Help us improve your experience.

Let us know what you think.

Do you have time for a two-minute survey?

 
 

MX2008 DC Power System

MX2008 Seven-Feed DC Power Distribution Module Description

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDM.

In the DC power configuration, the router contains up to two DC PDMs located at the rear of the chassis in slots PDM0/Input0 and PDM1/Input1 (bottom to top). A minimum of one PDM is required per system (two PDMs per MX2008 chassis) for nonredundant power. The DC PDMs provides power interface to nine PSMs.

Four PDMs provide full redundancy.

Note:

Power backplane distributes regulated 52 VDC to all boards supplied by that system.

Each DC PDM has seven DC inputs (–48 VDC and return terminals for each input) (see Figure 1). Select 60 A or 80 A input feed capacity on the DC PDM by setting the switch to the rated amperage of DC power input feeds.

Note:

This switch applies to all inputs of this PDM. Selecting 60 A reduces the available power output capacity of the PSMs supplied by this PDM.

Figure 1: DC Power Distribution ModuleDC Power Distribution Module
Note:

The type of feed that you use on the DC PDM (60 A or 80 A) depends on the distribution scheme and distribution equipment. With a 60-A feed, the maximum power supply output power is limited to 2100 W while the maximum power supply input power is limited to 2400 W. With an 80-A feed, the maximum power supply output is limited to 2500 W while maximum power supply input power is limited to 2800 W. The system power management software calculates the available and used power based on DIP switch positions in the PDM.

Figure 2: DC Power Distribution Module (240 V China)DC Power Distribution Module (240 V China)

MX2008 DC Power Distribution Module (-48 V) Description

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

In the DC power configuration, the router contains up to two DC power distribution modules (PDMs) located at the rear of the chassis in slots PDM0/Input0 and PDM1/Input1 (bottom to top). A minimum of one PDM is required per system (two PDMs per chassis) for nonredundant power. The DC PDM provides a power interface to nine power supply modules (PSMs).

Two PDMs provide full redundancy. In a redundant configuration, a total of fourteen 60-A or 80-A input feeds (7-feed DC PDMs), and a total of eighteen 60-A or 80-A input feeds (9-feed DC PDMs) are supported.

Note:

The power backplane for a subsystem distributes regulated 52 VDC to all boards supplied by that subsystem.

Each DC PDM has seven or nine DC inputs (–48 VDC and return terminals for each input). You can select 60-A or 80-A input feed capacity on the DC PDM by setting the DIP switch on the PDM to the rated amperage of the DC power input feeds.

Note:

The selected input capacity applies to all inputs of this PDM. Selecting 60 A reduces the available power output capacity of the PSMs supplied by this PDM.

Figure 3 shows the MX2008 DC PDM.

Figure 3: MX2008 DC PDMMX2008 DC PDM
Note:

The type of feed that you use on the DC PDM (60-A or 80-A) depends on the distribution scheme and distribution equipment. With a 60-A feed, the maximum power supply output power is limited to 2100 W while the maximum power supply input power is limited to 2400 W. With an 80-A feed, the maximum power supply output is limited to 2500 W while the maximum power supply input power is limited to 2800 W. The system power management software calculates the available and used power based on DIP switch positions in the PDM.

MX2000 DC Power Distribution Module (240 V China) Description

In the DC power configuration, the router contains up to two DC power distribution modules (PDMs) located at the rear of the chassis in slots PDM0/Input0 and PDM1/Input1 (bottom to top). A minimum of one PDM is required per system (two PDMs per chassis) for nonredundant power. The DC PDM provides a power interface to nine power supply modules (PSMs).

Two PDMs provide full redundancy for the router. In a redundant configuration, a total of a total of eighteen (9-feed DC PDMs) are supported.

Note:

The power backplane for a subsystem distributes regulated 52 VDC to all boards supplied by that subsystem.

Each DC PDM (240 V China) has nine DC inputs, (see Figure 4).

Figure 4: MX2000 DC PDM (240 V China)MX2000 DC PDM (240 V China)

MX2008 DC Power Distribution Module (-48 V) LEDs

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

Each DC PDM faceplate contains one bicolor LED for each of the nine –48 V input power feeds, indicating the correct or incorrect polarity connection of each feed. See . Figure 5

Figure 5: DC Power Distribution Module LEDsDC Power Distribution Module LEDs
Table 1: DC Power Distribution Module LEDs

Label

Color

State

Description

–48V=80A

Green

On

RTN and –48V input feeds are connected. PDM is functioning normally.

Off

RTN input feed is not connected or present.

–48V input feed is not connected or present.

RTN and –48V input feeds are not connected.

Red

On

RTN or –48V input feeds may be reversed, feed live.

MX2000 DC Power Distribution Module (240 V China) LEDs

Each DC PDM (240 V China) faceplate contains one LED for each of the nine input power feeds, indicating the correct or incorrect polarity connection of each feed. See Figure 6 and Table 2 DC PDM (240 V China) LEDs.

Figure 6: DC Power Distribution Module (240 V China) LEDsDC Power Distribution Module (240 V China) LEDs
  1

LED

 
Table 2: DC Power Distribution Module (240 V China) LEDs

Color

State

Description

Green

On

Positive and negative input feeds are connected. PDM is functioning normally.

Off

Positive input feed is not connected or present.

Negative input feed is not connected or present.

MX2008 DC Power Supply Module (-48 V) Description

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

The MX2008 supports a DC power system. The DC power system operates with feeds of 60 A or 80 A current limited. A total of nine feeds are required to fully power the MX2008. Another nine feeds are required to provide feed redundancy (a total of 18 60-A or 80-A feeds). In the DC power configuration, the router contains up to nine DC PSMs located at the rear of the chassis in slots PSM0 through PSM8, (left to right). The DC PSMs in slots PSM0 through PSM8 provide power to the all router components including MPCs in slot 0 through 9, RCBs in slot 0 and 1, SFBs in slot 0 through 7, and fan trays 0 and 1.

Note:

The MX2008 systems configured for DC input power must use only DC PDMs and DC PSMs. You cannot mix AC and DC PSMs or PDMs within a single system.

Up to nine PSMs may be connected in parallel to increase available system power across MPCs as needed and provide redundancy. Figure 7 shows the DC PSM.

Figure 7: DC (-48 V) Power Supply ModuleDC (-48 V) Power Supply Module

The DC power system is feed redundant. Each DC PSM can be connected to two separate feeds from different sources that are used to provide feed redundancy. If two feeds are connected, PSM input power is drawn from the feed with the higher voltage present. There are two PDMs per power system capable of carrying nine feeds each. Connect feeds from one source to one PDM and feeds from the other source to the second PDM of the power system. The primary input of the PSM is a dual redundant feed, INP0 and INP1. Both feeds are active during operation, but both feeds might or might not be providing current. Move the input mode DIP switch to the on or off position to determine the power supply feeds (see Table 3 and Figure 8). In addition, a PSM failure triggers the alarm LED on the craft interface. Each PDM has an LED per feed indicating whether the feed is active or not, or whether the feed is connected properly, see MX2008 DC Power (-48 V) System Electrical Specifications.

Table 3: DIP Switch Positions on the DC (-48 V) PSM

Left Switch Position

Right Switch Position

Input Source

Off

Off

None

On

Off

Input 0 (INP0)

Off

On

Input 1 (INP1)

On

On

Both Input 0 and Input 1

Figure 8: Selecting Input Feed on the DC (-48 V) Power Supply ModuleSelecting Input Feed on the DC (-48 V) Power Supply Module

MX2000 DC Power Supply Module (240 V China) Description

The MX2008 supports a DC power system. The 240 V China DC power system operates with nine feeds. A total of nine feeds are required to fully power the MX2008. Another nine feeds are required to provide feed redundancy (a total of 18 feeds In the DC power configuration, the router contains up to nine DC PSMs located at the rear of the chassis in slots PSM0 through PSM8, (left to right). The DC PSMs in slots PSM0 through PSM8 provide power to the all router components including MPCs in slot 0 through 9, RCBs in slot 0 and 1, SFBs in slot 0 through 7, and fan trays 0 and 1.

Note:

The MX2008 systems configured for DC (240 V China) input power must use only DC (240 V China) PDMs and DC PSMs. AC and DC PSMs or PDMs must not be mixed within a single system.

Up to nine PSMs may be connected in parallel to increase available system power across MPCs as needed and provide redundancy. MX2008 DC Power Supply Module (-48 V) Description) shows the DC PSM.

Figure 9: DC Power Supply Module (240 V China)DC Power Supply Module (240 V China)

The DC power system is feed redundant. Each DC PSM can be connected to two separate feeds from different sources that are used to provide feed redundancy. If two feeds are connected, PSM input power will be drawn from the feed with the higher voltage present. There are two PDMs per power subsystem capable of carrying nine feeds each. Connect feeds from one source to one PDM and feeds from the other source to the second PDM of the power subsystem. The primary input of the PSM is a dual redundant feed, INP0 and INP1. Both feeds are active during operation, but both feeds may or may not be providing current. Move the input mode DIP switch to the on or off position to determine the power supply feeds (see MX2008 DC Power Supply Module (-48 V) Description and MX2008 DC Power Supply Module (-48 V) Description). In addition, a PSM failure triggers the alarm LED on the craft interface. Each PDM has an LED per feed indicating whether the feed is active or not, or whether the feed is connected properly, see MX2008 Router DC (240 V China) System Electrical Specifications.

Table 4: DIP Switch Positions on the DC (240 V China) PSM

Left Switch Position

Right Switch Position

Input Source

Off

Off

None

On

Off

Input 0 (INP0)

Off

On

Input 1 (INP1)

On

On

Both Input 0 and Input 1

Figure 10: Selecting Input Feed on the DC Power Supply Module (240 V China)Selecting Input Feed on the DC Power Supply Module (240 V China)

MX2008 DC Power Supply Module LEDs

Each DC PSM (-48 V and 240 China) faceplate contains four LEDs. These LEDs are described in Table 5. Nine bicolor LEDs, labeled 0 through 8 for the nine PSMs, are located in the center of the craft interface.

The primary input of the PSM is a dual redundant feed, INP0 and INP1. Both feeds are active during operation, but both feeds might or might not be providing current. In addition, a PSM failure triggers the alarm LED on the craft interface.

Table 5: MX2008 DC Power Supply Module LEDs

Label

Color

State

Description

PWR OK

Green

On

PSM is functioning normally with no alarms.

Yellow

On

PSM controller is off with both INP0 and INP1 voltage out of range.

Off

PSM is not functioning normally or the PSM controller is off.

FAULT

Red

On

PSM is not functioning normally or the DC input voltage of one or more feeds is out of range.

Off

PSM is functioning normally or both the DIP switches are set to off.

INP0

Green

On

DC input is within required voltage range and the DIP switch is set to on.

Yellow

On

DC input is detected but voltage is out of range.

Off

DC input to the PSM is not present.

INP1

Green

On

DC input is within required voltage range and the DIP switch is set to on.

Yellow

On

DC input is detected but voltage is out of range.

Off

DC input to the PSM is not present.

MX2008 DC Power Requirements

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

Table 6 lists the FRU power requirements for SFBs, RCBs, MPCs, and MICs. In addition, Table 6 lists the MPC power requirements with MICs and optics at various operating temperatures.

Typical power represents power under certain temperatures and normal operating conditions.

For PDMs with 60 A feeds, we recommend that you select the 60 A  @ –48 VDC switch for each input.

For PDMs with 80 A feeds, we recommend that you select the 80 A @ –48 VDC switch for each input.

Note:

The 240 V China DC PDMs do not have a switch selection.

If you do not plan to provision as recommended above, you can use the information in Table 6 to calculate the power consumption for your hardware configuration.

Note:

Unlike all the other MPCs, MPC6E, MPC8E, and MPC9E does not require an adapter card (ADC) to house the MPC in the MX2008 router.

Table 6: FRU DC Power Requirements

Component

Model Number

Maximum Power Requirement

Switch Fabric Boards (SFBs)

MX2008 SFB2

MX2008-SFB2

100 W (Typical)

110 W at 55° C

100 W at 40° C

95 W at 25° C

Fan Trays

Fan Trays

MX2000-FANTRAY-S

1500 W (Typical)

1700 W at 55° C

1500 W at 40° C

350 W at 25° C

Adapter Cards

ADC

MX2000-LC-ADAPTER

150 W

Routing Control Board (RCB)

RCB

REMX2008-X8-64G

100 W (Typical)

120 W at 55° C

100 W at 40° C

95 W at 25° C

MPCs

16x10GE MPC (seeMPC-3D-16XGE-SFPP)

MPC-3D-16XGE-SFPP

440 W at 55° C ambient

MPC1 (see MPC1)

MX-MPC1-3D

MX-MPC1E-3D

165 W

With MICs and optics:

239 W at 55° C

227 W at 40° C

219 W at 25° C

MPC1 Q (see MPC1 Q)

MX-MPC1-3D-Q

MX-MPC1E-3D-Q

175 W

With MICs and optics:

249 W at 55° C

237 W at 40° C

228 W at 25° C

MPC2 (see MPC2)

MX-MPC2-3D

MX-MPC2E-3D

274 W

With MICs and optics:

348 W at 55° C

329 W at 40° C

315 W at 25° C

MPC2 Q (see MPC2 Q)

MPC2 EQ (see MPC2 EQ)

MX-MPC2-3D-Q

MX-MPC2-3D-EQ

MX-MPC2E-3D-Q

MX-MPC2E-3D-EQ

294 W

With MICs and optics:

368 W at 55° C

347 W at 40° C

333 W at 25° C

MCP2E P (see MPC2E P)

MX-MPC2E-3D-P

294 W

With MICs and optics:

368 W at 55° C

347 W at 40° C

333 W at 25° C

MPC3E (see MPC3E)

MX-MPC3E-3D

440 W

With MICs and optics:

520 W at 55° C, two 40 W MICs

420 W at 40° C, two CFP MICs with LR4 optics

408 W at 25° C, two CFP MICs with LR4 optics

32x10GE MPC4E (see 32x10GE MPC4E)

MX-MPC4E-3D-32XGE-SFPP

610 W

With MICs and optics:

610 W at 55° C, two 40 W MICs

560 W at 40° C, two CFP MICs with LR4 optics

550 W at 25° C, two CFP MICs with LR4 optics

2x100GE + 8x10GE MPC4E (see 2x100GE + 8x10GE MPC4E)

MX-MPC4E-2CGE-8XGE

610 W

With MICs and optics:

610 W at 55° C, two 40 W MICs

550 W at 40° C, two CFP MICs with LR4 optics

530 W at 25° C, two CFP MICs with LR4 optics

6x40GE + 24x10GE MPC5E

6x40GE + 24x10GE MPC5EQ

MPC5E-40G10G

MPC5EQ-40G10G

With optics:

607 W at 55° C

541 W at 40° C

511 W at 25° C

2x100GE + 4x10GE MPC5E

2x100GE + 4x10GE MPC5EQ

MPC5E-100G10G

MPC5EQ-100G10G

With optics:

607 W at 55° C

541 W at 40° C

511 W at 25° C

MPC6E

MX2K-MPC6E

1088 W with MICs and optics

MPC7E-MRATE

MPC7E-MRATE

400 W (Typical)

545 W at 55° C

465 W at 40° C

440 W at 25° C

MPC8E

(without MICs)

MX2K-MPC8E

688 W (Typical)

805 W at 55° C

720 W at 40° C

690 W at 25° C

MPC9E

(without MICs)

MX2K-MPC9E

838 W (Typical)

1018 W at 55° C

870 W at 40° C

840 W at 25° C

MICs

ATM MIC with SFP

MIC-3D-8OC3-2OC12-ATM

35 W

Gigabit Ethernet MIC with SFP

MIC-3D-20-GE-SFP

37 W

10-Gigabit Ethernet MIC with XFP

2-Port: MIC-3D-2XGE-XFP

4-Port: MIC-3D-4XGE-XFP

2-Port: 29 W

4-Port: 37 W

10-Gigabit Ethernet MIC with SFP+

MIC6-10G

74 W

With optics:

53 W at 55° C, 40° C and 25° C with 10G BASE-SR and 10G BASE-LR optics

66 W at 55° C, 40° C and 25° C with 10G BASE-ER optics

74 W at 55° C, 40° C and 25° C with 10G BASE-ZR optics

10-Gigabit Ethernet DWDM OTN MIC

MIC6-10G-OTN

84 W

With optics:

63 W at 55° C with 10G BASE-LR OTN optics

63 W at 40° C with 10G BASE-LR OTN optics

63 W at 25° C with 10G BASE-LR OTN optics

40-Gigabit Ethernet MIC with QSFPP

MIC3-3D-2X40GE-QSFPP

18 W

100-Gigabit Ethernet MIC with CFP

MIC3-3D-1X100GE-CFP

40 W

100-Gigabit Ethernet MIC with CXP

MIC3-3D-1X100GE-CXP

20 W

100-Gigabit Ethernet MIC with CFP2

MIC6-100G-CFP2

104 W

With optics:

94 W at 55° C with 100G BASE-LR4 OTN optics

86 W at 40° C with 100G BASE-LR4 OTN optics

74 W at 25° C with 100G BASE-LR4 OTN optics

100-Gigabit Ethernet MIC with CXP

MIC6-100G-CXP

57 W

49 W at 55° C with CXP SR10 optics

49 W at 40° C with CXP SR10 optics

49 W at 25° C with CXP SR10 optics

100-Gigabit DWDM OTN MIC with CFP2

MIC3-100G-DWDM

With optics:

91 W at 55° C

83 W at 25° C

SONET/SDH OC3/STM1 Multi-Rate MIC

4-Port: MIC-3D-4OC3OC12-1OC48

8-Port: MIC-3D-8OC3OC12-4OC48

4-Port:

24 W at 55° C

22.75 W at 40° C

21.5 W at 25° C

8-Port:

29 W at 55° C

27.75 W at 40° C

26.5 W at 25° C

OC192/STM64 MIC with XFP

MIC-3D-1OC192-XFP

41 W at 55° C

38.5 W at 40° C

36 W at 25° C

Channelized SONET/SDH OC3/STM1 Multi-Rate MIC

4-Port: MIC-3D-4CHOC3-2CHOC12

8-Port: MIC-3D-8CHOC3-4CHOC12

4-Port:

41 W at 55° C

40 W at 40° C

39 W at 25° C

8-Port:

52 W at 55° C

50.5 W at 40° C

49 W at 25° C

Channelized OC48/STM16 MIC with SFP

MIC-3D-1CHOC48

56.5 W at 55° C

54.5 W at 40° C

53 W at 25° C

Tri-Rate MIC

MIC-3D-40GE-TX

41 W

MIC MRATE

MIC-MRATE

  • When installed into MPC8E: 1.250 A @ 48 V (60 W)

  • When installed into MPC9E: 1.771 A @ 48 V (85 W)

DS3/E3 MIC

MIC-3D-8DS3-E3

MIC-3D-8CHDS3-E3-B

36 W at 55° C

35 W at 40° C

34 W at 25° C

Channelized OC3/STM1 (Multi-Rate) Circuit Emulation MIC with SFP

MIC-3D-4COC3-1COC12-CE

33.96 W

MX2008 DC Power Distribution Description (-48 V)

Most sites distribute DC power through a main conduit that leads to frame-mounting DC power distribution panels, one of which might be located at a location near the rack that houses the router. A pair of cables (one input and one return) connects each set of PDM input terminal studs to the power distribution panel.

The PSMs can be connected to two separate feeds from different sources that are used for feed redundancy. There are two PDMs located in slots PDM0/Input0 and PDM1/Input1 that are capable of carrying seven to nine feeds each. Each feed is connected from one source to one PDM and feeds from the other source to the second PDM of the DC power system. This configuration balances power draw for the system by using the commonly deployed A/B feed redundancy.

Each system provides N+1 PSM redundancy along with N+N feed redundancy. If both DC feeds are available, operating power draws from the feed with higher voltage. These feeds are set by the input mode DIP switch located on the DC PSM (see MX2008 DC Power Supply Module (-48 V) Description). Each set of power cables powers a single DC PSM and is capable of delivering 2500 W of power if 80-A feeds are connected. If feeds that connect to one PDM fail in a redundant configuration, the other feed starts to provide full power.

Figure 11 shows a typical DC source cabling arrangement.

Figure 11: Typical DC Source Cabling to the RouterTypical DC Source Cabling to the Router

All DC PSMs in a subsystem share the load. If one PSM fails in a redundant configuration, the remaining PSMs provide power to FRUs. Up to nine PSMs might be required to supply power to a fully configured router. A portion of power from each zone is reserved to power critical FRUs. These FRUs allow the system to operate even if power to a complete zone fails.

CAUTION:

You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (-) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the terminal studs on each PDM.

Warning:

For field-wiring connections, use copper conductors only.

CAUTION:

Power cords and cables must not block access to device components or drape where people could trip on them.

MX2008 DC Power Distribution Description (240 V China)

Most sites distribute DC power through a main conduit that leads to frame-mounting DC power distribution panels, one of which might be located at a location near the rack that houses the router. A pair of cables (one input and one return) connects each set of PDM input terminal studs to the power distribution panel.

The PSMs can be connected to two separate feeds from different sources that are used for feed redundancy. There are two PDMs located in slots PDM0/Input0 and PDM1/Input1 that are capable of carrying seven to nine feeds each. Each feed is connected from one source to one PDM and feeds from the other source to the second PDM of the DC power system. This configuration balances power draw for the system by using the commonly deployed A/B feed redundancy.

Each system provides N+1 PSM redundancy along with N+N feed redundancy. If both DC feeds are available, operating power draws from the feed with higher voltage. These feeds are set by the input mode DIP switch located on the DC PSM (see MX2000 DC Power Supply Module (240 V China) Description). Each set of power cables powers a single DC PSM and is capable of delivering 2500 W of power if 20 A 240 V source is connected. If feeds that connect to one PDM fail in a redundant configuration, the other feed starts to provide full power.

Figure 12 shows a typical DC source cabling arrangement.

Figure 12: Typical DC Source Cabling to the RouterTypical DC Source Cabling to the Router

All DC PSMs in a subsystem share the load. If one PSM fails in a redundant configuration, the remaining PSMs provide power to FRUs. Up to nine PSMs might be required to supply power to a fully configured router. A portion of power from each zone is reserved to power critical FRUs. These FRUs allow the system to operate even if power to a complete zone fails.

CAUTION:

You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (-) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the terminal studs on each PDM.

CAUTION:

The two input sources must have similar grounding type because the PSM can see 480 V if one source has positive ground (-240 V), and the other source has negative ground (+240 V). This might damage the PSM.

Warning:

For field-wiring connections, use copper conductors only.

CAUTION:

Power cords and cables must not block access to device components or drape where people could trip on them.

MX2008 DC Power (-48 V) System Electrical Specifications

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

Table 7 lists the DC power system electrical specifications.

Table 7: DC (-48 V) PSM Electrical Specifications per Input Configurations

Item

Specification

Maximum input current rating input voltage @ –40 VDC to –72 VDC

60 A (for 2100 W output)

73 A (for 2500 W output)

Maximum output power

2100 W @ 60 A

2500 W @ 73 A

Redundancy

N+1 PSM

N+N feed redundancy

DC input voltage

–40 VDC to –72 VDC

DC nominal input current @ 48 VDC IN

49 A (for 2100 W output)

59 A (for 2500 W output)

Maximum DC output @ 52 VDC (upper and lower cage)

2500 W

DC standby output @ 5 VDC

30 W

Efficiency

Note:

This value is within load range 17–67% and nominal input voltage at 48 VDC.

91%

DC Power Supply Input Fuses

The DC (-48 V) PSM has a power supply input fuse in the negative terminals of both INP0 and INP1. Table 8 lists the electrical specification for this fuse.

Table 8: Electrical Specifications for the DC Power Supply Input Fuse

Electrical Characteristic

Value

Fuse

Littelfuse FUSE M P 80A 170VDC E, P/N TLS080LS

Voltage Rating

170 Vdc

Ampere Range

80 A

Interrupting Rating

100 kA

Approvals

UL Recognized (File: E71611)

Construction

Body: Glass melamine

Caps: Silver-plated brass

Environmental

RoHS Compliant, Lead (Pb) Free

MX2008 Router DC (240 V China) System Electrical Specifications

Table 9 lists the DC power system electrical specifications.

Table 9: DC PSM (240 V China) Electrical Specifications Per Input Configurations

Item

Specification

Maximum input current rating input voltage @ 190 - 290 VDC

16 A (for 2500 W output)

Maximum output power

2500 W @ 190 V/16 A

Redundancy

N+1 PSM

N+N feed redundancy

DC input voltage

190 VDC to 290 VDC

DC nominal input current @ 240 VDC IN

14 A (for 2500 W output)

Maximum DC output @ 52 VDC (upper and lower cage)

2500 W

DC standby output @ 5 VDC

30 W

Efficiency

Note:

This value is within load range 17-67% and nominal input voltage at 240 VDC.

91%

DC Power Supply Input Fuses

The DC PSM has a power supply input fuse in the negative terminals of both INP0 and INP1. Table 10 lists the electrical specification for this fuse.

Table 10: Electrical Specifications for the DC Power Supply (240 V China) Input Fuse

Electrical Characteristic

Value

Fuse

Fuse Walter MHP-20

Voltage Rating

500 Vdc

Ampere Range

20 A

Interrupting Rating

20 kA

Approvals

UL Recognized (File: E71611)

Construction

Body: Glass melamine

Caps: Silver-plated brass

Environmental

RoHS Compliant, Lead (Pb) Free

DC Power (-48 V) Circuit Breaker Requirements for the MX2008 Router

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

To operate a maximally or minimally configured DC-powered router, you must use a dedicated circuit breaker for each input DC feed. The circuit breaker must have the following specifications:

  • Breaker Type: Hydraulic Magnetic

  • Voltage Rating: Up to 125VDC

  • Current Rating: 80A DC

  • Delay Feature: DC Short Delay

  • Interrupting Rating : 5000A

  • Number of Poles: Single

DC Power (240 V China) Circuit Breaker Requirements for the MX2000 Router

For PDMs, if you plan to operate a maximally configured DC-powered router, we recommend that you provision at least 20 A  @ 240 VDC (nominal) for each DC input to the system. Use a customer site 2 pole circuit breaker rated according to respective National Electrical Code and customer site internal standards to maintain proper level of protection for the current specified above.

If you plan to operate a DC-powered router at less than the maximum configuration, we recommend that you provision a 2 pole circuit breaker according to respective National Electrical Code and customer site internal standards to maintain proper level of protection for the current specified above or each DC power supply rated for at least 125% of the continuous current that the system draws at 240 VDC.

DC Power Cable Specifications for the MX2008 Router

Note:

The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.

The cable lugs attach to the terminal studs of each PDM (see Figure 13).

Note:

The MX2008 supports 4-AWG DC power cable lugs for 80-A input and 60-A input.

Figure 13: 4-AWG DC Power Cable Lug 4-AWG DC Power Cable Lug
CAUTION:

Before you install the router, a licensed electrician must attach a cable lug to the grounding and power cables that you supply. A cable with an incorrectly attached lug can damage the router.

CAUTION:

The router is installed in restricted access location. It has a separate protective earthing terminal (Metric [–M6] and English [–¼-20] screw ground lugs) provided on the chassis in addition to the grounding pin of the power supply cord. This separate protective earth terminal must be permanently connected to earth.

Table 11 summarizes the specifications for the DC power cables, which you must supply.

Table 11: DC Power Cable Specifications

Cable Type

Quantity and Specification

Power

Eighteen pairs of 4-AWG (21.2 mm2), used with 60-A or 80-A PDM. Minimum 75°C wire, or as required by the local code.

You can select 60-A or 80-A input feed capacity on the DC PDM by setting the DIP switch on the PDM to the rated amperage of the DC power input feeds.

CAUTION:

You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the terminal studs on each PDM.