Troubleshooting EX9200 Components

Troubleshooting the Cooling System in an EX9200 Switch

Problem

Description

The fans in the fan tray are not functioning normally.

Cause

Solution

Follow these guidelines to troubleshoot the fans:

  • Check the fan LEDs and alarm LEDs on the craft interface.

    If the major alarm LED on the craft interface glows, use the CLI to get information about the source of an alarm condition:

    If the CLI output lists only one fan failure and the other fans are functioning normally, the fan is most likely faulty and you must replace the fan tray.

  • Place your hand near the exhaust vents at the side of the chassis to determine whether the fans are pushing air out of the chassis.

  • If a fan tray is removed, both a minor alarm and a major alarm occur.

  • The following conditions automatically cause the fans to run at full speed and also trigger the indicated alarm:

    • A fan fails (major alarm).

    • The switch temperature exceeds the temperature warm threshold (minor alarm).

    • The temperature of the switch exceeds the temperature hot threshold (major alarm and automatic shutdown of the power supplies).

Troubleshooting Power Supplies in an EX9200 Switch

Problem

Description

The power system is not functioning normally.

Cause

Solution

  • Check the LEDs on each power supply faceplate.

    • If an AC power supply is correctly installed and functioning normally, the AC OK and DC OK LEDs light steadily, and the PS FAIL LED is not lit.

    • If a DC power supply is correctly installed and functioning normally, the PWR OK, BRKR ON, and INPUT OK LEDs glow steady green.

  • Issue the CLI show chassis environment pem command to check the status of installed power supplies. As shown in the sample output, the value Online in the rows labeled State must indicate that each of the power supplies is functioning normally.

    The output is of an EX9208 switch. The output is similar for EX9204 and EX9214 switches.

If a power supply is not functioning normally, perform the following steps to diagnose and correct the problem:

  • If a major alarm condition occurs, issue the show chassis alarms command to determine the source of the problem.

  • If all power supplies have failed, the system temperature might have exceeded the threshold, causing the system to shut down.

    Note:

    If the system temperature exceeds the threshold, Junos OS shuts down all power supplies so that no status is displayed.

    Junos OS also can shut down one of the power supplies for other reasons. In this case, the remaining power supplies provide power to the switch, and you can still view the system status through the CLI or display.

  • Check that the DC circuit breaker or AC input switch is in the on position and that the power supply is receiving power.

  • Verify that the source circuit breaker has the proper current rating. Each power supply must be connected to a separate source circuit breaker.

  • Verify that the AC power cord or DC power cables from the power source to the switch are not damaged. If the insulation is cracked or broken, immediately replace the cord or cable.

  • Connect the power supply to a different power source with a new power cord or power cables. If the power supply status LEDs indicate that the power supply is not operating normally, the power supply is the source of the problem. Replace the power supply with a spare.

Troubleshooting Line Cards in EX9200 Switches

Problem

Description

Line card is not functioning normally.

Solution

  • Monitor the LED labeled OK on the craft interface as soon as a line card is seated in an operating switch.

    The Routing Engine downloads the line card software to it under two conditions: the line card is present when the Routing Engine boots Junos OS, and the line card is installed and requested online through the CLI or the button on the front panel. The line card then runs diagnostics, during which the OK LED blinks. When the line card is online and functioning normally, the OK LED is lit green steadily.

  • Make sure the line card is properly seated in the midplane. Check that each ejector handle has been turned clockwise and is tight.

  • Check the OK/FAIL LED on the line card and OK and FAIL line card LEDs on the craft interface. When the line card is online and functioning normally, the OK LED is lit green steadily.

  • Issue the show chassis fpc command to check the status of installed line cards. As shown in the sample output, the value Online in the column labeled State indicates that the line card is functioning normally:

    Note:

    The show chassis fpc command displays the status of the line cards.

    For more detailed output, add the detail option. The following example does not specify a slot number, which is optional:

Troubleshooting Traffic Drops on EX9200-6QS Line Cards

Problem

Description

The EX9200-6QS line card drops all routed traffic, including both data plane and control plane traffic.

Environment

The switch in which the EX9200-6QS line card is installed runs Junos OS Release 14.2R1 and an IRB logical interface is configured on the line card as part of a VLAN.

Cause

On EX9200 switches, if an IRB logical interface is configured on an EX9200-6QS line card as part of a VLAN, any device that is connected through that interface is unable to route traffic outside of the subnet because the EX9200-6QS line card drops all ARP requests. This happens because even though the minimum Junos OS release that supports the EX9200-6QS line card is Junos OS Release 14.2R1, this release does not support a configuration that includes an IRB logical interface configured on an EX9200-6QS line card as part of a VLAN.

Solution

Upgrade Junos OS to the release specified in TSB16659.

Understand Alarm Types and Severity Levels on EX Series Switches

Note:

This topic applies only to the J-Web Application package.

Alarms alert you to conditions that might prevent normal operation of the switch. Before monitoring alarms on a Juniper Networks EX Series Ethernet switch, become familiar with the terms defined in Table 1.

Table 1: Alarm Terms

Term

Definition

alarm

Signal alerting you to conditions that might prevent normal operation. On a switch, the alarm signal is the ALM LED lit on the front of the chassis.

alarm condition

Failure event that triggers an alarm.

alarm severity

Seriousness of the alarm. If the Alarm (ALM) LED is red, this indicates a major alarm. If the Alarm LED is yellow or amber, this indicates a minor alarm. If the Alarm LED is unlit, there is no alarm or the switch is halted.

chassis alarm

Preset alarm triggered by a physical condition on the switch such as a power supply failure, excessive component temperature, or media failure.

system alarm

Preset alarm triggered by a missing rescue configuration or failure to install a license for a licensed software feature.

Note:

On EX6200 switches, a system alarm can be triggered by an internal link error.

Alarm Types

The switch supports these alarms:

  • Chassis alarms indicate a failure on the switch or one of its components. Chassis alarms are preset and cannot be modified.

  • System alarms indicate a missing rescue configuration. System alarms are preset and cannot be modified, although you can configure them to appear automatically in the J-Web interface display or the CLI display.

Alarm Severity Levels

Alarms on switches have two severity levels:

  • Major (red)—Indicates a critical situation on the switch that has resulted from one of the following conditions. A red alarm condition requires immediate action.

    • One or more hardware components have failed.

    • One or more hardware components have exceeded temperature thresholds.

    • An alarm condition configured on an interface has triggered a critical warning.

  • Minor (yellow or amber)—Indicates a noncritical condition on the switch that, if left unchecked, might cause an interruption in service or degradation in performance. A yellow or amber alarm condition requires monitoring or maintenance.

    A missing rescue configuration generates a yellow or amber system alarm.

Chassis Component Alarm Conditions on EX9200 Switches

This topic describes the chassis component alarm conditions on EX9200 switches.

Table 2 lists the alarms that the chassis components can generate on EX9200 Switches.

Table 2: Chassis Component Alarm Conditions on EX9200 Switches

Chassis Component

Alarm Condition

Alarm Severity

Remedy

Air filters

Change air filter.

Minor (yellow)

Replace the air filter.

Alternative media

The switch boots from an alternate boot device, the hard disk. The CompactFlash card is typically the primary boot device. The Routing Engine boots from the hard disk when the primary boot device fails.

Minor (yellow)

Open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

Craft interface

The craft interface has failed.

Major (red)

Replace the failed craft interface.

Line Cards

A line card is offline.

Minor (yellow)

Check the line card. Remove and reinstall the line card. If this fails, replace the failed card.

A line card has failed.

Major (red)

Replace the failed line card.

A line card has been removed.

Major (red)

Install a line card in the empty slot.

Modular Interface Cards (MICs)

A MIC is offline.

Minor (yellow)

Check the MIC. Remove and reinstall the MIC. If this fails, replace the failed card.

A MIC has failed.

Major (red)

Replace the failed MIC.

A MIC has been removed.

Major (red)

Install a MIC in the empty slot.

Fan trays

A fan tray has been removed from the chassis.

Major (red)

Install the missing fan tray.

One fan in the chassis is not spinning or is spinning below required speed.

Major (red)

Replace the fan tray.

A higher-cooling capacity fan tray is required when an MPC is installed on the chassis.

Minor (yellow)

Upgrade to a high-capacity fan tray.

Host subsystem

A host subsystem has been removed.

Minor (yellow)

Install a host subsystem in the empty slot.

A host subsystem has failed.

Major (red)

Replace the failed host subsystem.

Hot swapping

Too many hot-swap interrupts are occurring. This message generally indicates that a hardware component that plugs into the switch’s backplane from the front (generally, an FPC) is broken.

Major (red)

Replace the failed components.

Power supplies

A power supply has been removed from the chassis.

Minor (yellow)

Install a power supply in the empty slot.

A power supply has a high temperature.

Major (red)

Replace the failed power supply or power entry module.

A power supply input has failed.

Major (red)

Check power supply input connection.

A power supply output has failed.

Major (red)

Check power supply output connection.

A power supply has failed.

Major (red)

Replace the failed power supply.

Invalid AC power supply configuration.

Major (red)

When two AC power supplies are installed, install one power supply in an odd-numbered slot and the other power supply in an even-numbered slot.

Invalid DC power supply configuration.

Major (red)

When two DC power supplies are installed, install one power supply in an odd-numbered slot and the other power supply in an even-numbered slot.

AC and DC power supplies are installed.

Major (red)

Do not mix AC and DC power supplies.

Inadequate number of power supplies.

Major (red)

Install an additional power supply.

Switch Fabric Module (SF module)

An SF module has been removed.

Minor (yellow)

Install an SF module in the empty slot.

An SF module has failed.

Major (red)

Replace the failed SF module.

Routing Engine

Excessive framing errors on console port.

An excessive framing error alarm is triggered when the default framing error threshold of 20 errors per second on a serial port is exceeded.

A faulty serial console port cable might be connected to the device.

Minor (yellow)

Replace the serial cable connected to the device.

If the cable is replaced and no excessive framing errors are detected within 5 minutes from the last detected framing error, the alarm is cleared automatically.

Error in reading or writing hard disk.

Minor (yellow)

Reformat the hard disk and install the bootable image. If this fails, replace the failed Routing Engine.

Error in reading or writing CompactFlash card.

Minor (yellow)

Reformat the CompactFlash card and install the bootable image. If this fails, replace the failed Routing Engine.

System booted from the default backup Routing Engine. If you manually switched primary role, ignore this alarm condition.

Minor (yellow)

Install the bootable image on the default primary Routing Engine. If this fails, replace the failed Routing Engine.

System booted from hard disk.

Minor (yellow)

Install the bootable image on the CompactFlash card. If this fails, replace failed the Routing Engine.

CompactFlash card missing in boot list.

Major (red)

Replace the failed Routing Engine.

Hard disk missing in boot list.

Major (red)

Replace the failed Routing Engine.

Routing Engine failed to boot.

Major (red)

Replace the failed Routing Engine.

The Ethernet management interface (fxp0 or em0) on the Routing Engine is down.

Major (red)

  • Check the interface cable connection.

  • Reboot the system.

  • If the alarm recurs, open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

/var partition usage is high.

Minor (yellow)

Clean up the system file storage space on the switch. For more information, see Freeing Up System Storage Space.

/var partition is full.

Major (red)

Clean up the system file storage space on the switch. For more information, see Freeing Up System Storage Space.

Rescue configuration is not set.

Minor (yellow)

Use the request system configuration rescue save command to set the rescue configuration.

Feature usage requires a license or the license for the feature usage has expired.

Minor (yellow)

Install the required license for the feature specified in the alarm. For more information, see Understanding Software Licenses for EX Series Switches.

Temperature

The chassis temperature has exceeded 131° F (55° C), the fans have been turned on to full speed, and one or more fans have failed.

Minor (yellow)

  • Check room temperature.

  • Check air filter and replace it, if required.

  • Check airflow.

  • Replace the fan tray.

The chassis temperature has exceeded 149° F (65° C), and the fans have been turned on to full speed.

Minor (yellow)

  • Check room temperature.

  • Check air filter and replace it, if required.

  • Check airflow.

  • Check the fans.

The chassis temperature has exceeded 149° F (65° C), and a fan has failed. If this condition persists for more than four minutes, the switch shuts down.

Major (red)

  • Check room temperature.

  • Check air filter and replace it, if required.

  • Check airflow.

  • Check the fan.

Chassis temperature has exceeded 167° F (75° C). If this condition persists for more than four minutes, the switch shuts down.

Major (red)

  • Check room temperature.

  • Check air filter and replace it, if required.

  • Check airflow.

  • Check fan.

The temperature sensor has failed.

Major (red)

Open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

Backup Routing Engine Alarms

For switches with primary and backup Routing Engines, a primary Routing Engine can generate alarms for events that occur on a backup Routing Engine. Table 3 lists chassis alarms generated for events that occur on a backup Routing Engine.

Note:

Because the failure occurs on the backup Routing Engine, alarm severity for some events (such as Ethernet interface failures) is yellow instead of red.

Note:

For information about configuring redundant Routing Engines, see the Junos OS High Availability Library for Routing Devices.

Table 3: Backup Routing Engine Alarms

Chassis Component

Alarm Condition

Alarm Severity

Remedy

Alternative media

The backup Routing Engine boots from an alternate boot device, the hard disk. The CompactFlash card is typically the primary boot device. The Routing Engine boots from the hard disk when the primary boot device fails.

Minor (yellow)

Open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

Boot Device

The boot device (CompactFlash or hard disk) is missing in boot list on the backup Routing Engine.

Major (red)

Replace the failed backup Routing Engine.

Ethernet

The Ethernet management interface (fxp0 or em0) on the backup Routing Engine is down.

Minor (yellow)

  • Check the interface cable connection.

  • Reboot the system.

  • If the alarm recurs, open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

FRU Offline

The backup Routing Engine has stopped communicating with the primary Routing Engine.

Minor (yellow)

Open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

Hard Disk

Error in reading or writing hard disk on the backup Routing Engine.

Minor (yellow)

Reformat hard disk and install bootable image. If this fails, replace failed backup Routing Engine.

Multibit Memory ECC

The backup Routing Engine reports a multibit ECC error.

Minor (yellow)

  • Reboot the system with the board reset button on the backup Routing Engine.

  • If the alarm recurs, open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll free, US & Canada) or 1-408-745-9500 (from outside the United States).

Monitor System Log Messages

Purpose

Note:

This topic applies only to the J-Web Application package.

Use the monitoring functionality to filter and view system log messages for EX Series switches.

Action

To view events in the J-Web interface, select Monitor > Events and Alarms > View Events.

Apply a filter or a combination of filters to view messages. You can use filters to display relevant events. Table 4 describes the different filters, their functions, and the associated actions.

To view events in the CLI, enter the following command:

show log

Table 4: Filtering System Log Messages

Field

Function

Your Action

System Log File

Specifies the name of a system log file for which you want to display the recorded events.

Lists the names of all the system log files that you configure.

By default, a log file, messages, is included in the /var/log/ directory.

To specify events recorded in a particular file, select the system log filename from the list— for example, messages.

Select Include archived files to include archived files in the search.

Process

Specifies the name of the process generating the events you want to display.

To view all the processes running on your system, enter the CLI command show system processes.

For more information about processes, see the Junos OS Installation and Upgrade Guide.

To specify events generated by a process, type the name of the process.

For example, type mgd to list all messages generated by the management process.

Date From

To

Specifies the time period in which the events you want displayed are generated.

Displays a calendar that allows you to select the year, month, day, and time. It also allows you to select the local time.

By default, the messages generated during the last one hour are displayed. End Time shows the current time and Start Time shows the time one hour before End Time.

To specify the time period:

  • Click the Calendar icon and select the year, month, and date— for example, 02/10/2007.

  • Click the Calendar icon and select the year, month, and date— for example, 02/10/2007.

  • Click to select the time in hours, minutes, and seconds.

Event ID

Specifies the event ID for which you want to display the messages.

Allows you to type part of the ID and completes the remainder automatically.

An event ID, also known as a system log message code, uniquely identifies a system log message. It begins with a prefix that indicates the generating software process or library.

To specify events with a specific ID, type the partial or complete ID— for example, TFTPD_AF_ERR.

Description

Specifies text from the description of events that you want to display.

Allows you to use regular expressions to match text from the event description.

Note:

Regular expression matching is case-sensitive.

To specify events with a specific description, type a text string from the description with regular expression.

For example, type ^Initial* to display all messages with lines beginning with the term Initial.

Search

Applies the specified filter and displays the matching messages.

To apply the filter and display messages, click Search.

Reset

Resets all the fields in the Events Filter box.

To reset the field values that are listed in the Events Filter box, click Reset.

Generate Raw Report

Note:
  • Starting in Junos OS Release 14.1X53, a Raw Report can be generated from the log messages being loaded in the Events Detail table. The Generate Raw Report button is enabled after the event log messages start loading in the Events Detail table.

  • After the log messages are completely loaded in the Events Detail table, Generate Raw Report changes to Generate Report.

Generates a list of event log messages in nontabular format.

To generate a raw report:

  1. Click Generate Raw Report.

    The Opening filteredEvents.html window appears.

  2. Select Open with to open the HTML file or select Save File to save the file.

  3. Click OK.

Generate Report

Note:

Starting in Junos OS Release 14.1X53, a Formatted Report can be generated from event log messages being loaded in an Events Detail table. The Generate Report button appears only after event log messages are completely loaded in the Events Detail table. The Generate Raw Report button is displayed while event log messages are being loaded.

Generates a list of event log messages in tabular format, which shows system details, events filter criteria, and event details.

To generate a formatted report:

  1. Click Generate Report.

    The Opening Report.html window appears.

  2. Select Open with to open the HTML file or select Save File to save the file.

  3. Click OK.

Meaning

Table 5 describes the Event Summary fields.

Note:

By default, the View Events page in the J-Web interface displays the most recent 25 events, with severity levels highlighted in different colors. After you specify the filters, Event Summary displays the events matching the specified filters. Click the First, Next, Prev, and Last links to navigate through messages.

Table 5: Viewing System Log Messages

Field

Function

Additional Information

Process

Displays the name and ID of the process that generated the system log message.

The information displayed in this field is different for messages generated on the local Routing Engine than for messages generated on another Routing Engine (on a system with two Routing Engines installed and operational). Messages from the other Routing Engine also include the identifiers re0 and re1 that identify the Routing Engine.

Severity

Severity level of a message is indicated by different colors.

  • Unknown—Gray—Indicates no severity level is specified.

  • Debug/Info/Notice—Green—Indicates conditions that are not errors but are of interest or might warrant special handling.

  • Warning—Yellow or Amber—Indicates conditions that warrant monitoring.

  • Error—Blue—Indicates standard error conditions that generally have less serious consequences than errors in the emergency, alert, and critical levels.

  • Critical—Pink—Indicates critical conditions, such as hard-drive errors.

  • Alert—Orange—Indicates conditions that require immediate correction, such as a corrupted system database.

  • Emergency—Red—Indicates system panic or other conditions that cause the switch to stop functioning.

A severity level indicates how seriously the triggering event affects switch functions. When you configure a location for logging a facility, you also specify a severity level for the facility. Only messages from the facility that are rated at that level or higher are logged to the specified file.

Event ID

Displays a code that uniquely identifies the message.

The prefix on each code identifies the message source, and the rest of the code indicates the specific event or error.

The event ID begins with a prefix that indicates the generating software process.

Some processes on a switch do not use codes. This field might be blank in a message generated from such a process.

An event can belong to one of the following type categories:

  • Error—Indicates an error or failure condition that might require corrective action.

  • Event—Indicates a condition or occurrence that does not generally require corrective action.

Event Description

Displays a more detailed explanation of the message.

 

Time

Displays the time at which the message was logged.

 

Troubleshoot Temperature Alarms in EX Series Switches

Problem

Description

EX Series switches trigger a temperature alarm FPC 0 EX-PFE1 Temp Too Hot when the switch temperature becomes too hot.

Cause

Temperature sensors in the chassis monitor the temperature of the chassis. The switch triggers an alarm if a fan fails or if the temperature of the chassis exceeds permissible levels for some other reason.

Solution

When the switch triggers a temperature alarm such as the FPC 0 EX-PFE1 Temp Too Hot alarm, use the show chassis environment and the show chassis temperature-thresholds commands to identify the condition that triggered the alarm.

CAUTION:

To prevent the switch from overheating, operate it in an area with an ambient temperature within the recommended range. To prevent airflow restriction, allow at least 6 inches (15.2 cm) of clearance around the ventilation openings.

  1. Connect to the switch by using Telnet, and issue the show chassis environment command. This command displays environmental information about the switch chassis, including the temperature. The command also displays information about the fans, power supplies, and Routing Engines. Following is a sample output on an EX9208 switch. The output is similar on other EX Series switches.

    show chassis environment (EX9208 Switch)

    Table 6 lists the output fields for the show chassis environment command. The table lists output fields in the approximate order in which they appear.

    Table 6: show chassis environment Output Fields

    Field Name

    Field Description

    Class

    Information about the category or class of chassis component:

    • Temp: Temperature of air flowing through the chassis in degrees Celsius (°C) and degrees Fahrenheit (°F)

    • Fans: Information about the status of fans and blowers

    Item

    Information about the chassis components:

    • Flexible PIC Concentrators (FPCs)—that is, the line cards

    • Control Boards (CBs)

    • Routing Engines

    • Power entry modules (PEMs)—that is, the power supplies

    Status

    Status of the specified chassis component. For example, if Class is Fans, the fan status can be:

    • OK: The fans are operational.

    • Testing: The fans are being tested during initial power-on.

    • Failed: The fans have failed or the fans are not spinning.

    • Absent: The fan tray is not installed.

    Measurement

    Depends on the Class. For example, if Class is Temp, indicates the temperature in degrees Celsius (°C) and degrees Fahrenheit (°F). If the Class is Fans, indicates actual fan RPM.

  2. Issue the command show chassis temperature-thresholds . This command displays the chassis temperature threshold settings. The following is a sample output on an EX9208 switch. The output is similar on other EX Series switches.

    show chassis temperature-thresholds (EX9208 Switch)

    Table 7 lists the output fields for the show chassis temperature-thresholds command. The table lists output fields in the approximate order in which they appear.

    Table 7: show chassis temperature-thresholds Output Fields

    Field Name

    Field Description

    Item

    Chassis component. You can configure the threshold information for components such as the chassis, the Routing Engines, and FPC for each slot in each FRU to display in the output. By default, information is displayed only for the chassis and the Routing Engines.

    Fan speed

    Temperature thresholds, in degrees Celsius, for the fans to operate at normal and at high speed.

    • Normal—The temperature threshold at which the fans operate at normal speed and when all the fans are present and functioning normally.

    • High—The temperature threshold at which the fans operate at high speed or when a fan has failed or is missing.

    Note:

    An alarm is triggered when the temperature exceeds the threshold settings for a yellow, amber, or red alarm.

    Yellow or amber alarm

    Temperature threshold, in degrees Celsius, that triggers a yellow or amber alarm.

    • Normal—The temperature threshold that must be exceeded on the device to trigger a yellow or amber alarm when the fans are running at full speed.

    • Bad fan—The temperature threshold that must be exceeded on the device to trigger a yellow or amber alarm when one or more fans have failed or are missing.

    Red alarm

    Temperature threshold, in degrees Celsius, that triggers a red alarm.

    • Normal—The temperature threshold that must be exceeded on the device to trigger a red alarm when the fans are running at full speed.

    • Bad fan—The temperature threshold that must be exceeded on the device to trigger a red alarm when one or more fans have failed or are missing.

    Fire shutdown

    Temperature threshold, in degrees Celsius, at which the switch shuts down in case of fire.

When a temperature alarm is triggered, you can identify the condition that triggered it by running the show chassis environment command to display the chassis temperature values for each component and comparing those with the temperature threshold values. You can display the temperature threshold values by running the show chassis temperature-thresholds command.

For example, for FPC 3:

  • If the temperature of FPC 3 exceeds 55° C, the output indicates that the fans are operating at a high speed (no alarm is triggered).

  • If the temperature of FPC 3 exceeds 65° C, a yellow alarm is triggered to indicate that one or more fans have failed.

  • If the temperature of FPC 3 exceeds 75° C, a yellow alarm is triggered to indicate that the temperature threshold limit is exceeded.

  • If the temperature of FPC 3 exceeds 80° C, a red alarm is triggered to indicate that one or more fans have failed.

  • If the temperature of FPC 3 exceeds 105° C, a red alarm is triggered to indicate that the temperature threshold limit is exceeded.

  • If the temperature of FPC 3 exceeds 110° C, the switch is powered off.

Table 8 lists the possible causes for the switch to generate a temperature alarm. It also lists the respective remedies.

Table 8: Causes and Remedies for Temperature Alarms

Cause

Remedy

Ambient temperature is above threshold temperature.

Ensure that the ambient temperature is within the threshold temperature limit. See Environmental Requirements and Specifications for EX Series Switches.

Fan module or fan tray has failed.

Perform the following steps:
  1. Check the fan.

  2. Replace the faulty fan module or fan tray.

  3. If the above two checks show no problems, open a support case using the Case Manager link at https://www.juniper.net/support/ or call 1-888-314-5822 (toll-free within the United States and Canada) or 1-408-745-9500 (from outside the United States).

Restricted airflow through the switch due to insufficient clearance around the installed switch.

Ensure that there is sufficient clearance around the installed switch.

Change History Table

Feature support is determined by the platform and release you are using. Use Feature Explorer to determine if a feature is supported on your platform.

Release
Description
14.1X53
Starting in Junos OS Release 14.1X53, a Raw Report can be generated from the log messages being loaded in the Events Detail table.
14.1X53
Starting in Junos OS Release 14.1X53, a Formatted Report can be generated from event log messages being loaded in an Events Detail table.