Power Requirements for an MX240 Router

The following tables list the MX240 component power requirements.Table 1 lists the MX240 base system power requirements. Table 2 lists the Switch Control Board (SCB) power requirements. Table 3 lists the FRU power requirements for Routing Engines, Modular Port Concentrators (MPCs), Modular Interface Cards (MICs), and Dense Port Concentrators (DPCs).

Table 1: MX240 Common Component Power Requirements

Component

Maximum Power Requirement (Watts)

Base system

40 W

Normal-capacity cooling system

70 W

High-capacity cooling system

85 W

Note:

The power for the cooling system comes from a different tap on the power supply, reserved for the cooling system only. The cooling system power requirement does not need to be deducted from the output power budget of the power supply.

Table 2: Maximum Power Consumption for SCB Models (MX240)

SCB Model

Ambient Temperature

Maximum Power Consumption

SCB-MX

55°C

40°C

25C°

185 W

160 W

155 W

SCBE-MX

55°C

40°C

25C°

160 W

130 W

120 W

SCBE2-MX

55°C

40°C

25C°

185 W

160 W

155 W

SCBE3-MX

55°C

40°C

25C°

275 W (SCB 0 (Primary); 295 W SCB 1 (Backup)

260 W (SCB 0 (Primary); 285 W SCB 1 (Backup)

245 W (SCB 0 (Primary); 265 W SCB 1 (Backup)

Table 3: FRU Power Requirements

Component

Part Number

Maximum Power Requirement

Routing Engines

 

RE-S-X6-64G

RE-S-X6-128G

110 W

 

RE-S-1300-2048 (EOL’d)

RE-S-2000-4096 (EOL’d)

RE-S-1800 (all variants)

90 W

Fixed Configuration Modular Port Concentrators (MPC)

MPC-3D-16XGE-SFPP

MPC-3D-16XGE-SFPP

MPC-3D-16XGE-SFPP-R-B

440 W at 131° F (55° C) ambient

423 W at 77° F (25° C) ambient

Multiservices MPC

MS-MPC-128G

590 W

32x10GE MPC4E

MPC4E-3D-32XGE-SFPP

610 W

With optics:

607 W at 131° F (55° C), with SFPP ZR optics

584 W at 40° C, with SFPP ZR optics

565 W at 77° F (25° C), with SFPP ZR optics

2x100GE + 8x10GE MPC4E

MPC4E-3D-2CGE-8XGE

610 W

With optics:

607 W at 131° F (55° C), with SFPP ZR and CFP LR4 optics

584 W at 104° F (40° C), with SFPP ZR and CFP LR4 optics

565 W at 77° F (25° C), with SFPP ZR and CFP LR4 optics

6x40GE + 24x10GE MPC5E

6x40GE + 24x10GE MPC5EQ

MPC5E-40G10G

MPC5EQ-40G10G

With optics:

607 W at 131° F (55° C)

541 W at 104° F (40° C)

511 W at 77° F (25° C)

2x100GE + 4x10GE MPC5E

2x100GE + 4x10GE MPC5EQ

MPC5E-100G10G

MPC5EQ-100G10G

With optics:

607 W at 131° F (55° C)

541 W at 104° F (40° C)

511 W at 77° F (25° C)

MPC7E-MRATE

MPC7E-MRATE

With optics:

545 W at 131° F (55° C)

465 W at 104° F (40° C)

440 W at 77° F (25° C)

MPC10E-10C-MRATE

MPC10E-10C-MRATE

620 W at 131° F (55° C)

590 W at 104° F (40° C)

545 W at 77° F (25° C)

MPC10E-15C-MRATE

MPC10E-15C-MRATE

785 W at 104° F (40° C): 720 W at 77° F (25° C)

Modular Port Concentrators (MPC)

MPC1

MPC1E

MX-MPC1-3D

MX-MPC1E-3D

165 W

With MICs and optics:

239 W at 131° F (55° C)

227 W at 104° F (40° C)

219 W at 77° F (25° C)

MPC1 Q

MPC1E Q

MX-MPC1-3D-Q

MX-MPC1E-3D-Q

175 W

With MICs and optics:

249 W at 131° F (55° C)

237 W at 104° F (40° C)

228 W at 77° F (25° C)

MPC2

MPC2E

MX-MPC2-3D

MX-MPC2E-3D

274 W

With MICs and optics:

348 W at 131° F (55° C)

329 W at 104° F (40° C)

315 W at 77° F (25° C)

MPC2 Q

MPC2E Q

MPC2 EQ

MPC2E EQ

MX-MPC2-3D-Q

MX-MPC2E-3D-Q

MX-MPC2-3D-EQ

MX-MPC2E-3D-EQ

294 W

With MICs and optics:

368 W at 131° F (55° C)

347 W at 104° F (40° C)

333 W at 77° F (25° C)

MPC2E P

MX-MPC2E-3D-P

294 W

With MICs and optics:

368 W at 131° F (55° C)

347 W at 104° F (40° C)

333 W at 77° F (25° C)

MPC2E NG

MPC2E-3D-NG

474 W

With MICs and optics:

474 W at 131° F (55° C)

417 W at 104° F (40° C)

400 W at 77° F (25° C)

MPC2E NG Q

MPC2E-3D-NG-Q

529 W

With MICs and optics:

529 W at 131° F (55° C)

460 W at 104° F (40° C)

438 W at 77° F (25° C)

MPC3E

MX-MPC3E-3D

440W

With MICs and optics:

500 W at 131° F (55° C), two 40 W MICs

485 W at 104° F (40° C), two CFP MICs with LR4 optics

473 W at 77° F (25° C), two CFP MICs with LR4 optics

MPC3E-3D-NG

MPC3E-3D-NG

534  W

With MICs and optics:

534 W at 131° F (55° C)

485 W at 104° F (40° C)

461 W at 77° F (25° C)

MPC3E-3D-NG-Q

MPC3E-3D-NG-Q

583 W

With MICs and optics:

583 W at 131° F (55° C)

532 W at 104° F (40° C)

503 W at 77° F (25° C)

Modular Interface Cards (MIC)

ATM MIC with SFP

MPC4E-3D-2CGE-8XGE

610 W

With optics:

607 W at 131° F (55° C), with SFPP ZR and CFP LR4 optics

584 W at 40° C, with SFPP ZR and CFP LR4 optics

565 W at 77° F (25° C), with SFPP ZR and CFP LR4 optics

Gigabit Ethernet MIC with SFP

MIC-3D-20-GE-SFP

37 W

10-Gigabit Ethernet MICs with XFP

2-Port: MIC-3D-2XGE-XFP

4-Port: MIC-3D-4XGE-XFP

2-Port: 29 W

4-Port: 37 W

40-Gigabit Ethernet MIC with QSFP+

MIC3-3D-2X40GE-QSFPP

18 W

100-Gigabit Ethernet MIC with CFP

MIC3-3D-1X100GE-CFP

40 W

100-Gigabit Ethernet MIC with CFP2

MIC6-100G-CFP2

104 W

100-Gigabit Ethernet MIC with CXP

MIC3-3D-1X100GE-CXP

20 W

100-Gigabit Ethernet MIC with CXP (4 Ports)

MIC6-100G-CXP

57 W

100-Gigabit DWDM OTN MIC with CFP2

MIC3-100G-DWDM

With optics:

91 W at 131° F (55° C)

83 W at 77° F (25° C)

100-Gigabit DWDM OTN MIC with CFP2-ACO

MIC3-100G-DWDM

With optics:

91 W at 131° F (55° C)

83 W at 77° F (25° C)

Multiservices MIC

MS-MIC-16G

60 W

SONET/SDH OC3/STM1 (Multi-Rate) MICs with SFP

4-Port: MIC-3D-4OC3OC12-1OC48

4-Port:

24 W at 131° F (55° C)

22.75 W at 40° C

21.5 W at 77° F (25° C)

8-Port: MIC-3D-8OC3OC12-4OC48

8-Port:

29 W at 131° F (55° C)

27.75 W at 40° C

26.5 W at 77° F (25° C)

SONET/SDH OC192/STM64 MIC with XFP

MIC-3D-1OC192-XFP

41 W at 131° F (55° C)

38.5 W at 40° C

36 W at 77° F (25° C)

Channelized SONET/SDH OC3/STM1 (Multi-Rate) MICs with SFP

4-Port: MIC-3D-4CHOC3-2CHOC12

4-Port:

41 W at 131° F (55° C)

40 W at 40° C

39 W at 77° F (25° C)

8-Port: MIC-3D-8CHOC3-4CHOC12

8-Port:

52 W at 131° F (55° C)

50.5 W at 40° C

49 W at 77° F (25° C)

Tri-Rate MIC

MIC-3D-40GE-TX

41 W

DS3/E3 MIC

MIC-3D-8DS3-E3

MIC-3D-8CHDS3-E3-B

36 W at 131° F (55° C)

35 W at 40° C

34 W at 77° F (25° C)

Channelized E1/T1 Circuit Emulation MIC

MIC-3D-16CHE1-T1-CE

29.08 W at 131° F (55° C)

27.84 W at 40° C

26.55 W at 77° F (25° C)

Channelized OC3/STM1 (Multi-Rate) Circuit Emulation MIC with SFP

MIC-3D-4COC3-1COC12-CE

36.48 W at 131° F (55° C)

35.04 W at 40° C

33.96 W at 77° F (25° C)

Dense Port Concentrators (DPC)

Gigabit Ethernet DPC with SFP

DPC-R-40GE-SFP

335 W

Gigabit Ethernet Enhanced DPC with SFP

DPCE-R-40GE-SFP

DPCE-X-40GE-SFP

335 W

Gigabit Ethernet Enhanced Queuing IP Services DPCs with SFPGigabit Ethernet Enhanced Queuing Ethernet Services DPC with SFP

DPCE-R-Q-40GE-SFP

DPCE-X-Q-40GE-SFP

365 W

Gigabit Ethernet Enhanced Queuing IP Services DPCs with SFP

DPCE-R-Q-20GE-SFP

200 W

10-Gigabit Ethernet DPC with XFP

DPC-R-4XGE-XFP

310 W

10-Gigabit Ethernet Enhanced DPC with XFP

DPCE-R-2XGE-XFP

175 W

10-Gigabit Ethernet Enhanced DPCs with XFP

DPCE-R-4XGE-XFP

DPCE-X-4XGE-XFP

310 W

10-Gigabit Ethernet Enhanced Queuing Ethernet Services DPC with XFP

DPCE-R-Q-4XGE-XFP

DPCE-X-Q-4XGE-XFP

330 W

Multi-Rate Ethernet Enhanced Ethernet Services DPC with SFP and XFP

DPCE-R-20GE-2XGE

DPCE-X-20GE-2XGE

333 W

Multi-Rate Ethernet Enhanced Queuing IP Services DPC with SFP and XFP

DPCE-R-Q-20GE-2XGE

335 W

Tri-Rate Enhanced DPC or Tri-Rate Enhanced Ethernet Services DPC

DPCE-R-40GE-TX

DPCE-X-40GE-TX

320 W

Multiservices DPC

MS-DPC

265 W

Flexible PIC Concentrators (FPC)

FPC Type 2

MX-FPC2

190 W (with PICs and optics)

FPC Type 3

MX-FPC3

265 W (with PICs and optics)

Calculating Power Requirements for MX240 Routers

The information in this topic helps you determine which power supplies are suitable for various configurations, as well as which power supplies are not suitable because output power is exceeded. You determine suitability by subtracting the total power draw from the maximum output of the power supplies. Afterward, the required input power is calculated. Finally, you calculate the thermal output. A sample configuration is provided in Table 4.

We recommend that you provision power according to the maximum input current listed in the power supply electrical specifications (see AC Power Supply Electrical Specifications for the MX240 Router and DC Power Supply Electrical Specifications for the MX240 Router).

Use the following procedures to calculate the power requirement:

  1. Calculate the power requirement.

  2. Evaluate the power budget.

  3. Calculate input power.

  4. Calculate thermal output (BTUs) for cooling requirements.

The following sample configuration shows an MX240 router with:

  • Two 16-port 10-Gigabit Ethernet MPCs with SFP+

  • Two SCBs with two (redundant) RE-1800x2 routing engines

  • High-capacity cooling system

    Note:

    The high-capacity cooling system satisfies cooling requirements of MPCs, and must be used for proper cooling.

  1. Calculate the power requirements (usage) using the values in Power Requirements for an MX240 Router as shown in Table 4.

    Table 4: Sample Power Requirements for an MX240 Router

    Chassis Component

    Part Number

    Power Requirement

    Base system

    MX240BASE-AC-HIGH

    40 W

    High-capacity cooling system

    FANTRAY-MX240-HC

    85 W

    MPC - Slot 2 -

    MPC-3D-16XGE-SFPP-R-B

    440 W

    MPC - Slot 1

    MPC-3D-16XGE-SFPP-R-B

    440 W

    SCB 1/Slot 0

    SCBE2-MX with

    RE-S-1800X2-8G

    185 W

    90 W

    SCB 0

    SCBE2-MX with

    RE-S-1800X2-8G

    185 W

    90 W

    Total output power

    1555 W

    Output power excluding cooling system

    1470 W

  2. Evaluate the power budget. In this step, we check the total output power against the maximum output power of available power supply options.

    Note:

    The power for the cooling system comes from a different tap on the power supply, reserved for the cooling system only. The cooling system power requirement does not need to be deducted from the output power budget of the power supply.

    Table 5 lists the power supplies, their maximum output power, and unused power (or a power deficit). See DC Power Supply Electrical Specifications for the MX240 Router and AC Power Supply Electrical Specifications for the MX240 Router for more information about the MX240 power supply electrical specifications.

    Table 5: Calculating Power Budget

    Power Supply

    Maximum System Output Power

    Unused Power1

    MX240 AC Normal-capacity (low-line)

    2054 W

    654 W

    MX240 AC Normal-capacity (high-line)

    1590 W

    190 W

    MX240 AC High-capacity (low-line)

    2334 W

    934 W

    MX240 AC High-capacity (high-line)

    2050 W

    650 W

    MX240 DC Normal-capacity

    1600 W

    200 W

    MX240 DC High-capacity (DIP=0)

    2400 W

    1000 W

    MX240 DC High-capacity (DIP=1)

    2600 W

    1200 W

    1 For this configuration, output power excluding the cooling system is 1400 W.

  3. Calculate input power. In this step, the input power requirements for the example configuration are calculated. To do this, divide the total output requirement by the efficiency of the power supply as shown in Table 6.

    Table 6: Calculating Input Power Examples

    Power Supply

    Power Supply Efficiency1

    Input Power Requirement2

    MX240 AC Normal-capacity (high-line)

    85 %

    1747 W

    MX240 AC High-capacity (high-line)

    89 %

    1669 W

    MX240 DC Normal-capacity

    ~98 %

    1515 W

    MX240 DC High-capacity

    ~98 %

    1515 W

    1 These values are at full load and nominal voltage.

    2 For this configuration, total power is 1485 W.

  4. Calculate thermal output (BTUs). To calculate this, multiply the input power requirement (in watts) by 3.41. See Table 7.

    Table 7: Calculating Thermal Output

    Power Supply

    Thermal Output (BTUs per hour)

    MX240 AC Normal-capacity (high-line)

    1747 * 3.41 = 5957 BTU/hr

    MX240 AC High-capacity (high-line)

    1669 * 3.41 = 5576 BTU/hr

    MX240 DC Normal-capacity

    1515 * 3.41 = 5166 BTU/hr

    MX240 DC High-capacity

    1515 * 3.41 = 5166 BTU/hr