- play_arrow Fast Track: Initial Installation
- play_arrow Site Planning, Preparation, and Specifications
- play_arrow Planning and Preparing the Site
- Overview of Preparing the Site for the MX2010 Router
- MX2010 Cabinet Airflow Requirements
- MX2010 Cabinet Size and Clearance Requirements
- MX2010 Chassis Moving Guidelines
- MX2010 Physical Specifications
- MX2010 Rack Requirements
- MX2010 Router Transport Kit Moving Requirements and Guidelines
- MX2010 Router Environmental Specifications
- MX2000 Router Grounding Specifications
- MX2010 Site Preparation Checklist
- Clearance Requirements for Airflow and Hardware Maintenance for the MX2010 Router
- play_arrow Transceiver and Cable Specifications
- play_arrow Pinout Specifications
- play_arrow AC Power Requirements, Specifications, and Guidelines
- MX2010 AC Power Requirements
- MX2000 AC Power Cord Specifications
- MX2000 AC Power System Electrical Specifications
- MX2000 Router Grounding Specifications
- MX2000 Three-Phase Delta AC Power Distribution Module Electrical Specifications
- MX2000 Three-Phase Wye AC Power Distribution Module Electrical Specifications
- MX2000 Single-Phase AC Power Distribution Module Electrical Specifications
- Calculating AC Power Requirements for MX2010 Routers
- Mapping Input Power from AC Power Distribution Modules to AC Power Supply Modules on MX2000 Routers
- play_arrow DC Power Requirements, Specifications, and Guidelines
- MX2010 DC Power Requirements
- MX2010 DC Power Distribution Description (-48 V)
- MX2010 DC Power Distribution (240 V China) Description
- MX2010 DC Power (-48 V) System Electrical Specifications
- MX2010 Router DC (240 V China) System Electrical Specifications
- Calculating DC Power Requirements for MX2010 Routers
- DC Power (-48 V) Circuit Breaker Requirements for the MX2010 Router
- DC Power (240 V China) Circuit Breaker Requirements for the MX2000 Router
- DC Power Cable Specifications for the MX2010 Router
- play_arrow Universal (HVAC/HVDC) Power Requirements, Specifications, and Guidelines
- MX2010 High-Voltage Universal (HVAC/HVDC) Power Requirements
- MX2000 High-Voltage Universal PDM (MX2K-PDM-HV) Power Cord Specifications
- MX2000 Router High-Voltage Universal (HVAC/HVDC) Power Subsystem Electrical Specifications
- Determining High-Voltage Universal (HVAC/HVDC) Power Requirements for Your MX2010 Router
- High-Voltage Universal (HVAC/HVDC) Power Circuit Breaker Requirements for the MX2000 Router
-
- play_arrow Initial Installation and Configuration
- play_arrow Installation Overview
- Installing an MX2010 Router Overview
- Tools and Parts Required to Unpack the MX2010 Router
- Tools Required to Install the MX2010 Router Using a Pallet Jack
- Tools Required to Install the MX2010 Router Using a Router Transport Kit
- Tools and Parts Required to Maintain the MX2010 Hardware Components
- Tools and Parts Required for Connecting an MX2000 Router to Power
- Tools and Parts Required for MX2010 Router Connections
- play_arrow Unpacking the Router
- play_arrow Installing the Mounting Hardware
- play_arrow Installing the Router
- Removing Components from the MX2010 Router Chassis Before Installing It in a Rack
- Installing an MX2010 Router Using a Pallet Jack Overview
- Installing the Pallet Jack Attachment
- Installing the MX2010 Router Using a Pallet Jack with Attachment
- Installing an MX2010 Router Using a Router Transport Kit Overview
- Installing the Router Transport Kit on the MX2010 Router
- Securing the MX2010 Router to the Router Transport Platform
- Using the Router Transport Kit to Install the MX2010 Router in a Four-Post Rack
- Using the Router Transport Kit to Install the MX2010 Router in an Open-Frame Rack
- Reinstalling Components in the MX2000 Router After Initially Installing the Router in a Rack
- play_arrow Connecting the Router to Power
- Grounding an MX2000 Router
- Connecting AC Power to an MX2000 Router with Three-Phase Delta AC Power Distribution Modules
- Connecting AC Power to an MX2000 Router with Three-Phase Wye AC Power Distribution Modules
- Connecting Power to an MX2000 Single-Phase AC Power Distribution Module
- Mapping Input Power from AC Power Distribution Modules to AC Power Supply Modules on MX2000 Routers
- Connecting Power to a DC-Powered MX2010 Router with Power Distribution Modules (-48 V)
- Connecting Power to a DC-Powered MX2000 Router with DC Power Distribution Modules (240 V China)
- Connecting Power to a High Voltage-Powered MX2000 Router with Power Distribution Modules
- Connecting an MX2000 DC Router Power Distribution Module (-48 V) Cable
- Connecting an MX2000 DC Router Power Distribution Module (240 V China) Cable
- Powering On the DC-Powered MX2010 Router
- Powering On the DC-Powered (240 V China) MX2000 Router
- Powering On the High-Voltage Powered Universal (HVAC/HVDC) MX2000 Router
- Powering On a Three-Phase AC-Powered MX2000 Router
- play_arrow Connecting the Router to the Network
- Connecting the MX2010 Router to Management and Alarm Devices
- Connecting the MX2010 Router to a Network for Out-of-Band Management
- Connecting an MX2000 Router to a Console or Auxiliary Device
- Connecting an MX2010 Router to an External Alarm-Reporting Device
- Connecting the Alarm Relay Wires to the MX2010 Craft Interface
- Disconnecting the Alarm Relay Wires from the MX2010 Craft Interface
- Connecting MPC or MIC Cables to the MX2010 Router
- Register Products—Mandatory to Validate SLAs
- play_arrow Initially Configuring the Router
-
- play_arrow Installing and Replacing Components
- play_arrow Installing Components
- Installing an MX2010 Adapter Card
- Installing the MX2010 Air Filter
- Installing the MX2010 Craft Interface
- Installing the MX2010 Standard DC Cable Manager
- Installing an MX2000 Router DC Power Distribution Module (-48 V)
- Installing an MX2000 Router DC Power Distribution Module (240 V China)
- Installing an MX2000 Router High-Voltage Universal (HVAC/HVDC) Power Distribution Module
- Installing an MX2010 DC Power Supply Module (-48 V)
- Installing MX2000 Router DC Power Supply Modules (240 V China)
- Installing MX2000 Router High-Voltage Universal (HVAC/HVDC) Power Supply Modules
- Installing an MX2010 Dual-Wide MIC
- Installing the MX2010 Standard EMI Cover
- Installing the MX2010 Extended EMI Cover
- Installing an MX2010 Fan Tray
- Installing the MX2010 Air Baffle
- Installing the MX2010 Standard Cable Manager
- Installing the MX2010 Extended Cable Manager
- Installing the MX2010 Extended DC Cable Manager
- Installing an MX2010 MIC
- Installing an MX2000 SFB
- Installing an MX2010 CB-RE
- Installing MX2000 Router AC Power Supply Modules
- Installing MX2000 Router DC Power Supply Modules (-48 V)
- Installing an MX2000 Router Three-Phase Delta AC Power Distribution Module
- Installing an MX2000 Router Three-Phase Wye AC Power Distribution Module
- Installing an MX2000 Single-Phase AC Power Distribution Module
- Installing an SFP or XFP into an MX2000 MPC or MIC
- play_arrow Replacing Components
- Tools and Parts Required for Replacing MX2010 Hardware Components
- Tools and Parts Required to Remove Components from an MX2010 Router
- Removing a CB-RE from an MX2000 Router
- Upgrading to the Control Board-Routing Engine REMX2K-X8-64G in a Redundant Host Subsystem
- Upgrading to the REMX2K-X8-64G CB-RE in a Nonredundant Host Subsystem
- Replacing a Cable on an MX2010 MPC or MIC
- Replacing the MX2010 Air Filters
- Replacing the MX2010 Standard Cable Managers
- Replacing the MX2010 Extended Cable Manager
- Replacing the MX2010 Craft Interface
- Replacing an MX2010 DC Power Supply Module (-48 V)
- Replacing an MX2000 DC Power Supply Module (240 V China)
- Replacing an MX2000 High-Voltage Second-Generation Universal (HVAC/HVDC) Power Supply Module
- Replacing an MX2000 DC Power Distribution Module (-48 V)
- Replacing an MX2000 DC Power Distribution Module (240 V China)
- Replacing an MX2000 High-Voltage Universal (HVAC/HVDC) Power Distribution Module
- Replacing an MX2010 DC Power Distribution Module Cable
- Connecting an MX2000 DC Router Power Distribution Module (240 V China) Cable
- Replacing the MX2010 Standard EMI Cover
- Replacing the MX2010 Extended EMI Cover
- Replacing an MX2010 Fan Tray
- Replacing the MX2010 Air Baffle
- Replacing an MX2010 MIC
- Replacing an MX2010 MPC and Adapter Card
- Replacing an MX2000 SFB
- Replacing an MX2000 CB-RE
- Replacing an SFP or XFP Transceiver on an MX2010 MPC or MIC
- Replacing an MX2000 AC Power Supply Module
- Replacing an MX2010 Three-Phase Delta AC Power Cord
- Replacing an MX2000 Three-Phase Delta AC Power Distribution Module
- Replacing an MX2010 Three-Phase Wye AC Power Cord
- Replacing an MX2020 Three-Phase Wye AC Power Distribution Module
-
- play_arrow Maintaining the Chassis and Components
- play_arrow Maintaining Components
- Maintaining the MX2010 Adapter Cards
- Maintaining Cables That Connect to MX2010 MPCs or MICs
- Maintaining and Verifying the Status of the MX2010 Router Components
- Maintaining the MX2010 Air Filters
- Maintaining the MX2010 Air Vents
- Maintaining the MX2010 Chassis FRU Power-On Sequence
- Maintaining the MX2010 Control Boards
- Maintaining the MX2010 Cooling System Components
- Maintaining the MX2010 Cooling System Zones
- Maintaining the MX2010 Ethernet Switch
- Maintaining the MX2010 Fan Trays
- Maintaining the MX2010 Air Baffle
- Maintaining the MX2010 Host Subsystem
- Maintaining MX2010 MICs
- Maintaining MX2010 MPCs
- Maintaining MX2010 Packet Forwarding Engine Components
- Maintaining the Power Supply Modules on the MX2000 Line of Routers
- Maintaining the MX2010 Power Usage
- Converting an MX2000 Router Between AC and DC Power
- Maintaining the MX2010 Routing Engines
- Maintaining the MX2010 SFB
- Maintaining the MX2010 Switch Processor Mezzanine Board (SPMB)
- Maintaining and Verifying the MX2010 Router Version
- Maintaining and Verifying the Status of the MX2010 Craft Interface
- Taking an MX2000 Host Subsystem Offline
- Holding an MX2010 MPC
- Storing an MX2010 MPC
- Routine Maintenance Procedures for the MX2010 Router
- play_arrow Packing and Returning Components
- play_arrow Powering Off the Router
-
- play_arrow Troubleshooting Hardware
- play_arrow Contacting Customer Support and Returning the Chassis or Components
- play_arrow Contacting Customer Support
- play_arrow Locating Component Serial Numbers
- Displaying MX2010 Router Components and Serial Numbers
- MX2010 CB-RE Serial Number Label
- MX2010 Chassis Serial Number Label
- MX2010 Craft Interface Serial Number Label
- MX2010 Fan Tray Serial Number Label
- MX2010 MIC Serial Number Label
- MX2010 MPC Serial Number Label
- MX2010 Power Distribution Module Serial Number Label
- MX2010 Power Supply Module Serial Number Label
- MX2010 SFB Serial Number Label
- play_arrow Packing and Returning Components
-
- play_arrow Safety and Compliance Information
- play_arrow General Safety Guidelines and Warnings
- play_arrow Installation and Maintenance Safety Guidelines and Warnings
- play_arrow Radiation and Laser Warnings
- play_arrow Maintenance and Operational Safety Guidelines and Warnings
- play_arrow Electrical Safety Guidelines and Warnings
- General Electrical Safety Guidelines and Warnings
- Prevention of Electrostatic Discharge Damage
- AC Power Electrical Safety Guidelines
- AC Power Disconnection Warning
- DC Power Copper Conductors Warning
- DC Power Disconnection Warning
- DC Power Grounding Requirements and Warning
- DC Power Wiring Sequence Warning
- DC Power Wiring Terminations Warning
- Midplane Energy Hazard Warning
- Multiple Power Supplies Disconnection Warning
- Action to Take After an Electrical Accident
- play_arrow Agency Approvals and Compliance Statements
-
MX2010 Component Redundancy
A fully configured router is designed so that no single point of failure can cause the entire system to fail. Only a fully configured router provides complete redundancy. All other configurations provide partial redundancy. The following major hardware components are redundant:
Host subsystem—The host subsystem consists of a combined Control Board and Routing Engine (CB-RE) functioning together. The router can have one or two host subsystems. If two host subsystems are installed, one functions as the primary and the other functions as the backup. If the primary host subsystem (or either of its components) fails, the backup can take over as the primary.
DC power system—The MX2010 DC power system (-48 V and 240 V China) is made up of three components: nine power supply modules (PSMs), two power distribution modules (PDMs), and a power midplane (PMP). For telecom (48 VDC) power supplies the power system distributes power from a pool of 22.5 KW (20 KW for PSM non-redundant and 2.5 KW reserved for PSM redundancy). This pool provides power to ten line-card slots, four fan trays and critical FRUs. These critical FRUs consist of two CB-REs and eight SFBs located in the top portion of the chassis.
DC power feed redundancy—The MX2010 router power system is feed redundant. Each PSM can be connected to two separate feeds from different sources that are used to provide feed redundancy. There are two PDMs per power subsystem that carry nine feeds each. Users should connect feeds from one power source to one PDM and feeds from the other power source to the second PDM of the power subsystem (see Figure 1).
Figure 1: DC Power System Feed RedundancyEach PSM has a set of two DIP switches located on the faceplate. These DIP switches are used to indicate whether a user wants to connect one feed to the power system, two feeds, or none. These DIP switches provide critical information to the power management system to help generate alarms in case of a feed failure or a wrong connection. Each PDM has an LED per feed indicating whether the feed is active or not, or whether the feed is connected properly. See MX2010 DC Power Supply Module (-48 V) Description.
High-Voltage Second-Generation Universal (HVAC/HVDC) PDMs—The universal PDM accepts either an HVAC or HVDC input. You can install a total of two PDMs into a router. Each universal PDM operates with nine feeds of a 30-A current limit. Each universal PSM is capable of delivering 3400 W of power with-dual feeds and 3000 W of power with a single-feed. In this configuration, each subsystem provides N+1 output PSM redundancy along with N+N feed redundancy. The power feeds from different sources need to be connected to different PDMs. If feeds that connect to one PDM fail in a redundant configuration, the other feed provides full power. For the high-voltage second-generation universal (HVAC/HVDC) power system, both input power feeds are active, and share the load when they are present.
Figure 2 illustrates the power distribution from the universal (HVAC/HVDC) PDMs to the universal (HVAC/HVDC) PSMs.
Figure 2: MX2010 Router Universal (HVAC/HVDC) Power Subsystem Feed RedundancyAC power system—The MX2010 supports connection of a three-phase AC power system. There are two types of three-phase power systems: the three-phase delta and three-phase wye. The AC power going to the PSMs is split into three individual phases—each PSM works on a single phase. This means the power system works independent of the kind of AC feed is connected. The user can connect one or two feeds, depending on the power system configuration (number of PSMs, redundancy, and so on). Each phase from each of the two feeds is distributed among one or two PSMs (one feed has each phase going to two PSMs, and the other feed has each phase going to a single PSM). See Figure 3 and Figure 4.
Figure 3: Power Distribution from Three-Phase Feed Delta PDM to the AC PSMsFigure 4: Power Distribution from Three-Phase Feed Wye PDM to the AC PSMsThe AC power system is feed redundant—each PSM takes in two AC feeds and uses one of the two. One AC feed is active at a time. If one feed fails, the PSM automatically switches over to the other feed without disrupting system function (see MX2000 Three-Phase Delta AC Power Distribution Module Description, MX2000 Three-Phase Wye AC Power Distribution Module Description, and MX2000 AC Power Supply Module Description).
AC power requirements—Table 1 shows the MX2010 current requirements for the three-phase delta and wye power feeds.
Table 1: AC PDM Delta and Wye Current Requirements Three-Phase Voltage
Input Feed
Current Delta per Three-Phase PDM
Current Wye per Three-Phase PDM
200 V (minimum–nominal) (line-to-line) for delta (per phase)
1
50 A
–
2
25 A
–
200 V (minimum–nominal) (line-to-neutral) for wye (per phase)
1
–
30 A
2
–
15 A
Note:This is the minimum required to provide 2.5 KW per PSM. Based on facilities guidelines, you should over-provision the MX2010 router. The two numbers listed in the current columns reflect the distribution of phases from the feed to PSM. For example, from one feed each phase goes to two PSMs and from other feed each phase goes to only one PSM.
Power distribution modules (PDMs)—In the DC configuration, each system provides N+1 PSM redundancy along with N+N feed redundancy. The power feeds from different sources need to be connected to different PDMs. If feeds that connect to one PDM fail in a redundant configuration, the other feed starts to provide full power.
Note:Depending on the voltage of the DC feeds (-48 VDC or 240 V China,) power can be drawn from both feeds. The feed with higher voltage provides more power. If the difference between the voltages is sufficient, then the higher voltage feed provides all the power. When the voltages are exactly the same, equal power is drawn from both feeds. For high-voltage second-generation universal (HVAC/HVDC) power system, both input power feeds are active, and share the load when they are present.
A total of two PDMs can be installed into a router. Each DC PDM (-48 V) operates with up to nine separate feeds of either 60-A or 80-A current limit. The capacity of these feeds is relayed to system software through a switch located on the DC PDM. Each DC PDM (240 V China) or DC PDM (-48 V)—operates with nine feeds each. The MX2010 router supports two types of three-phase power system PDMs. The three-phase delta and three-phase wye. Individual phases are taken from three-phase feeds to individual PSMs. One AC feed provides power to six PSMs, while the second input feed provides power to the remaining three PSMs (supporting a total of nine PSMs).
Power supply modules (PSMs)—All nine AC, DC, 240 V China, or universal HVAC/HVDC PSMs in a system share the load. For the high-voltage second-generation universal (HVAC/HVDC) power system, both input power feeds are active, and share the load when they are present. If one PSM fails in a redundant configuration, the remaining eight PSMs provide power to FRUs. Up to nine PSMs might be required to supply power to a fully configured router. Nine PSMs supply power to the two CB-REs (active and redundant), eight SFBs, ten MPCs, and four fan trays (active and redundant).
Cooling system—The cooling system has a total of four fan trays— two per cooling zone (cooling zone 0 and cooling zone 1)—which are controlled and monitored by the host subsystem. Each cooling zone consists of two fan trays. The bottom fan trays are used to cool the bottom half of the CB-REs and SFBs, along with the ten line cards. The top fan trays are used to cool the top half of the CB-REs and SFBs. If a fan fails or the temperature rises above the temperature threshold, the speed of the remaining fans in the zone is automatically adjusted to keep the temperature within the acceptable range (see MX2010 Cooling System Description).