Help us improve your experience.

Let us know what you think.

Do you have time for a two-minute survey?

 
 

PTX10008 Power Planning for JNP10008-SF Switch Fabric

Use this information to calculate the power consumption for the PTX10008 in a JNP10008-SF switch fabric and plan your configuration’s power requirements.

Power Requirements for PTX10008 Components in a JNP10008-SF Fabric

Table 1 lists the power requirements for the PTX10008 router running the JNP10008-SF switch fabric under typical voltage conditions and optics.

Table 1: Power Consumption JNP10008-SF Fabric Systems

Component

Description

At 25° C

At 55° C

JNP10008-SF

PTX10008 Switch Interface Board

170 W

235 W

JNP10008-FAN

PTX10008 fan tray

225 W

475 W

JNP10008-FAN2

PTX10008 enhanced fan tray

600 W

1280 W at maximum fan speed

JNP10K-RE0

PTX10008 standard Routing Control Board

50 W

100 W

JNP10K-RE1 or JNP10K-RE1-LT

PTX10008 enhanced Routing Control Board

150 W

175 W

PTX10K-LC1101

PTX10008 30-port QSFP28 line card

890 W

1750 W

PTX10K-LC1102

PTX10008 36-port QSFP+ line card

520 W

675 W

PTX10K-LC1104

PTX10008 coherent DWDM line card

900 W

1050 W

PTX10K-LC1105

PTX10008 30-port MACsec QSFP28 line card

950 W

1250 W

QFX10000-60S-60Q

QFX10000 60-port SFP+ and 6-port QSFP+ line card

365 W

465 W

CAUTION:

To ensure adequate power and to avoid raising a power alarm, we recommend that you maintain n +1 power supplies in your router at all times. Replace failed power supplies immediately to prevent unexpected failures.

If a new line card is installed in an operational router, power management does not power on the line card if the increased power demand exceeds the total available power, including redundant power. If redundant power is used to power on the line card, a minor alarm is raised, which becomes a major alarm in five minutes if the condition is not corrected.

You can view the total power provided to the chassis, the power required to operate the chassis and the components installed in it, and the balance power available in the chassis by using the show chassis power detail command.

Calculate Power Requirements for a PTX10008

Use the information in this topic to calculate power requirements of your PTX10008 configuration and the number of power supplies required for different PTX10008 router configurations.

CAUTION:

To ensure adequate power and to avoid raising a power alarm, we recommend that you maintain n +1 power supplies in JNP10008-SF configurations at all times. Replace failed power supplies immediately to prevent unexpected failures.

If a new line card is installed in an operational router, power management does not power on the line card if the increased power demand exceeds the total available power, including redundant power. If redundant power is used to power on the line card, a minor alarm is raised, which becomes a major alarm in five minutes if the condition is not corrected.

Note:

The calculations in this topic represent the maximum power requirements that you need to budget for your PTX10008 router configuration. The actual power consumption of your router will be less than the calculated results shown here and will vary based on the hardware and software configuration of your router, the amount of traffic passing through the line cards, and environmental variables such as room temperature.

Before you begin these calculations:

This topic describes these tasks:

Calculate the Power Consumption of Your PTX10008 Configuration

Use the following procedure to determine the maximum power you need to supply to the router. To calculate maximum system power consumption, you first determine the combined maximum internal power requirements of all the router components and then divide this result by the power supply output power.

To calculate maximum system power consumption:

  1. Determine the maximum power consumption of the base chassis components (that is, the components other than the line cards). Use Table 2 if your router is configured as either the standard base or redundant configuration.
    Table 2: Chassis Power Consumption for Standard Configurations

    Chassis Component

    Base Configuration

    Premium Configuration

    JNP10008-FAN

    950 W

    950 W

    JNP10008-FAN2 *

    JNP10K-RE0, or JNP10K-RE1

    175 W

    350 W

    JNP10008-SF

    1175 W (5 SIBs)

    1410 W (6 SIBs)

    Total

    2300 W

    2710 W

    * JNP10008-FAN2 is an optional upgrade that replaces JNP10008-FAN. Use 2,560 W for JNP10008-FAN2 configurations. JNP10008-FAN2 systems require JNP10K-PWR-AC2 or JNP10K-PWR-DC2 power supplies.

  2. Calculate the maximum internal power consumption of the entire router by adding in the power requirements of each line card. See Table 3 for a chart of the power needed for line cards.
    Table 3: Line Card Power Consumption

    Line Cards

    PTX10K-LC1101

    PTX10K-LC1102

    PTX10K-LC1104

    PTX10K-LC1105

    QFX10000-60S-6Q

    1

    1150 W

    675 W

    1050 W

    1250 W

    455 W

    2

    2300 W

    1350 W

    2100 W

    2500 W

    910 W

    3

    3450 W

    2025 W

    3150 W

    3750 W

    1365 W

    4

    4600 W

    2700 W

    4200 W

    5000 W

    1820 W

    5

    5750 W

    3375 W

    6250 W

    2275 W

    6

    6900 W

    4050 W

    7500 W

    2730 W

    7

    8050 W

    4725 W

    8750 W

    3185 W

    8

    9200 W

    5400 W

    10,000 W

    3640 W

    Note:

    * The PTX10K-LC1201-36CD power numbers do not include the power draw of optical transceivers. See the Hardware Compatibility Tool for further information.

    Note:

    The PTX10K-LC1104 line card is designed to comply with NEBS regulations on the PTX10008 Packet Transport Router when these routers are used in typical configurations. In a typical configuration, a PTX10008 router supports up to eight line cards, with up to four PTX10K-LC1104 line cards in any of the eight slots.

    For example, for a PTX10008 with five PTX10K-LC1102 line cards and three PTX10K-LC1101 line cards, the maximum power consumption is:

    = 5 (power consumed by PTX10K-LC1102 in watts) + 3 (power consumed by PTX10K-LC1101 line cards in watts)

    = 5 (675 W) + 3 (1150 W)

    = (3375 W + 3450 W)

    = 6825 W

  3. Add the power consumption from Step 1 and the total line card consumption from Step 2.

    To continue from the previous example, add the wattage from five PTX10K-LC1102 and three PTX10K-LC1101 cards to a premium configuration.

    (6825 W) + (2710 W)

    = 9535 W required

Calculate the Number of Power Supplies Required for Your PTX10008 Configuration

Use this procedure to calculate the number of power supplies required by your router configuration. The minimum power configuration for PTX10008 routers is three power supplies. However, using the calculated minimum power configuration does not prevent the system from raising a power alarm. If you are running the router in a JNP10008-SF switch fabric configuration, you must configure your router for n+1 power supplies to ensure you do not log power alarms.

To calculate the number of power supplies required for your minimum router configuration:

  1. Determine the power available from the power supplies. Table 4 shows the power available for installed power supplies.
    Note:

    DC systems are supported only in the redundant configuration.

    Table 4: Total Power Available

    Power Supply Module Models

    With Three Power Supplies

    With Four Power Supplies

    With Five Power Supplies

    JNP10K-PWR-AC

    8,100 W

    10,800 W

    13,500 W

    JNP10K-PWR-AC2 dual feed, high power (30-A) setting

    16,500 W

    22,000 W

    27,500 W

    JNP10K-PWR-AC2 single feed, high power (30-A) setting

    15,000 W

    20,000 W

    25,000 W

    JNP10K-PWR-AC2, dual feed, low power (20-A) setting

    9,000 W

    12,000 W

    15,000 W

    JNP10K-PWR-AC2, single feed, low power (20-A) setting

    8,100 W

    10,800 W

    13,500 W

    JNP10K-PWR-AC3, single active feed, (15-A) setting

    7,500 W

    10,000 W

    12,500 W

    JNP10K-PWR-AC3, two active feeds, (15-A) setting

    15,000 W

    20,000 W

    25,000 W

    JNP10K-PWR-AC3, three active feeds, (15-A) setting

    22,500 W

    30,000 W

    37,500 W

    JNP10K-PWR-AC3, four active feeds, (15-A) setting

    23,400 W

    31,200 W

    39,000 W

    JNP10K-PWR-AC3, single active feed, (20-A) setting

    9,000 W

    12,000 W

    15,000 W

    JNP10K-PWR-AC3, two active feeds, (20-A) setting; (either A0 and A1 or B0 and B1)

    18,000 W

    24,000 W

    30,000 W

    JNP10K-PWR-AC3, three or four active feeds, (20-A) setting

    23,400 W

    31,200 W

    39,000 W

    JNP10K-PWR-DC

    7,500 W

    10,000 W

    12,500 W

    JNP10K-PWR-DC2 dual feed, high power (80-A) setting

    16,500 W

    22,000 W

    27,500 W

    JNP10K-PWR-DC2 dual feed, low power (60-A) setting

    13,200 W

    17,600 W

    22,000 W

    JNP10K-PWR-DC2 single feed, high power (80-A) setting

    8,250 W

    11,000 W

    13,750 W

    JNP10K-PWR-DC2 single feed, low power (60-A) setting

    6,600 W

    8,800 W

    11,000 W

    Note:

    The JNP10K-PWR-AC2 power supply has a set of DIP switches on the faceplate that allows you to configure the power supply for either high power (30 A) or low power (20 A) input mode. If any JNP10K-PWR-AC2 power supply is set to 20 A, then the power budget for all power supplies installed in the system becomes 20 A, regardless of whether other power supplies are set at 30 A. This design helps prevent overloading of the power supply that is set to 20 A. See Table 5 for details about setting the DIP switches and available power.

    Table 5: Power Input and Output Voltages for JNP10K-PWR-AC2 Power Supplies

    INP0 (Switch 1)

    INP1 (Switch 2)

    H/L (High Input 30 A/Low Input 20A)

    Output Power

    On

    On

    On (30 A)

    5500 W

    On

    On

    Off (20 A)

    3000 W

    On

    Off

    On (30 A)

    5000 W

    Off

    On

    On (30 A)

    5000 W

    On

    Off

    Off (20 A)

    2700 W

    Off

    On

    Off (20 A)

    2700 W

    Note:

    The JNP10K-PWR-AC3 power supply has a set of five DIP switches on the faceplate that allows you to configure the power supply for either high power (20 A) or low power (15 A) input mode. If any JNP10K-PWR-AC3 power supply is set to 15 A, then the power budget for all power supplies installed in the system becomes 15 A, regardless of whether other power supplies are set at 20 A. This design helps prevent overloading of the power supply that is set to 15 A.

    Table 6: Power Input and Output Voltages for JNP10K-PWR-AC3 Power Supplies

    INP-A0 (Switch 0)

    INP-A1 (Switch 1)

    INP-B0 (Switch 2)

    INP-B1 (Switch 3)

    Switch 4 (High Input 20 A/Low Input 15 A)

    Output Power

    15-A

    Off

    Off

    Off

    On

    Off (15 A)

    2500 W

    Off

    Off

    On

    Off

    Off (15 A)

    2500 W

    Off

    Off

    On

    On

    Off (15 A)

    5000 W

    Off

    On

    Off

    Off

    Off (15 A)

    2500 W

    Off

    On

    Off

    On

    Off (15 A)

    5000 W

    Off

    On

    On

    On

    Off (15 A)

    7500 W

    Off

    On

    On

    Off

    Off (15 A)

    5000 W

    On

    Off

    Off

    Off

    Off (15 A)

    2500 W

    On

    Off

    Off

    On

    Off (15 A)

    5000 W

    On

    Off

    On

    Off

    Off (15 A)

    5000 W

    On

    Off

    On

    On

    Off (15 A)

    7500 W

    On

    On

    Off

    Off

    Off (15 A)

    5000 W

    On

    On

    Off

    On

    Off (15 A)

    7500 W

    On

    On

    On

    Off

    Off (15 A)

    7500 W

    On

    On

    On

    On

    Off (15 A)

    7800 W

    20-A

    Off

    Off

    Off

    On

    On (20 A)

    3000 W

    Off

    Off

    On

    Off

    On (20 A)

    3000 W

    Off

    Off

    On

    On

    On (20 A)

    6000 W

    Off

    On

    Off

    Off

    On (20 A)

    3000 W

    Off

    On

    Off

    On

    On (20 A)

    6000 W

    Off

    On

    On

    Off

    On (20 A)

    6000 W

    Off

    On

    On

    On

    On (20 A)

    7800 W

    On

    Off

    Off

    Off

    On (20 A)

    3000 W

    On

    Off

    Off

    On

    On (20 A)

    6000 W

    On

    Off

    On

    Off

    On (20 A)

    6000 W

    On

    Off

    On

    On

    On (20 A)

    7800 W

    On

    On

    Off

    Off

    On (20 A)

    6000 W

    On

    On

    Off

    On

    On (20 A)

    7800 W

    On

    On

    On

    Off

    On (20 A)

    7800 W

    On

    On

    On

    On

    On (20 A)

    7800 W

  2. Determine the total power required for your configuration with line cards installed. The total power available to the chassis is calculated by dividing the wattage needed by the power rating, and then rounding up.

    In the previous examples, we calculated that a premium PTX10008 AC system would require 9535 W with five PTX10K-LC1102 and three PTX10K-LC1101 line cards. In this example, we calculate the total power available for the 2700 W JNP10K-PWR-AC power supplies:

    = (9535 W) / (2700 W)

    = 3.5

    Round up the result to 4 AC power supplies to determine the minimum power level.

    CAUTION:

    The minimum power level does not prevent the system from raising a power alarm. Add an additional power supply for redundancy (n+1) to ensure you have covered the maximum power budget for your specific configuration.

    In our example, a basic configuration (3 power supplies, standard) would require two additional power supplies, one for the minimum power level and second as the redundant power supply. In a redundant AC system (6 power supplies, standard), the system would have sufficient power supplies for both minimum and n+1 redundancy.

  3. Calculate how much power the power supplies need. To determine the power required, multiply the number of power supplies by the power supply wattage and divide by the efficiency of the power supply. The efficiency rate accounts for the loss of energy within the power supply and is 89 percent for PTX10008 power supplies.

    For example, if you have an AC system with four power supplies:

    = 4 (2700 W) / (efficiency rating)

    = (10800 W) / (0.89)

    = 12135 W

JNP10K-PWR-AC Power Specifications

PTX10008 and PTX10016 redundant-configuration routers can use either AC or DC power supplies; base-configuration routers are AC only. You can run the JNP10K-PWR-AC power supply only in routers in which you have installed the JNP10008-SF or JNP10016-SF switch fabric.

Table 7 lists the power specifications for the AC power supply (JNP10K-PWR-AC) used in a PTX10008 or PTX10016 chassis.

Table 7: Power Specifications for a JNP10K-PWR-AC Power Supply

Item

Specification

AC input voltage

Operating range: 200–240 VAC

AC input line frequency

50–60 Hz

AC input current rating

16 A

AC output power

2700 W

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.

Table 8 shows the physical specifications for an AC power supply.

Table 8: Physical Specifications for a JNP10K-PWR-AC Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

14.4 in. (36.58 cm)

Weight

6.8 lb (3.08 kg)

JNP10K-PWR-AC2 Power Specifications

The JNP10K-PWR-AC2 power supply supports AC, HVAC, and HVDC. You can run JNP10K-PWR-AC2 power supplies in either a JNP10008-SF or a JNP10008-SF3 system. If you are upgrading a JNP10008-SF system to use JNP10K-PWR-AC2 power supplies, also upgrade your fans and fan tray controllers to ensure the proper airflow. JNP10K-PWR-AC2 power supplies require JNP10008-FAN2 and JNP10008-FTC2 cooling systems.

Table 9 lists the power specifications for the AC power supply (JNP10K-PWR-AC2) used in a PTX10008 or PTX10016 chassis.

Table 9: Power Specifications for a JNP10K-PWR-AC2 Power Supply

Item

Specifications

AC input voltage

180–305 VAC

DC input voltage

190–410  VDC

Input current rating

28.5 A

DC output power

5500 W with dual feed and 5000 W with single feed

Table 10 shows the physical specifications for a JNP10K-PWR-AC2 power supply.

Table 10: Physical Specifications for a JNP10K-PWR-AC2 Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

16.6 in. (42.16 cm)

Weight

11.4 lb (5.17 kg)

JNP10K-PWR-AC3 Power Specifications

The JNP10K-PWR-AC3 power supply supports AC.

#concept_a51_wft_hzb__table_b51_wft_hzb lists the power specifications for the AC power supply (JNP10K-PWR-AC3) used in a PTX10004 chassis.

Table 11: Power Specifications for a JNP10K-PWR-AC3 Power Supply

Specification

Value

AC input voltage

180–264 VAC

Input current rating

16 A

DC output power

12.3 V

#concept_a51_wft_hzb__table_c51_wft_hzb shows the physical specifications for a JNP10K-PWR-AC3 power supply.

Table 12: Physical Specifications for a JNP10K-PWR-AC3 Power Supply

Specification

Value

Height

3.386 in. (8.60 cm)

Width

3.584 in. (9.10 cm)

Depth

17.15 (43.57 cm)

Weight

12.8 lbs (5.8 kg)

PTX10008 Power Cables Specifications

Most sites distribute power through a main conduit that leads to frame-mounted power distribution panels, one of which can be located at the top of the rack that houses the router. An AC power cord connects each power supply to the power distribution panel.

Note:

In North America, AC power cords must not exceed 15 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52 and Canadian Electrical Code (CEC) Section 4-010(3). The cords shipped with the router to North America and Canada are in compliance.

PTX10008 AC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) power supplies have specific cord requirements. Use the following sections to determine the cable requirements based on the model of your power supply and any mode settings:

JNP10K-PWR-AC Power Cable Specifications

Each JNP10K-PWR-AC power supply has two independent 16 A rated AC inlets on the faceplate.

Each detachable AC power cord is 8 feet (approximately 2.5 meters) long. The coupler end of the appliancecord inserts into the AC appliance inlet on the faceplate of the AC power supply. The coupler type is C19 as described by the International Electrotechnical Commission (IEC) standard 60320. The plug end of the power cord fits into the power source outlet that is standard for your geographical location.

Table 13 lists the AC power cord specifications for JNP10K-PWR-AC for various countries and regions.

Table 13: AC Power Cord Specifications for JNP10K-PWR-AC Power Supplies

Country/Region

Electrical Specifications

Plug Standards

Juniper Model Number

Graphic

Argentina

250 VAC, 16 A, 50 Hz

IRAM Type RA/3/20

CBL-EX-PWR-C19-AR

Australia

250 VAC, 15 A, 50 Hz

AS/NZS 3112 Type SAA/3/15

CBL-EX-PWR-C19-AU

Brazil

250 VAC, 16 A, 50 Hz

NBR 14136: 2002 Type BR/3/20

CBL-EX-PWR-C19-BR

China

250 VAC, 16 A, 50 Hz

GB 1002 Type PRC/3/16

CBL-EX-PWR-C19-CH

Europe (except Italy, Switzerland, and United Kingdom)

250 VAC, 16 A, 50 Hz

CEE (7) VII Type VIIG

CBL-EX-PWR-C19-EU

India

250 AC, 16 A, 50 Hz

SABS 164/1:1992 Type ZA/3

CBL-EX-PWR-C19-SA

Israel

250 AC, 16 A, 50 Hz

SI 32/1971 Type IL/3

CBL-EX-PWR-C19-IL

Italy

250 VAC, 16 A, 50 Hz

CEI 23-16 Type I/3/16

CBL-EX-PWR-C19-IT

Japan

250 VAC, 16 A, 60 Hz

NEMA 6–20 Type N6/20

CBL-EX-PWR-C19-JP (default)

250 VAC, 16 A, 60 Hz

NEMA L6–20P Type NEMA Locking

CBL-EX-PWR-C19-JPL

Korea

250 VAC, 16 A, 50 Hz

CEE (7) VII Type VIIG

CBL-EX-PWR-C19-KR

North America

250 VAC, 16 A, 60 Hz

NEMA 6–20 Type N6/20

CBL-EX-PWR-C19-US (default)

250 VAC, 16 A, 60 Hz

NEMA L6–20P Type NEMA Locking

CBL-EX-PWR-C19-USL

South Africa

250 VAC, 16 A, 50 Hz

SABS 164/1:1992 Type ZA/3

CBL-EX-PWR-C19-SA

Switzerland

250 VAC, 16 A, 50 Hz

SEV 5934/2 Type 23G

CBL-EX-PWR-C19-SZ

United Kingdom

250 VAC, 13 A, 50 Hz

BS 1363/A Type BS89/13

CBL-EX-PWR-C19-UK

Worldwide (except Japan)

250 VAC, 16 A, 50 Hz

EN 60320-2-2/1

CBL-EX-PWR-C19-C20

JNP10K-PWR-AC2 Power Cable Specifications

The JNP10K-PWR-AC2 power supply operates in two modes:

  • JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input shows cables and connectors for 30-A input with 5500-W output. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C, while the other end of the cable is bare wire.

  • Table 14 shows cables appropriate for 20-A input with 3000-W output. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C. An example of the connector is shown in Figure 1.

Warning:

Do not run JNP10K-PWR-AC2 power supplies using 16-A or 20-A cables if connected to 30-A input.

CAUTION:

You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.

CAUTION:

It is important to connect both input feeds of the JNP10K-PWR-AC2 power supply to AC mains before loading the system with power.

Table 14: JNP10K-PWR-AC2 Power Cable Specifications for 20-A Input

Locale

Cord Set Rating

Plug Standards

Spare Juniper Model Number

Graphic

Argentina

16 A, 250 VAC

IRAM 2073 Type RA/3

CBL-JNP-SG4-AR

Australia and New Zealand

15 A, 250  VAC

AS/NZS 3112

CBL-JNP-SG4-AU

Brazil

16 A, 250 VAC

NBR 14136 Type BR/3

CBL-JNP-SG4-BR

China

16 A, 250 VAC

GB2099

CBL-JNP-SG4-CH

China, Europe, and Japan

16 A, 250 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20-CH

Europe (except Italy, Switzerland, and United Kingdom)

20 A, 250 VAC

CEE 7/7

CBL-JNP-SG4-EU

Great Britain

13 A, 250 VAC,

BS1363

CBL-JNP-SG4-UK

India

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Israel

16 A, RA, 250 VAC

SI 32/1971 Type IL/3C

CBL-JNP-SG4-IL

Italy

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-IT

North America

20 A, 250 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20

16 A, 250 VAC

Locking NEMA L6-20P

CBL-JNP-SG4-US-L

NEMA 6-20P

CBL-JNP-SG4-US

20 A, 277 V

NEMA I7-20P

CBL-JNP-SG4-HVAC

South Africa

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Switzerland

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-SZ

Figure 1: Bare Cable with Anderson Connector Bare Cable with Anderson Connector

JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input

The JNP10K-PWR-AC2 AC or HVDC power supply require a high current cable assembly when set for 30-A input. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C, while the other end of the cable is bare wire. See Figure 2 and Table 15. These cables are separately orderable and are not shipped automatically with JNP10K-PWR-AC2 orders. An example of the right-angle cable and connector is shown in Figure 4.

For connection to AC systems, Juniper provides a cable with either a NEMA 30-A connector (Figure 2) or an IEC 330P6W connector (Figure 3).

Figure 2: NEMA 30-A Connector NEMA 30-A Connector
Figure 3: IEC 330P6W ConnectorIEC 330P6W Connector
Table 15: 30-A Cabling Options

Locale

Cord Set Rating

Plug Standards

Connector

Spare Juniper Model Number

AC/HVDC power cord

Any

30-A, 400 VAC

UL 950 and IEC 60950

Anderson/straight to bare wire

CBL-PWR2-BARE

30-A, 400 VAC

UL 950 and IEC 60950

Anderson/right-angle to bare wire

CBL-PWR2-BARE-RA

AC power cord

Continental Europe

30-A 250 VAC

UL 950 and IEC332P6

Anderson/right-angle to IEC 332P6

CBL-PWR2-332P6W-RA

30-A 250 VAC

UL 950 and IEC332P6

Anderson/straight to IEC332P6

CBL-PWR2-332P6W

North America

30-A 250 VAC

IEC330P6

Anderson/right-angle to IEC 330P6

CBL-PWR2-330P6W-RA

30-A 250 VAC

IEC330P6

Anderson/straight to IEC 330P6

CBL-PWR2-330P6W

30-A 250 VAC

UL 498, CSA

Anderson/right-angle to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P-RA

30-A 250 VAC

UL 498, IEC5958P4

Anderson/straight to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P

Figure 4: Right-Angle, Bare Cable with Anderson ConnectorRight-Angle, Bare Cable with Anderson Connector
  1

Black wire – “+” or “-“ for HVDC and “Hot or neutral” for AC

  3

White wire – “+” or “-“ for HVDC and “Hot or neutral” for AC

  2

Green wire - Ground

 

JNP10K-PWR-AC3 Power Cable Specifications

The JNP10K-PWR-AC3 power supply operates in two modes:

  • 20-A input with 7800 W or 6000 W or 3000 W output

  • 15-A input with 7800 W or 7500 W, or 5000 W, or 2500 W output

Note:

When power cords with right angle plugs at the PSU end are selected, they must be in pairs of Right Angle Left Plugs for inputs A0 or B0 and Extended Right Angle Left Plugs for inputs A1 or B1.

See Table 16 for a list of appropriate cables.

Warning:

Do not run JNP10K-PWR-AC3 power supplies using 16-A or 20-A cables if connected to 15-A input.

CAUTION:

You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.

With right angle power cords and the baffle installed, the power cords will be exposed to hot exhaust air. The IEC C21 plugs have a temperature rating of 155C and the power cord cables have a rating of 90C.

Table 16: JNP10K-PWR-AC3 Power Cable Specifications for 20-A and 15-A Input

Locale

Cord Set Rating

Plug Standard

Spare Juniper Model Number

Graphic

Straight Plug at PSU Input

Australia and New Zealand

15 A, 250 VAC AS/NZS 3112

CBL-PWRC21-AU

Europe (except Italy, Switzerland, and United Kingdom)

16A, 250 VAC CEE 7/7

CBL-PWRC21-EU

Italy

16A, 250 VAC CEI 23-16

CBL-PWRC21-IT

North America

20A, 250 VAC

Locking NEMA L6-20P

CBL-PWRC21-US-L

NEMA 6-20P

CBL-PWRC21-US

International 16A, 250VAC

IEC-309 316P6W

CBL-PWRC21-316P6

 
North America 20A, 250 VAC

IEC-309 320P6W

CBL-PWRC21-320P6

 
Japan 20A, 250 VAC NEMA L6-20P

CBL-PWRC21-JP-L

China 16A, 250 VAC GB2099-1

CBL-PWRC21-CN

North America 20A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-NA

Europe 16A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-EU

Japan 20A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-JP

China 16A, 250 VAC IEC-320-C20

CBL-PWRC21-C20-CN

Switzerland 16A, 250 VAC SEV1011

CBL-PWRC21-SZ

 
South Africa 16A, 250 VAC

RA SANs 164/1

CBL-PWRC21-SA

India 16A, 250VAC RA IS 1293

CBL-PWRC21-IN

United Kingdom 16A, 250 VAC BS 1363

CBL-PWRC21-UK

Israel 16A, 250 VAC

SI 32/1971

Type IL/3G

CBL-PWRC21-IL

Brazil 16A, 250 VAC

NBR 14136

Type BR/3

CBL-PWRC21-BR

Argentina 16A, 250 VAC

IRAM 2073

Type RA/3

CBL-PWRC21-AR

Right Angle Left Plug at PSU Input
USA 20A, 250 VAC NEMA L6-20P CBL-PWRC21R-US-L
USA 20A, 250 VAC NEMA 6-20P CBL-PWRC21R-US
Europe 16A, 250 VAC CEE 7/7 CBL-PWRC21R-EU
Australia 15A, 250 VAC AS/NZ 3112 CBL-PWRC21R-AU
Italy 16A, 250 VAC CEI 23-50 CBL-PWRC21R-IT
International 16A, 250 VAC

IEC 60309

316P6W

CBL-PWRC21R-316P6  
North America 16A, 250VAC

IEC 60309

320P6W

CBL-PWRC21R-320P6  
Japan 20A, 250 VAC NEMA L6-20P CBL-PWRC21R-JP-L
China 16A, 250 VAC GB2099-1 CBL-PWRC21R-CN
North America 16A, 250 VAC

IEC-60320

C20

CBL-PWRC21R-C20-NA
Europe 16A, 250 VAC

IEC 60320

C20

CBL-PWRC21R-C20-EU
Japan 20A, 250 VAC

IEC 60320

C20

CBL-PWRC21R-C20-JP
China 16A, 250 VAC

IEC 60320

C20

CBL-PWRC21R-C20-CN
Switzerland 16A, 250 VAC SEV 1011 CBL-PWRC21R-SZ  
South Africa 16A, 250 VAC SANS 164/1 CBL-PWRC21R-SA
India 16A, 250 VAC IS 1293, RA CBL-PWRC21R-IN
United Kingdom 16A, 250 VAC BS1363 CBL-PWRC21R-UK
Israel 16A, 250 VAC

SI 32/1971

TYPE IL/3G

CBL-PWRC21R-IL
Brazil 16A, 250 VAC

NBR 14136

TYP BR/3

CBL-PWRC21R-BR
Argentina 16A, 250 VAC

IRAM 2073

TYPE RA/3

CBL-PWRC21R-AR
Extended Right Angle Left Plug at PSU Input
USA 20A, 250 VAC NEMA L6-20P CBL-PWRC21RL-US-L
USA 20 A, 250 VAC NEMA 6-20P CBL-PWRC21RL-US
Europe 16A, 250 VAC CEE 7/7 CBL-PWRC21RL-EU
Australia 15A, 250 VAC AS/NZ 3112 CBL-PWRC21RL-AU
Italy 16A, 250 VAC CEI 23-50 CBL-PWRC21RL-IT
International 16A, 250 VAC

IEC-60309

316P6W

CBL-PWRC21RL-316P6  
North America 20A, 250 VAC

IEC-60309

320P6W

CBL-PWRC21RL-320P6  
Japan 20A, 250 VAC NEMA L6-20P CBL-PWRC21RL-JP-L
China 16A, 250 VAC GB2099-1 CBL-PWRC21RL-CN
North America 20A, 250 VAC

IEC-60320

C20

CBL-PWRC21RL-C20NA
Europe 16A, 250 VAC

IEC-60320

C20

CBL-PWRC21RL-C20EU
Japan 20A, 250 VAC

ICE-60320

C20

CBL-PWRC21RL-C20JP
China 16A, 250 VAC

IEC-60320

C20

CBL-PWRC21RL-C20CN
Switzerland 16A, 250 VAC SEV 1011 CBL-PWRC21RL-SZ  
South Africa 16A, 250 VAC SANS 164/1 CBL-PWRC21RL-SA
India 16A, 250 VAC IS1293, RA CBL-PWRC21RL-IN
United Kingdom 16A, 250 VAC BS 1363 CBL-PWRC21RL-UK
Israel 16A, 250 VAC

SI 32/1971

Type IL/3G

CBL-PWRC21RL-IL
Brazil 16A, 250 VAC

NBR 14136

Type BR/3

CBL-PWRC21RL-BR
Argentina 16A, 250 VAC

IRAM 2073

Type RA/3

CBL-PWRC21RL-AR

JNP10K-PWR-DC Power Specifications

The DC power supply (JNP10K-PWR-DC) is supported only in routers in which you have installed the JNP10008-SF or JNP10016-SF switch fabric. Table 17 lists the power specifications for the JNP10K-PWR-DC power supply used in PTX10008 and PTX10016 routers.

Table 17: Power Specifications for the JNP10K-PWR-DC Power Supply

Item

Specifications

DC input voltage

  • Minimum operating voltage: –40 VDC

  • Nominal operating voltage: –48 VDC

  • Operating voltage range: –40 VDC through –72 VDC

DC input current rating

60 A maximum at nominal operating voltage (–48 VDC) for each input terminal

Output power

2500 W

Table 18 shows the physical specifications of the JNP10K-PWR-DC power supply.

Table 18: Physical Specifications of the JNP10K-PWR-DC Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

14.4 in. (36.58 cm)

Weight

6 lb (2.72 kg)

JNP10K-PWR-DC2 Power Specifications

If you are upgrading a JNP10008-SF system to use JNP10K-PWR-DC2 power supplies, also upgrade your fans and fan tray controllers to ensure the proper airflow. JNP10K-PWR-DC2 power supplies require JNP10008-FAN2 and JNP10008-FTC2 cooling systems.Table 19 lists the power specifications for the dual DC power supply used in a PTX10008 chassis.

Table 19: Power Specifications for the JNP10K-PWR-DC2 Power Supply

Item

Specifications

DC input voltage

  • Minimum operating voltage: –40 VDC

  • Nominal operating voltage: –48 VDC

  • Operating voltage range: –40 VDC through –72 VDC

DC input current rating

  • 76-A maximum at minimum operating voltage (-40 VDC) with 80-A DIP switch setting and 5500-W output load

  • 64-A maximum at nominal operating voltage (–48 VDC) with 80-A DIP switch setting and 5500-W output load

  • 60-A maximum at minimum operating voltage (-40 VDC) with 60-A DIP switch setting and 4400-W output load

  • 50-A maximum at nominal operating voltage (-48 VDC) with 60-A DIP switch setting and 4400-W output load

Output power

2200 W for low input (60-A) single feed

4400 W for low input (60-A) dual feed

2750 W for high input (80-A) single feed

5500 W for high input (80-A) dual feed

Table 20 shows the physical specifications for a JNP10K-PWR-DC2 power supply.

Table 20: Physical Specifications of a JNP10K-PWR-DC2 Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (1.63 cm)

Depth

16.05 in. (40.77 cm)

Weight

8.6 lb (3.9 kg)