Monitoring Nodes in the Fabric

As an administrator or operator, you can use Junos Space to track the status of physical and logical components of deployed nodes in a fabric.

Junos Space Network Management Platform supports SNMP Monitoring by an SNMP Manager for SNMP v1, v2c, and v3.

The SNMP manager polls Junos Space to obtain information about the logical components of the nodes using an object identifier (OID) in SNMP v1 and v2, or v3 as a user. The response is provided by the Junos Space SNMP agent and the polled data is displayed in the Network Monitoring workspace.

This topic contains the following sections:

Viewing and Modifying the SNMP Configuration for a Fabric Node

To view and edit the Junos Space SNMP configuration for self-monitoring:

  1. Select Administration > Fabric.

    The Fabric page appears.

  2. Select the node whose configuration you want to view or modify, and from the Actions menu, select SNMP Configuration.

    The SNMP Configuration window appears with the title bar displaying the IP address of the selected node.

  3. Set the SNMP configuration parameters as required, using Table 1 to guide you.
    Note:

    By default, the system load parameters are set to 4, which means that an alert is indicated only when all CPUs are under 100 percent load.

    Table 1: SNMP Configuration

    Setting

    Explanation

    Recommended Settings

    Default Value

    Enable SNMP over TCP

    Enables SNMP communication over TCP

    Note:

    By default, SNMP communication occurs over UDP.

    Cleared

    Cleared

    Monitor Web Service

    Includes monitoring the performance of the Junos Space GUI

    Note:

    This parameter is enabled only for the Junos Space VIP node.

    Selected

    Selected

    Monitor All Disks

    Includes all disks on the current Junos Space server

    Cleared

    Cleared

    Monitor RAID

    Enables Net-SNMP to monitor the RAID state

    When a RAID controller fault is detected, a trap is sent.

    Note:

    From Junos Space Platform Release 16.1 onward, if you want to use the Monitor RAID option, you need to install StorMan-7.31-18856.x86_64.rpm . For installation instructions, see Installing StorMan RPM for Monitor RAID Functionality.

    Note:

    This field is not applicable to and is disabled for Junos Space Virtual Appliances.

    Selected

    Cleared

    Disk Usage %

    When the percentage of the disk in use exceeds the configured disk usage percentage, an alarm is triggered.

    5

    5

    System Load (1 min)

    When the average system load (over 1 minute) exceeds the configured value, an alarm is triggered.

    4

    4

    System Load (5 min)

    When the average system load (over 5 minutes) exceeds the configured value, an alarm is triggered.

    4

    4

    System Load (15 min)

    When the average system load (over 15 minutes) exceeds the configured value, an alarm is triggered.

    4

    4

    System Location

    Location of the fabric node

    Actual geographical or other location

    unknown

    System Contact

    E-mail address to which the system sends notifications

    E-mail address of actual person

    root <root@localhost>

    Disk Mount Path

    Disk mount path that is to be monitored

    Note:

    This field is disabled if the Monitor All Disks field is selected.

    Actual path, if available

    /

    CPU Max Temp (mC)

    When the temperature exceeds the configured value, an alarm is triggered.

    50000

    50000

    CPU Min Fan (RPM)

    When the CPU fan speed goes below the configured value, an alarm is triggered.

    1000

    1000

    CPU Min Voltage (mV)

    When the CPU voltage goes below the configured value, an alarm is triggered.

    1000

    1000

  4. Select Confirm to apply the SNMP configuration changes to the node, or select Cancel if you do not want to make any changes to the SNMP configuration.

Table 2 shows the configuration parameters for monitoring disk usage.

Table 2: SNMP Configuration Parameters: Monitoring Disk Usage

Monitoring Disk Usage

Parameter: Disk Usage (%)

Default: 5%

When the free disk space is greater than the configured threshold, the trap shown in Figure 1 is generated.

Figure 1: Disk Usage Threshold Is NormalDisk Usage Threshold Is Normal

Figure 2 shows the OID details for the trap generated when disk usage is normal.

Figure 2: Trap Details When Disk Usage NormalTrap Details When Disk Usage Normal

When the free disk space is less than the configured threshold, the trap shown in Figure 3 is generated.

Figure 3: Disk Usage Threshold Exceeds Configured ThresholdDisk Usage Threshold Exceeds Configured Threshold

Figure 4 shows the OID details for the trap generated when disk usage exceeds the configured threshold.

Figure 4: Trap Details When DIsk Usage Exceeds Configured ThresholdTrap Details When DIsk Usage Exceeds Configured Threshold

Table 3 shows the configuration parameters for monitoring the CPU load average.

Table 3: SNMP Configuration Parameters: Monitoring the CPU Load Average

Monitoring the CPU Load Average (System Load)

Parameter: CPU Load (1 min, 5 min, 15 min)

Default Threshold Value: 4

When the CPU Load Average threshold is less than or equal to the configured threshold limit, the trap shown in Figure 5 is generated:

Figure 5: CPU Load Average Threshold Is NormalCPU Load Average Threshold Is Normal

Figure 6 shows the OID details for the trap generated when the CPU load is normal.

Figure 6: Trap Details When CPU Load Average Threshold Is NormalTrap Details When CPU Load Average Threshold Is Normal

Figure 7 shows the traps generated when the 15 minute, 5 minute, or 1 minute CPU Load Average threshold is exceeded.

Figure 7: CPU Load Average Threshold – Upper Limit ExceededCPU Load Average Threshold – Upper Limit Exceeded

Figure 8 shows the OID details for the trap generated when the CPU load 5 minute average exceeds the threshold.

Figure 8: Trap Details When CPU Load 5 Minute Average Exceeds ThresholdTrap Details When CPU Load 5 Minute Average Exceeds Threshold

Table 4 shows monitoring processes for the Junos Space Network Management Platform.

Table 4: SNMP Configuration Parameters: Monitoring Processes

Monitoring Processes

Parameter: Node Management Agent (NMA)

When the NMA process is up, the trap shown in Figure 9 is generated:

Figure 9: NMA Is UpNMA Is Up

Figure 10 shows the OID details for the trap generated when the NMA process is up.

Figure 10: Trap Details When NMA Is UpTrap Details When NMA Is Up

When the NMA process is down, the trap shown in Figure 11 is generated:

Figure 11: NMA is DownNMA is Down

Figure 12 shows the OID details for the trap generated when the NMA process is down.

Figure 12: Trap Details When NMA is DownTrap Details When NMA is Down

Parameter: Webproxy

When the WebProxy process is up, the trap shown in Figure 13 is generated:

Figure 13: WebProxy Is UpWebProxy Is Up

Figure 14 shows the OID details for the trap generated when the WebProxy process is up.

Figure 14: Trap Details When WebProxy Is UpTrap Details When WebProxy Is Up

When the WebProxy process is down, the trap shown in Figure 15 is generated:

Figure 15: WebProxy Is DownWebProxy Is Down

Figure 16 shows the OID details for the trap generated when the WebProxy is down.

Figure 16: Trap Details When WebProxy Is DownTrap Details When WebProxy Is Down

Parameter: JBoss

When the JBoss process is up, the trap shown in Figure 17 is generated:

Figure 17: JBoss Is UpJBoss Is Up

Figure 18 shows the OID details for the trap generated when the JBoss process is up.

Figure 18: Trap Details When JBoss Is UpTrap Details When JBoss Is Up

When the JBoss process is down, the trap shown in Figure 19 is generated:

Figure 19: JBoss Is DownJBoss Is Down

Figure 20 shows the OID details for the trap generated when JBoss is down.

Figure 20: Trap Details When JBoss Is DownTrap Details When JBoss Is Down

Parameter: Mysql

When the Mysql process is up, the trap shown in Figure 21 is generated:

Figure 21: Mysql Is UpMysql Is Up

Figure 22 shows the OID details for the trap generated when the Mysql process is up.

Figure 22: Trap Details When Mysql Is UpTrap Details When Mysql Is Up

When the Mysql process is down, the trap shown in Figure 23 is generated:

Figure 23: Mysql Is DownMysql Is Down

Figure 24 shows the OID details for the trap generated when the Mysql process is down.

Figure 24: Trap Details When Mysql Is DownTrap Details When Mysql Is Down

Parameter: Postgresql

When the Postgresql process is up, the trap shown in Figure 25 is generated:

Figure 25: Postgresql Is UpPostgresql Is Up

Figure 26 shows the OID details for the trap generated when the Postgresql process is up.

Figure 26: Trap Details When Postgresql Is UpTrap Details When Postgresql Is Up

When the Postgresql process is down, the trap shown in Figure 27 is generated:

Figure 27: Postgresql Is DownPostgresql Is Down

Figure 28 shows the OID details for the trap generated when the Postgresql process is up.

Figure 28: Trap Details When Postgresql Is DownTrap Details When Postgresql Is Down

Parameter: Free swap memory

When the free swap memory is greater than the upper threshold limit, the trap shown in Figure 29 is generated:

Figure 29: Swap Memory Usage Is NormalSwap Memory Usage Is Normal

Figure 30 shows the OID details for the trap generated when swap memory usage is normal.

Figure 30: Trap Details When Swap Memory Is NormalTrap Details When Swap Memory Is Normal

When the free swap memory is less than the upper threshold limit, the trap shown in Figure 31 is generated:

Figure 31: Swap Memory Usage Threshold Exceeds Upper LimitSwap Memory Usage Threshold Exceeds Upper Limit

Figure 32 shows the OID details for the trap generated when swap memory usage is exceeds upper limit.

Figure 32: Trap Details When Swap Memory Usage Exceeds Upper LimitTrap Details When Swap Memory Usage Exceeds Upper Limit

Table 5 shows the configuration parameters for monitoring Junos Space Network Management Platform hardware.

Table 5: SNMP Configuration Parameters: Monitoring Linux Hardware

Monitoring Linux Hardware

Note:

LM-SENSORS-MIB is not supported by the Junos Space Virtual Appliance, but only by the Junos Space Appliance. Therefore the threshold settings of CPU Max Temp (mC), CPU Min Fan (RPM) and CPU Min Voltage (mV) will not trigger any traps in the virtual appliance.

Parameter: CPU min FAN (rpm)

Default Threshold Value: 1500

When the CPU fan speed is greater than the configured threshold (minimum fan speed), the trap shown in Figure 33 is generated:

Figure 33: CPU Fan Speed NormalCPU Fan Speed Normal

Figure 34 shows the OID details for the trap generated when CPU fan speed is normal.

Figure 34: Trap Details When CPU Fan Speed Is NormalTrap Details When CPU Fan Speed Is Normal

When the CPU fan speed is less than the configured threshold (minimum fan speed), the trap shown in Figure 35 is generated:

Figure 35: CPU Fan Speed Is Below the Configured ThresholdCPU Fan Speed Is Below the Configured Threshold

Figure 36 shows the OID details for the trap generated when CPU fan speed lower than the configured threshold.

Figure 36: Trap Details When CPU Fan Speed Is Below the Configured ThresholdTrap Details When CPU Fan Speed Is Below the Configured Threshold

Parameter: CPU min Voltage (mV)

When the CPU voltage is greater than the configured value, the trap shown in Figure 37 is generated:

Figure 37: CPU Voltage NormalCPU Voltage Normal

Figure 38 shows the OID details for the trap generated when CPU voltage is normal.

Figure 38: Trap Details When CPU Voltage Is NormalTrap Details When CPU Voltage Is Normal

Default Threshold Value: 1000

When the CPU voltage is lower than the configured value, the trap shown in Figure 39 is generated:

Figure 39: CPU Voltage Is Lower Than Configured ThresholdCPU Voltage Is Lower Than Configured Threshold

Figure 40 shows the OID details for the trap generated when CPU voltage is lower than the configured threshold.

Figure 40: Trap Details When CPU Voltage Is Lower Than Configured ThresholdTrap Details When CPU Voltage Is Lower Than Configured Threshold

Parameter: CPU Temperature

When the CPU temperature is lower than the configured threshold, the trap shown in Figure 41 is generated:

Figure 41: CPU Temperature NormalCPU Temperature Normal

Figure 42 shows the OID details for the trap generated when CPU temperature is normal.

Figure 42: Trap Details When CPU Temperature Is NormalTrap Details When CPU Temperature Is Normal

When the CPU temperature exceeds the configured threshold, the trap shown in Figure 43 is generated:

Figure 43: CPU Temperature Exceeds The Configured ThresholdCPU Temperature Exceeds The Configured Threshold

Figure 44 shows the OID details for the trap generated when CPU temperature is higher than the configured threshold.

Figure 44: Trap Details When CPU Temperature Exceeds The Configured ThresholdTrap Details When CPU Temperature Exceeds The Configured Threshold

Table 6 shows the configuration parameters for monitoring fabric health.

Table 6: SNMP Configuration Parameters: Monitoring Fabric Health
Monitoring Fabric Health

Parameter: Junos Space Node

When a Junos Space node is up, the trap shown in Figure 45 is generated:

Figure 45: Junos Space Node is UpJunos Space Node is Up

Figure 46 shows the OID details for the trap generated when a Junos Space node is up.

Figure 46: Trap Details When Junos Space Node Is UpTrap Details When Junos Space Node Is Up

When a Junos Space node is down, the trap shown in Figure 47 is generated:

Figure 47: Junos Space Node is DownJunos Space Node is Down

Figure 48 shows the OID details for the trap generated when a Junos Space node is down.

Figure 48: Trap Details When Junos Space Node is DownTrap Details When Junos Space Node is Down

Parameter: Junos Space Node Removal

When a Junos Space node is removed from the fabric, the trap shown in Figure 49 is generated:

Figure 49: Junos Space Node Is RemovedJunos Space Node Is Removed

Figure 50 shows the OID details for the trap generated when a Junos Space node is removed..

Figure 50: Trap Details When Junos Space Node Is RemovedTrap Details When Junos Space Node Is Removed

Parameter: JBoss Multi-Primary Detected

When there is more than one JBoss AppLogic primary node detected in the cluster, the trap shown in Figure 51 is generated:

Figure 51: JBoss Multi-Primary DetectedJBoss Multi-Primary Detected

Figure 52 shows the OID details for the trap generated when there is more than one JBoss AppLogic primary node detected in the cluster.

Figure 52: Trap Details When JBoss Multi-Primary Is DetectedTrap Details When JBoss Multi-Primary Is Detected

Parameter: VIP Bind Issue Detected in JBoss Node(s)

When VIP Bind issue is detected in JBoss node(s), the trap shown in Figure 53 is generated:

Figure 53: VIP Bind Issue Detected In JBoss Node(s)VIP Bind Issue Detected In JBoss Node(s)

Figure 54 shows the OID details for the trap generated when VIP Bind issue is detected in JBoss node(s).

Figure 54: Trap Details When VIP Bind Issue Is Detected In JBoss Node(s)Trap Details When VIP Bind Issue Is Detected In JBoss Node(s)

Parameter: Fabric Monitoring Process Inactive

When fabric monitoring process is inactive, the trap shown in Figure 55 is generated:

Figure 55: Fabric Monitoring Process InactiveFabric Monitoring Process Inactive

Figure 56 shows the OID details for the trap generated when fabric monitoring process is inactive.

Figure 56: Trap Details When Fabric Monitoring Process Is InactiveTrap Details When Fabric Monitoring Process Is Inactive

Parameter: Tables Exceed Size Limit

When one or more tables in the MySQL database exceed the size limit of 10 GB, the trap shown in Figure 57 is generated:

Figure 57: Tables Exceed Size LimitTables Exceed Size Limit

Figure 58 shows the OID details for the trap generated when one or more tables in the MySQL database exceed the size limit of 10 GB.

Figure 58: Trap Details When Tables Exceed Size LimitTrap Details When Tables Exceed Size Limit

Parameter: Device Session Count Exceeds Threshold Limit

When the device session count exceeds the threshold limit, the trap shown in Figure 59 is generated:

Figure 59: Device Session Count Exceeds Threshold LimitDevice Session Count Exceeds Threshold Limit

Figure 60 shows the OID details for the trap generated when the device session count exceeds the threshold limit.

Figure 60: Trap Details When Device Session Count Exceeds Threshold LimitTrap Details When Device Session Count Exceeds Threshold Limit

Parameter: HPROF Availability

When Heap and CPU Profiling Agent (HPROF) files are detected on a Junos Space node, the trap shown in Figure 61 is generated:

Figure 61: HPROF AvailabilityHPROF Availability

Figure 62 shows the OID details for the trap generated when HPROF files are detected on a Junos Space node.

Figure 62: Trap Details When HPROF Files Are AvailableTrap Details When HPROF Files Are Available

Parameter: JGroup Membership Issue Detected

When the removal of a JBoss node from JGroup is detected in the cluster, the trap shown in Figure 63 is generated:

Figure 63: JGroup Membership Issue DetectedJGroup Membership Issue Detected

Figure 64 shows the OID details for the trap generated when the removal of a JBoss node from JGroup is detected in the cluster.

Figure 64: Trap Details When JGroup Membership Issue DetectedTrap Details When JGroup Membership Issue Detected

Parameter: MySQL In Out Of Sync State

When a MySQL database synchronization issue is detected between nodes running the MySQL database, the trap shown in Figure 65 is generated:

Figure 65: MySQL In Out Of Sync StateMySQL In Out Of Sync State

Figure 66 shows the OID details for the trap generated when a MySQL database synchronization issue is detected between nodes running the MySQL database.

Figure 66: Trap Details When MySQL Is In Out Of Sync StateTrap Details When MySQL Is In Out Of Sync State

Parameter: File Intrusion Detection Monitoring

When changes in files or file permissions are detected, the trap shown in Figure 67 is generated.

Figure 67: File Intrusion Detection MonitoringFile Intrusion Detection Monitoring

Figure 68 shows the OID details for the trap generated when file or file permission changes are detected in the system.

Figure 68: Trap Details for File Intrusion Detection MonitoringTrap Details for File Intrusion Detection Monitoring

Parameter: Audit Logs Forwarding Failed

When the system fails to forward audit logs to the configured system log server, the trap shown in Figure 69 is generated:

Figure 69: Audit Logs Forwarding FailedAudit Logs Forwarding Failed

Figure 70 shows the OID details for the trap generated when the system fails to forward audit logs to the configured system log server.

Figure 70: Trap Details When Audit Logs Forwarding FailsTrap Details When Audit Logs Forwarding Fails

Parameter: One Or More Expected Process Are Inactive

Junos Space monitors critical process like JBoss. If any of these expected processes are inactive, the trap shown in Figure 71 is generated:

Figure 71: One or More Expected Processes Are InactiveOne or More Expected Processes Are Inactive

Figure 72 shows the OID details for the trap generated when one or more expected processes are inactive.

Figure 72: Trap Details When One or More Expected Processes Are InactiveTrap Details When One or More Expected Processes Are Inactive
Note:

LM-SENSORS-MIB is not supported by the Junos Space virtual appliance, but only by the Junos Space Appliance. Therefore the threshold settings of CPU Max Temp (mC), CPU Min Fan (RPM) and CPU Min Voltage (mV) will not trigger any traps in the virtual appliance.

Note:

Junos Space supports RAID-related traps on a Junos Space appliance. The following is a sample trap:

Starting SNMP Monitoring on Fabric Nodes

To start SNMP monitoring on one or more fabric nodes:

  1. Select Network Management Platform > Administration > Fabric.

    The Fabric page appears.

  2. Select the check box for each fabric node on which you want to start SNMP monitoring.
  3. From the Actions menu, select SNMP Start.

    The Confirm Start SNMP Agent dialog box is displayed.

  4. Click Yes.

    Junos Space begins SNMP monitoring on the selected fabric nodes.

    Note:

    This process might take a while.

  5. To view the status of SNMP monitoring on the selected fabric nodes, select Network Monitoring > Node List.

    The Network Monitoring > Node List page appears.

  6. Select the node on which you started the SNMP monitoring.

    The Junos Space node is represented as space-<number>.

    Figure 73 shows a sample view of network monitoring details for the selected fabric node.

    Figure 73: Network Monitoring Details for the Selected Fabric NodeNetwork Monitoring Details for the Selected Fabric Node

    Under Notification / Recent Events on the right of the Node List page, you see the results of the SNMP monitoring operation.

Stopping SNMP Monitoring on Fabric Nodes

To stop SNMP monitoring on one or more fabric nodes:

  1. Select Network Management Platform > Administration > Fabric.

    The Fabric page appears.

  2. Select the check box for each fabric node on which you want to stop SNMP monitoring.
  3. From the Actions menu, select SNMP Stop.

    The Confirm Stop SNMP Agent dialog box is displayed.

  4. Click Yes.

    Junos Space stops SNMP monitoring on the selected fabric nodes.

Restarting SNMP Monitoring on Fabric Nodes

To restart SNMP monitoring on one or more fabric nodes:

  1. Select Network Management Platform > Administration > Fabric.

    The Fabric page appears.

  2. Select the check box for each fabric node on which you want to restart SNMP monitoring.
  3. From the Actions menu, select SNMP Restart.

    The Confirm Restart SNMP Agent dialog box is displayed.

  4. Click Yes.

    Junos Space restarts SNMP monitoring on the selected fabric nodes.

Adding a Third-Party SNMP V1 or V2c Manager on a Fabric Node

To add a third-party SNMP V1 or V2c manager on a fabric node:

  1. Select Network Management Platform > Administration > Fabric > SNMP Manager.

    The SNMP Manager page appears.

  2. Click the Add SNMP Manager icon.

    The Add 3rd Party SNMP Manager dialog box is displayed.

  3. In the Manager IP field, enter the SNMP manager IP address.
    Note:
    • Depending on whether the Junos Space fabric is configured with only IPv4 addresses or both IPv4 and IPv6 addresses, Junos Space Platform allows you to enter an IPv4 address or either an IPv4 or IPv6 address respectively for the SNMP Manager.

    • The IPv4 and IPv6 addresses that you use must be valid addresses. Refer to http://www.iana.org/assignments/ipv4-address-space for the list of restricted IPv4 addresses and http://www.iana.org/assignments/ipv6-address-space for the list of restricted IPv6 addresses.

  4. In the Version field, select the SNMP version (V1 or V2c) .
  5. In the Community field, enter the community string.

    Any alphanumeric string (up to 254 characters) is acceptable, including spaces and symbols.

  6. Click OK.

    The newly added SNMP v1 or v2c Manager is displayed on the SNMP Manager page.

Adding a Third-Party SNMP V3 Manager on a Fabric Node

To add a third-party SNMP V3 manager on a fabric node:

  1. Select Platform > Administration > Fabric > SNMP Manager.

    The SNMP Manager page appears.

  2. Click the Add icon.

    The Add 3rd Party SNMP Manager dialog box displays.

  3. In the Manager IP field, enter the SNMP manager IP address.
    Note:
    • Depending on whether the Junos Space fabric is configured with only IPv4 addresses or both IPv4 and IPv6 addresses, Junos Space Platform allows you to enter an IPv4 address or either an IPv4 or IPv6 address respectively for the SNMP Manager.

    • The IPv4 and IPv6 addresses that you use must be valid addresses. Refer to http://www.iana.org/assignments/ipv4-address-space for the list of restricted IPv4 addresses and http://www.iana.org/assignments/ipv6-address-space for the list of restricted IPv6 addresses.

  4. In the Version field, select V3.
  5. In the User Name field, type the user name.

    The user name can contain a maximum of 32 alphanumeric characters including spaces and symbols.

  6. In the Authentication Type field, enter the authentication type (MD5 or SHA).
  7. In the Authentication Password field, enter the authentication password.

    Click the red information icon next to the Authentication Password field for information on the password rules.

  8. In the Confirm Authentication password, enter the authentication password again to confirm the password.
  9. From the Security Level list, select the security level:
    • noAuthNoPriv—Do not specify an authentication or privacy password.

    • authNoPriv—Specify only an authentication password.

    • authPriv—Specify both authentication and privacy passwords.

  10. In the Privacy Type field, enter the privacy type (AES or DES).
  11. In the Privacy Password field, enter the privacy password.

    Click the red information icon next to the Authentication Password field for information on the password rules.

  12. In the Confirm Privacy password field, enter the privacy password again to confirm the password.
  13. Click OK.

    The newly added SNMP Manager entry is displayed on the SNMP Manager page.

Note:

The trap settings for the SNMPv3 manager are not automatically updated in Network Monitoring. Therefore, to ensure that the Network Monitoring receives the traps from Junos Space, you must add the same settings manually in the /opt/opennms/etc/trapd-configuration.xml file. Table 7 displays the mapping between the parameters in the /opt/opennms/etc/trapd-configuration.xml file and the fields in the Add 3rd Party SNMP Manager page.

The following is a sample configuration in the /opt/opennms/etc/trapd-configuration.xml file.

Table 7: Mapping of SNMP V3 Settings

Parameter in trapd-configuration.xml File

Field in Add 3rd Party SNMP Manager Page

security-name

User Name

auth-passphrase

Authentication Password

privacy-passphrase

Privacy Password

privacy-protocol

Privacy Type

Deleting a Third-Party SNMP Manager from a Fabric Node

To delete a third-party SNMP manager configuration from a fabric node:

  1. Select Platform > Administration > Fabric > SNMP Manager.

    The SNMP Manager page appears.

  2. Select the SNMP manager configuration that you want to remove.
  3. Click the Delete SNMP Manager icon.
  4. To confirm the deletion of the SNMP manager, click Yes.

    The deleted SNMP manager is removed from the SNMP Manager page.

Installing StorMan RPM for Monitor RAID Functionality

To install StorMan RPM:

From Junos Space Platform CLI, run the following command: