QFX5210 Site Guidelines and Requirements
QFX5210 Environmental Requirements and Specifications
The switch must be installed in a rack or cabinet. It must be housed in a dry, clean, well-ventilated, and temperature-controlled environment.
Follow these environmental guidelines:
The site must be as dust-free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the switch cooling system.
Maintain ambient airflow for normal switch operation. If the airflow is blocked or restricted, or if the intake air is too warm, the switch might overheat, leading to the switch temperature monitor shutting down the device to protect the hardware components.
Table 1 provides the required environmental conditions for normal switch operation.
Description |
Tolerance |
---|---|
Altitude |
AFO models have no performance degradation to 6000 feet (1828.8 meters). AFI models have no performance degradation at sea level. |
Relative humidity |
Normal operation ensured in relative humidity range of 5% through 90%, noncondensing.
|
Temperature |
CAUTION: High wattage optics (greater than 3.5 W) are only supported in ports 32 to 63 on QFX5210-64C-AFI. There is no restriction on high wattage optics on QFX5210-64C-AFO. |
Seismic |
Designed to comply with Zone 4 earthquake requirements per GR-63 , Issue 4. |
Install QFX Series devices only in restricted areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.
See Also
General Site Guidelines
Efficient device operation requires proper site planning and maintenance. It also requires proper layout of the equipment, rack or cabinet, and wiring closet.
To plan and create an acceptable operating environment for your device and prevent environmentally caused equipment failures:
Keep the area around the chassis free from dust and conductive material, such as metal flakes.
Follow the prescribed airflow guidelines to ensure that the cooling system functions properly. Ensure that exhaust from other equipment does not blow into the intake vents of the device.
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent damaging the equipment. Static discharge can cause components to fail completely or intermittently over time.
Install the device in a secure area, so that only authorized personnel can access the device.
QFX5210 Grounding Cable and Lug Specifications
To ground a QFX5210, connect a grounding cable to earth ground and then attach it to the chassis grounding points. See Connecting the QFX5210 to Ground.
Before switch installation begins, a licensed electrician must attach a cable lug to the grounding cables that you supply. A cable with an incorrectly attached lug can damage the switch.
Before connecting the switch to earth ground, review the following information:
The grounding lug required is a Panduit LCD10-10A-L or equivalent. The grounding lug accommodates 10 AWG (5 mm²) stranded wire.
The grounding cable that you provide for a QFX5210 must be 10 AWG (5 mm²), minimum 60° C wire, or as permitted by the local code.
See Also
QFX5210 Clearance Requirements for Airflow and Hardware Maintenance
When planning the site for installing a QFX5210, you must allow sufficient clearance around the installed chassis (see ).
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See QFX5210 Cooling System for more information about the airflow through the chassis.
If you are mounting a QFX5210 in a rack or cabinet with other equipment, ensure that the exhaust from other equipment does not blow into the intake vents of the chassis.
Leave at least 24 in. (61 cm) both in front of and behind the QFX5210. For service personnel to remove and install hardware components, you must leave adequate space at the front and back of the switch.
See Also
QFX5210 Chassis Physical Specifications
The QFX5210 is a rigid sheet-metal structure that houses the hardware components. Table 2 summarizes the physical specifications of the QFX5210.
Product SKU |
Height |
Width |
Depth |
Weight |
---|---|---|---|---|
QFX5210-64C |
3.5 in. (8.89 cm) |
17.25 in. (43.82 cm) |
22.83 in. (57.99 cm) |
23.44 lbs (10.63 kg) without power supplies and fan. 31.09 lbs (14.1 kg) with power supplies and fans installed. |
See Also
Site Electrical Wiring Guidelines
Table 3 describes the factors you must consider while planning the electrical wiring at your site.
You must provide a properly grounded and shielded environment and use electrical surge-suppression devices.
Avertissement Vous devez établir un environnement protégé et convenablement mis à la terre et utiliser des dispositifs de parasurtension.
Site Wiring Factor |
Guidelines |
---|---|
Signaling limitations |
If your site experiences any of the following problems, consult experts in electrical surge suppression and shielding:
|
Radio frequency interference |
To reduce or eliminate RFI from your site wiring, do the following:
|
Electromagnetic compatibility |
If your site is susceptible to problems with electromagnetic compatibility (EMC), particularly from lightning or radio transmitters, seek expert advice. Strong sources of electromagnetic interference (EMI) can cause:
|
QFX5210 Rack Requirements
QFX5210 switches are designed to be installed on four-post racks.
Rack requirements consist of:
Rack type
Mounting bracket hole spacing
Rack size and strength
Table 4 provides the rack requirements and specifications for the QFX5210.
Rack Requirement |
Guidelines |
---|---|
Rack type |
Use a four-post rack that provides bracket holes or hole patterns spaced at 1 U (1.75 in. or 4.45 cm) increments and that meets the size and strength requirements to support the weight. A U is the standard rack unit defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310–D) published by the Electronics Industry Association. |
Mounting bracket hole spacing |
The holes in the mounting brackets are spaced at 1 U (1.75 in. or 4.45 cm), so that the switch can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
|
Rack connection to building structure |
|
See Also
QFX5210 Cabinet Requirements
You can mount the QFX5210 in an enclosure or cabinet that contains a four-post 19-in. open rack as defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310-D) published by the Electronics Industry Association.
Cabinet requirements consist of:
Cabinet size and clearance
Cabinet airflow requirements
Table 5 provides the cabinet requirements and specifications for the QFX5210.
Cabinet Requirement |
Guidelines |
---|---|
Cabinet size and clearance |
The minimum cabinet size for accommodating a QFX5210 device is 36 in. (91.4 cm) deep. Large cabinets improve airflow and reduce the chance of overheating. |
Cabinet airflow requirements |
When you mount the switch in a cabinet, ensure that ventilation through the cabinet is sufficient to prevent overheating.
|