 2 power supplies |
QFX5110-32Q |
1.72 in. (4.3 cm) |
17.36 in. (44.1 cm) |
20.48 in. (52.02 cm) excluding fan and power supply handles |
24.6 lbs (11.16 kg) with 2 power supplies |
See Also
QFX5110 Rack Requirements
QFX5110 switches are designed to be installed on four-post racks.
Rack requirements consist of:
Rack type
Mounting bracket hole spacing
Rack size and strength
Table 4 provides the rack requirements and specifications for the QFX5110.
Rack Requirement |
Guidelines |
---|---|
Rack type |
Use a four-post rack that provides bracket holes or hole patterns spaced at 1 U (1.75 in. or 4.45 cm) increments and that meets the size and strength requirements to support the weight. A U is the standard rack unit defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310–D) published by the Electronics Industry Association. |
Mounting bracket hole spacing |
The holes in the mounting brackets are spaced at 1 U (1.75 in. or 4.45 cm), so that the switch can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
|
Rack connection to building structure |
|