ON THIS PAGE
MX2008 High-Voltage Universal (HVAC/HVDC) Power Distribution Module Description
MX2008 High-Voltage Universal (HVAC/HVDC) Power Distribution Module LEDs
MX2008 High-Voltage Universal (HVAC/HVDC) Power Supply Module Description
MX2008 High-Voltage Second-Generation Universal Power Requirements
MX2000 High-Voltage Universal PDM (MX2K-PDM-HV) Power Cord Specifications
MX2000 Router High-Voltage Universal (HVAC/HVDC) Power Subsystem Electrical Specifications
High-Voltage Universal (HVAC/HVDC) Power Circuit Breaker Requirements for the MX2000 Router
MX2008 High-Voltage Universal (HVAC/HVDC) Power System
MX2008 High-Voltage Universal (HVAC/HVDC) Power Distribution Module Description
The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.
In the high-voltage second-generation universal (HVAC/HVDC) power configuration, the MX2000 router contains two high-voltage universal (MX2K-PDM-HV) PDMs located at the rear of the chassis in slots PDM0/Input0 and PDM1/Input1 (bottom to top). A minimum of one PDM is required per system (two PDMs per chassis) for nonredundant power. The universal (HVAC/HVDC) PDMs provide power interface to nine power supply modules (PSMs).
Two PDMs provide full redundancy for the router. In a redundant configuration, a total of a total of eighteen (9-feed PDMs) are supported.
The power backplane for a subsystem distributes regulated 52 VDC to all boards supplied by that subsystem.
Each high-voltage universal (HVAC/HVDC) PDM has nine (HVAC/HVDC) inputs, (see Figure 1).
See Also
MX2008 High-Voltage Universal (HVAC/HVDC) Power Distribution Module LEDs
Each universal PDM faceplate contains one LED for each of the nine input power feeds, indicating the correct or incorrect polarity connection of each feed. See Table 1 and Figure 2 high-voltage universal (HVAC/HVDC) PDM LEDs.
1 — LED |
Color |
State |
Description |
---|---|---|
Green |
On |
Positive and negative input feeds are connected. PDM is functioning normally. |
– |
Off |
Positive input feed is not connected or present. |
Negative input feed is not connected or present. |
See Also
MX2008 High-Voltage Universal (HVAC/HVDC) Power Supply Module Description
The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs.
The MX2008 supports a universal HVAC/HVDC power system. The HVAC/HVDC power system operates with nine feeds. A total of nine feeds are required to fully power the MX2010. Another nine feeds are required to provide feed redundancy (a total of 18 feeds In the HVAC/HVDC power configuration, the router contains up to nine HVAC/HVDC PSMs located at the rear of the chassis in slots PSM0 through PSM8, (left to right). The HVAC/HVDC PSMs in slots PSM0 through PSM8 provide power to the all router components including MPCs in slot 0 through 9, CB-REs in slot 0 and 1, SFBs in slot 0 through 7, and fan trays 0, 1, 2, and 3.
The MX2008 systems configured for universal (HVAC/HVDC) input power must use only universal PDMs and PSMs. AC, DC, 240 V China, and universal PSMs or PDMs must not be mixed within a single system.
Up to nine PSMs may be connected in parallel to increase available system power across MPCs as needed and provide redundancy. Figure 3 shows the universal PSM.
The HVAC/HVDC power system is feed redundant. Each universal PSM can be connected to two separate feeds from different sources that are used to provide feed redundancy. The PSM has two independent power trains connected in parallel at the output while each input is connected to its own feed. Power always is drawn from both feeds. There are two PDMs per power system capable of carrying nine feeds each. The bottom PDM in each power cage provides power to INP0 of all PSMs installed in the cage, while top PDM in each power cage provides power to INP1 of all PSMs installed in the cage. Feed connection to the PDMs should be done according to standard TIA-942 “Telecommunications Infrastructure Standard for Data” depending on tiering level. The primary input of the PSM is a dual-redundant feed, INP0 and INP1. Both feeds are active during operation, and always carry current. Two dual-position DIP switches accessible from front panel indicate whether respective input INP0 or INP1 is expected to be connected or not. Set the input mode DIP switch to the on or off position to determine the power supply feeds (see Table 2 and Figure 4). In addition, a PSM failure triggers the alarm LED on the craft interface. Each PDM has an LED per feed indicating whether the feed is active or not, or whether the feed is connected properly. See MX2008 High-Voltage Universal (HVAC/HVDC) Power Supply Module Description.
Switch Location Left (Input 0) |
Switch Location Middle (Input 1) |
Input Source |
---|---|---|
Off |
Off |
None are expected to be connected. |
On |
Off |
Only input (0) is expected to be connected. |
Off |
On |
Only input( 1) is expected to be connected. |
On |
On |
Both input 0 and input 1 are expected to be connected. |
The universal HVAC/HVDC PSM has one more (third) DIP input switch accessible from the front panel, see Figure 4. This switch indicates the system is using the universal (MX2K-PDM-HV) PDM that has 30 A rated power cord. This should be in the ON position.
Switch Location Right (Input 2) |
Meaning |
On. See Figure 4. |
PSM is using the universal HVAC/HVDC PDM that has 30 A-rated power cord. |
See Also
MX2008 High-Voltage Universal Power Supply Module LEDs
Each high-voltage second-generation universal (HVAC/HVDC) PSM faceplate contains four LEDs. These LEDs are shown in Figure 5 and Table 4. Nine bicolor LEDs, labeled 0 through 8 for the nine PSMs, are located in the center of the craft interface.
The primary input of the PSM is a dual redundant feed, INP0 and INP1. Both feeds are active during operation, and both feeds share the load current when present. In addition, a PSM failure triggers the alarm LED on the craft interface.
INP0 (V) AC or DC within range |
INP1 (V) AC or DC within range |
Dip 0 |
Dip 1 |
PSM Switch |
INP0 LED |
INP1 LED |
PWR OK LED |
FAULT LED |
PWR OK |
52V out |
5V out |
---|---|---|---|---|---|---|---|---|---|---|---|
Yes |
Yes |
1 |
0 |
Off |
Green |
Off |
Blinking amber |
Off |
Off |
Off |
Off |
Yes |
0 |
1 |
0 |
On |
Green |
Off |
Green |
Off |
On |
On |
On |
0 |
Yes |
0 |
1 |
Off |
Off |
Green |
Blinking amber |
Off |
Off |
Off |
Off |
0 |
Yes |
1 |
1 |
On |
Off |
Green |
Green |
Off |
On |
On |
On |
Yes |
Yes |
1 |
1 |
Off |
Green |
Green |
Blinking amber |
Off |
Off |
Off |
Off |
Yes |
Yes |
1 |
1 |
On |
Green |
Green |
Green |
Off |
On |
On |
On |
Yes |
Yes |
0 |
0 |
Off |
Green |
Green |
Blinking amber |
Off |
Off |
Off |
Off |
Yes |
Yes |
0 |
0 |
On |
Green |
Green |
Green |
Off |
On |
On |
On |
Yes |
0 |
0 |
1 |
Off |
Green |
Off |
Blinking amber |
Red |
Off |
On |
Off |
Yes |
0 |
0 |
1 |
On |
Green |
Off |
Green |
Red |
On |
On |
On |
0 |
Yes |
1 |
0 |
Off |
Off |
Green |
Blinking amber |
Red |
Off |
On |
Off |
0 |
Yes |
1 |
0 |
On |
Off |
Green |
Green |
Red |
On |
On |
On |
See Also
MX2008 High-Voltage Second-Generation Universal Power Requirements
The MX2008, MX2010, and MX2020 routers support the same power modules AC, DC, 240 V China, and universal PSMs and PDMs).
Table 5 lists the FRU power requirements for SFBs, RCBs, MPCs, and MICs. In addition, Table 5 lists the MPC power requirements with MICs and optics at various operating temperatures.
Typical power represents power under certain temperatures and normal operating conditions.
The universal PDMs do not have a switch selection.
If you do not plan to provision as recommended above, you can use the information inTable 5 to calculate the power consumption for your hardware configuration.
Component |
Model Number |
Maximum Power Requirement |
---|---|---|
Switch Fabric Boards (SFBs) | ||
MX2008 SFB2 |
MX2008-SFB2 |
100 W (Typical) 110 W at 55° C 100 W at 40° C 95 W at 25° C |
Fan Trays | ||
Fan Trays |
MX2000-FANTRAY-S |
1500 W (Typical) 1700 W at 55° C 1500 W at 40° C 350 W at 25° C |
Adapter Cards | ||
ADC |
MX2000-LC-ADAPTER |
150 W |
Routing Control Board (RCB) | ||
RCB |
REMX2008-X8-64G |
100 W (Typical) 120 W at 55° C 100 W at 40° C 95 W at 25° C |
MPCs | ||
16x10GE MPC (seeMPC-3D-16XGE-SFPP) |
MPC-3D-16XGE-SFPP |
440 W at 55° C ambient |
MPC1 (see MPC1) |
MX-MPC1-3D MX-MPC1E-3D |
165 W With MICs and optics:239 W at 55° C 227 W at 40° C 219 W at 25° C |
MPC1 Q (see MPC1 Q) |
MX-MPC1-3D-Q MX-MPC1E-3D-Q |
175 W With MICs and optics:249 W at 55° C 237 W at 40° C 228 W at 25° C |
MPC2 (see MPC2) |
MX-MPC2-3D MX-MPC2E-3D |
274 W With MICs and optics:348 W at 55° C 329 W at 40° C 315 W at 25° C |
MPC2 Q (see MPC2 Q) MPC2 EQ (see MPC2 EQ) |
MX-MPC2-3D-Q MX-MPC2-3D-EQ MX-MPC2E-3D-Q MX-MPC2E-3D-EQ |
294 W With MICs and optics:368 W at 55° C 347 W at 40° C 333 W at 25° C |
MCP2E P (see MPC2E P) |
MX-MPC2E-3D-P |
294 W With MICs and optics:368 W at 55° C 347 W at 40° C 333 W at 25° C |
MPC3E (see MPC3E) |
MX-MPC3E-3D |
440 W With MICs and optics:520 W at 55° C, two 40 W MICs 420 W at 40° C, two CFP MICs with LR4 optics 408 W at 25° C, two CFP MICs with LR4 optics |
32x10GE MPC4E (see 32x10GE MPC4E) |
MX-MPC4E-3D-32XGE-SFPP |
610 W With MICs and optics:610 W at 55° C, two 40 W MICs 560 W at 40° C, two CFP MICs with LR4 optics 550 W at 25° C, two CFP MICs with LR4 optics |
2x100GE + 8x10GE MPC4E (see 2x100GE + 8x10GE MPC4E) |
MX-MPC4E-2CGE-8XGE |
610 W With MICs and optics:610 W at 55° C, two 40 W MICs 550 W at 40° C, two CFP MICs with LR4 optics 530 W at 25° C, two CFP MICs with LR4 optics |
MPC5E-40G10G MPC5EQ-40G10G |
With optics:
607 W at 55° C 541 W at 40° C 511 W at 25° C |
|
MPC5E-100G10G MPC5EQ-100G10G |
With optics:
607 W at 55° C 541 W at 40° C 511 W at 25° C |
|
MX2K-MPC6E |
1088 W with MICs and optics |
|
MPC7E-MRATE |
400 W (Typical) 545 W at 55° C 465 W at 40° C 440 W at 25° C |
|
(without MICs) |
MX2K-MPC8E |
688 W (Typical) 805 W at 55° C 720 W at 40° C 690 W at 25° C |
(without MICs) |
MX2K-MPC9E |
838 W (Typical) 1018 W at 55° C 870 W at 40° C 840 W at 25° C |
MICs | ||
ATM MIC with SFP |
MIC-3D-8OC3-2OC12-ATM |
35 W |
Gigabit Ethernet MIC with SFP |
MIC-3D-20-GE-SFP |
37 W |
10-Gigabit Ethernet MIC with XFP |
2-Port: MIC-3D-2XGE-XFP 4-Port: MIC-3D-4XGE-XFP |
2-Port: 29 W 4-Port: 37 W |
10-Gigabit Ethernet MIC with SFP+ |
MIC6-10G |
74 W With optics:53 W at 55° C, 40° C and 25° C with 10G BASE-SR and 10G BASE-LR optics 66 W at 55° C, 40° C and 25° C with 10G BASE-ER optics 74 W at 55° C, 40° C and 25° C with 10G BASE-ZR optics |
10-Gigabit Ethernet DWDM OTN MIC |
MIC6-10G-OTN |
84 W With optics:63 W at 55° C with 10G BASE-LR OTN optics 63 W at 40° C with 10G BASE-LR OTN optics 63 W at 25° C with 10G BASE-LR OTN optics |
40-Gigabit Ethernet MIC with QSFPP |
MIC3-3D-2X40GE-QSFPP |
18 W |
100-Gigabit Ethernet MIC with CFP |
MIC3-3D-1X100GE-CFP |
40 W |
100-Gigabit Ethernet MIC with CXP |
MIC3-3D-1X100GE-CXP |
20 W |
100-Gigabit Ethernet MIC with CFP2 |
MIC6-100G-CFP2 |
104 W With optics:94 W at 55° C with 100G BASE-LR4 OTN optics 86 W at 40° C with 100G BASE-LR4 OTN optics 74 W at 25° C with 100G BASE-LR4 OTN optics |
100-Gigabit Ethernet MIC with CXP |
MIC6-100G-CXP |
57 W 49 W at 55° C with CXP SR10 optics 49 W at 40° C with CXP SR10 optics 49 W at 25° C with CXP SR10 optics |
100-Gigabit DWDM OTN MIC with CFP2 |
MIC3-100G-DWDM |
With optics:
91 W at 55° C 83 W at 25° C |
SONET/SDH OC3/STM1 Multi-Rate MIC |
4-Port: MIC-3D-4OC3OC12-1OC48 8-Port: MIC-3D-8OC3OC12-4OC48 |
4-Port: 24 W at 55° C 22.75 W at 40° C 21.5 W at 25° C 8-Port: 29 W at 55° C 27.75 W at 40° C 26.5 W at 25° C |
OC192/STM64 MIC with XFP |
MIC-3D-1OC192-XFP |
41 W at 55° C 38.5 W at 40° C 36 W at 25° C |
Channelized SONET/SDH OC3/STM1 Multi-Rate MIC |
4-Port: MIC-3D-4CHOC3-2CHOC12 8-Port: MIC-3D-8CHOC3-4CHOC12 |
4-Port: 41 W at 55° C 40 W at 40° C 39 W at 25° C 8-Port: 52 W at 55° C 50.5 W at 40° C 49 W at 25° C |
Channelized OC48/STM16 MIC with SFP |
MIC-3D-1CHOC48 |
56.5 W at 55° C 54.5 W at 40° C 53 W at 25° C |
Tri-Rate MIC |
MIC-3D-40GE-TX |
41 W |
MIC-MRATE |
|
|
DS3/E3 MIC |
MIC-3D-8DS3-E3 MIC-3D-8CHDS3-E3-B |
36 W at 55° C 35 W at 40° C 34 W at 25° C |
Channelized OC3/STM1 (Multi-Rate) Circuit Emulation MIC with SFP |
MIC-3D-4COC3-1COC12-CE |
33.96 W |
See Also
MX2000 High-Voltage Universal PDM (MX2K-PDM-HV) Power Cord Specifications
Table 6 provides specifications and plug standards for the AC (20-input and 16-input) power cord applicable to the universal (HVAC/HVDC) PDMs.
Spare Juniper Model Number |
Locale |
Cord Set Rating |
Connector |
---|---|---|---|
CBL-JNP-SG4-C20 |
North America AC Power Cord |
20 A, 250 VAC |
C20 to Anderson 3-5958p4 |
CBL-JNP-SG4-JPL |
Japan AC power cord |
20 A, 250 VAC |
SAF-D-Grid 400 to NEMAL6-20 |
CBL-JNP-SG4-C20-CH |
Worldwide AC power cord |
16 A, 250 VAC |
SAF-D-GRID 400 to IEC 60320 C20 |
Table 7 provides specifications and connectors on the 30-A power cord provided for each country or region applicable to the universal (HVAC/HVDC) PDMs.
Spare Juniper Model Number |
Locale |
Cord Set Rating |
Connector |
---|---|---|---|
CBL-PWR2-BARE See Figure 6. |
North America HVAC/HVDC power cord |
30 A, 400 VAC |
Anderson/straight to bare wire |
CBL-PWR-SG4 |
North America HVAC/HVDC power cord |
30-A, 400 VAC |
SAF-D-GRID 400 right-angle (LH) |
CBL-PWR2-L6-30P See Figure 7. |
North America AC Power Cord |
30 A, 400 VAC |
Anderson/straight to L6-30P |
CBL-PWR2-332P6W-RA |
Continental Europe AC power cord |
30-A 250 VAC |
Anderson/right-angle to IEC 332P6 |
CBL-PWR2-332P6W |
Continental Europe AC power cord |
30-A 250 VAC |
Anderson/right-angle to IEC 332P6 |
CBL-PWR-SG4-RA |
USA HVAC/HVDC power cord |
30-A, 400 VAC |
SAF-D-GRID 400 right-angle (LH) |
CBL-PWR2-L6-30P-RA |
North America AC power cord |
30 A, 250 VAC |
Anderson/right-angle to L6-30P |
CBL-PWR2-330P6W-RA Figure 8. |
Continental Europe AC power cord |
30 A, 250 VAC |
Anderson/right-angle to IEC 330P6 |
CBL-PWR2-330P6W |
North America AC power cord |
30 A, 250 VAC |
Anderson/right-angle to IEC 330P6 |
For the HVAC/HVDC power cord one end of the cable has an SAF-D-Grid 400 connector, the other end of the cable is bare wire. See Figure 6 and Table 7. These cables are separately orderable and are not shipped automatically with the MX2K-PDM-HV orders. An example of the bare wire cable and connector is shown in Figure 6.
For connection to AC systems, Juniper provides a cable with either a NEMA 30-A connector (Figure 7).
1 — Black wire–Positive (+) | 3 — White wire–Negative |
2 — Green wire-Ground |
The AC power cord for the router is intended for use with the router only and not for any other use.
Translation from Japanese: The attached power cable is only for this product. Do not use the cable for another product.
In North America, AC power cords must not exceed 4.5 m (approximately 14.75 ft) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52, and Canadian Electrical Code (CEC) Section 4-010(3). You can order AC power cords that are in compliance.
The router is installed in restricted access location. It has a separate protective earthing terminal (Metric [–M6] and English [–¼-20] screw ground lugs) provided on the chassis in addition to the grounding pin of the power supply cord. This separate protective earth terminal must be permanently connected to earth.
Power cords and cables must not block access to device components or drape where people could trip on them.
MX2000 Router High-Voltage Universal (HVAC/HVDC) Power Subsystem Electrical Specifications
Table 8 lists the high-voltage second-generation universal power subsystem electrical specifications.
Item |
Specification |
---|---|
Maximum input current rating input voltage @ 190 VDC or 180 VAC |
Maximum input current 30 A (for 3000 W) |
Maximum output power |
3400 W (dual feed) and 3000 W (single feed) @ 57.7 A |
Redundancy |
N+1 PSM N+N feed redundancy |
DC input voltage |
190 VDC to 410 VDC |
DC nominal input current @ 380 VDC IN |
10 A (3000 W for single feed) |
Maximum output @ 52 VDC (upper and lower cage) |
3400 W (dual feed) and 3000 W (single feed) |
DC standby output @ 5 VDC |
30 W |
AC input voltage |
Operating range: 180-305 VAC |
Maximum AC feed PSM input power |
3365 W for single input, 1910 W for each input with dual-input configuration. |
AC input line frequency |
47-63 Hz (+/-3Hz) |
AC system current rating |
19 A (single input) @ 180 VAC input voltage, 11 A for each input with dual-input configuration. |
Efficiency Note:
This value is maximum load. |
91% at full load |
See Also
High-Voltage Universal (HVAC/HVDC) Power Circuit Breaker Requirements for the MX2000 Router
The circuit breaker protection on all the power supplies should be designed according to National Electrical Code (NEC) of country of system installation or any similar local standard based on maximum drawn current of the power supply specified in this document.
Each high-voltage universal (HVAC/HVDC) PSM has dual feeds. The input AC or DC receptacle inlet is located on front panel of the PDM.
Each power cord feed should have dedicated circuit breakers. We recommend that size of the circuit breaker protection should be designed according to National Electrical Code (NEC) of country of system installation or any similar local standard based on maximum drawn current of the power supply specified in this document.
Use a 2-pole Circuit Breaker rated at minimum of 125% of the rated current per NEC or as local codes. Primary Overcurrent Protection by the Building Circuit Breaker. This breaker must protect against excess current, short circuit, and earth grounding fault in accordance with NEC which is ANSI/NFPA 70.