- play_arrow Fast Track: Initial Installation
- play_arrow Overview
- play_arrow System Overview
- play_arrow Chassis Components and Descriptions
- MX960 Chassis Description
- MX960 Component Redundancy
- MX960 Router Hardware and CLI Terminology Mapping
- MX960 Midplane Description
- MX960 Rack-Mounting Hardware
- MX960 Craft Interface Overview
- MX960 Alarm Relay Contacts on the Craft Interface
- MX960 Alarm LEDs and Alarm Cutoff/Lamp Test Button
- MX960 Component LEDs on the Craft Interface
- MX960 Cable Manager Description
- play_arrow Cooling System Components and Descriptions
- play_arrow Host Subsystem Components and Descriptions
- play_arrow Interface Modules—DPCs
- play_arrow Interface Modules—FPCs and PICs
- play_arrow Interface Modules—MPCs and MICs
- MX960 Application Services Modular Line Card Description
- MX960 Application Services Modular Storage Card Description
- MX960 Application Services Modular Processing Card Description
- MX960 AS MSC LEDs
- MX960 AS MXC LEDs
- MIC/MPC Compatibility
- MX960 Modular Interface Card Description
- MX960 Modular Interface Card (MIC) LEDs
- MICs Supported by MX Series Routers
- MX960 MIC Port and Interface Numbering
- MX960 Modular Port Concentrator Description
- MX960 Modular Port Concentrator LEDs
- MPCs Supported by MX Series Routers
- play_arrow Services Processing Card—MX-SPC3
- play_arrow Power System Components and Descriptions
- play_arrow Switch Control Board Components and Descriptions
-
- play_arrow Initial Installation and Configuration
- play_arrow Unpacking the MX960 Router
- play_arrow Installing the Mounting Hardware
- play_arrow Installing the MX960 Router
- Installing an MX960 Router Overview
- Removing Components from the MX960 Router Chassis Before Installing It with a Lift
- Tools Required to Install the MX960 Router with a Mechanical Lift
- Installing the MX960 Router Using a Mechanical Lift
- MX960 Acoustic Cover Installation Instructions
- MX960 Extended Cable Manager Installation Instructions
- Reinstalling Components in the MX960 Chassis After Installing It with a Lift
- play_arrow Connecting the MX960 Router to Power
- Tools and Parts Required for MX960 Router Grounding and Power Connections
- Grounding the MX960 Router
- Connecting Power to an AC-Powered MX960 Router with Normal-Capacity Power Supplies
- Connecting Power to an AC-Powered MX960 Router with High-Capacity Power Supplies
- Connecting Power to an AC-Powered MX960 Router with High-Capacity Second-Generation Power Supplies
- Powering On an AC-Powered MX960 Router with Normal Capacity Power Supplies
- Connecting Power to a DC-Powered MX960 Router with Normal-Capacity Power Supplies
- Connecting Power to a DC-Powered MX960 Router with High-Capacity Power Supplies
- Powering On a DC-Powered MX960 Router with Normal Capacity Power Supplies
- Connecting Power to an MX960 Router with High-Voltage Second-Generation Universal (HVAC or HVDC) Power Supplies
- Powering Off the MX960 Router
- Connecting an MX960 AC Power Supply Cord
- Connecting an MX960 DC Power Supply Cable
- play_arrow Connecting the MX960 Router to the Network
- Tools and Parts Required for MX960 Router Connections
- Connecting the MX960 Router to Management and Alarm Devices
- Connecting the MX960 Router to a Network for Out-of-Band Management
- Connecting the MX960 Router to a Management Console or Auxiliary Device
- Connecting an MX960 Router to an External Alarm-Reporting Device
- Connecting DPC, MPC, MIC, or PIC Cables to the MX960 Router
- Connecting the Alarm Relay Wires to the MX960 Craft Interface
- play_arrow Initially Configuring the MX960 Router
-
- play_arrow Installing and Replacing Components
- play_arrow Overview of Installing and Replacing Components
- play_arrow Installing Components
- Installing the MX960 Craft Interface
- Installing the MX960 Air Filter
- Installing an MX960 Fan Tray
- Installing an MX960 Routing Engine
- Installing an MX960 Switch Control Board
- Installing an MX960 DPC
- Installing an MX960 FPC
- Installing an MX960 MIC
- Installing an MX960 Dual-Wide MIC
- Installing an MX960 MPC
- Installing an MX960 PIC
- Installing a Cable on an MX960 DPC, MPC, MIC, or PIC
- Installing a MX960 AC Power Supply or High-Voltage Second-Generation Universal (HVAC or HVDC)
- Installing an MX960 DC Power Supply
- Installing an MX960 AS MLC
- Installing an MX960 AS MSC
- Installing an MX960 AS MXC
- Installing an SFP or XFP Transceiver into an MX960 DPC, MPC, MIC, or PIC
- Replacing a CFP2 Transceiver
- Replacing a CFP Transceiver
- play_arrow Replacing Chassis Components
- play_arrow Replacing Cooling System Component
- play_arrow Replacing Host Subsystem Components
- Replacing an MX960 Routing Engine
- Replacing an SSD Drive on an RE-S-1800
- Replacing an SSD Drive on an RE-S-X6-64G
- Replacing Connections to MX960 Routing Engine Interface Ports
- Upgrading to the RE-S-X6-64G Routing Engine in a Redundant Host Subsystem
- Upgrading to the RE-S-X6-64G Routing Engine in a Nonredundant Host Subsystem
- play_arrow Replacing Line Card Components
- play_arrow Replacing Power System Components
- play_arrow Replacing and Upgrading Switch Control Boards
-
- play_arrow Maintaining the Chassis and Components
- play_arrow Routine Maintenance Procedures
- play_arrow Maintaining Components
- Tools and Parts Required to Maintain the MX960 Router
- Maintaining the MX960 Air Filter
- Maintaining the MX960 Fan Trays
- Maintaining the MX960 Host Subsystem
- Maintaining MX960 DPCs
- Holding an MX960 DPC
- Storing an MX960 DPC
- Maintaining MX960 FPCs
- Holding an MX960 FPC
- Storing an MX960 FPC
- Maintaining MX960 MICs
- Maintaining MX960 MPCs
- Maintaining MX960 PICs
- Maintaining Cables That Connect to MX960 DPCs, MPCs, MICs, or PICs
- Maintaining MX-SPC3 Services Card
- Maintaining the MX960 Power Supplies
- Verifying the Version of the MX960 Cable Manager
- play_arrow Converting to a Different Type of Power Supply
-
- play_arrow Troubleshooting Hardware
- play_arrow Knowledge Base
- play_arrow Troubleshooting Components
-
- play_arrow Contacting Customer Support and Returning the Chassis or Components
- play_arrow Contacting Customer Support
- play_arrow Locating Component Serial Numbers
- Displaying MX960 Router Components and Serial Numbers
- MX960 Routing Engine Serial Number Label
- MX960 Chassis Serial Number and Agency Label
- MX960 Craft Interface Serial Number Label
- MX960 Fan Tray Serial Number Label
- MX960 Power Supply Serial Number Labels
- MX960 MIC Serial Number Label
- MX960 MPC Serial Number Label
- MX960 PIC Serial Number Label
- MX960 FPC Serial Number Label
- MX960 DPC Serial Number Label
- MX960 SCB Serial Number Label
- MX960 Midplane Serial Number Label
- Contact Customer Support
- play_arrow Packing and Returning Components
-
- play_arrow Safety and Compliance Information
- play_arrow General Safety Guidelines and Warnings
- play_arrow Installation and Maintenance Safety Guidelines and Warnings
- play_arrow Radiation and Laser Warnings
- play_arrow Maintenance and Operational Safety Guidelines and Warnings
- play_arrow Electrical Safety Guidelines and Warnings
- General Electrical Safety Guidelines and Warnings
- Prevention of Electrostatic Discharge Damage
- AC Power Electrical Safety Guidelines
- AC Power Disconnection Warning
- DC Power Copper Conductors Warning
- DC Power Disconnection Warning
- DC Power Grounding Requirements and Warning
- DC Power Wiring Sequence Warning
- DC Power Wiring Terminations Warning
- Midplane Energy Hazard Warning
- Multiple Power Supplies Disconnection Warning
- Action to Take After an Electrical Accident
- play_arrow Agency Approvals and Compliance Statements
- Agency Approvals for MX960 Routers
- Compliance Statements for NEBS for the MX960 Router
- Compliance Statements for EMC Requirements for the MX960 Router
- Compliance Statements for Environmental Requirements
- Compliance Statements for Acoustic Noise for the MX960 Router
- Statements of Volatility for Juniper Network Devices
-
Calculating Power Requirements for MX960 Routers
The information in this topic helps you determine which power supplies are suitable for various configurations, as well as which power supplies are not suitable because output power is exceeded. You determine suitability by subtracting the total power draw from the maximum output of the power supplies. Afterward, the required input current is calculated. Finally, you calculate the thermal output. A sample configuration is provided in Table 1.
We recommend that you provision power according to the maximum input current listed in the power supply electrical specifications (see Electrical Specifications for the MX960 AC Power Supply and Electrical Specifications for the MX960 DC Power Supply).
Use the following procedures to calculate the power requirement:
Calculate the power requirement.
Evaluate the power budget.
Calculate input power.
Calculate thermal output (BTUs) for cooling requirements.
Both normal-capacity and high-capacity MX960 chassis with DC power supplies; MX960 chassis with high-capacity AC power supplies; MX960 high-capacity second-generation AC power supplies; and MX960 high-voltage second-generation universal power supplies are zoned. MX960 chassis with normal-capacity AC power supplies have one overall zone. Zoning means that certain components are powered by specific power supplies (see Table 1 for information on zoning). When calculating power requirements, be sure that there is adequate power for each zone.
Three AC power supplies are mandatory for MX960 chassis with normal-capacity AC power supplies.
Chassis Power Configuration | Zone | Power Supply (PEM) | Components Receiving Power |
---|---|---|---|
MX960 DC (normal-capacity and high-capacity power supplies); MX960 AC (normal and high-capacity power supplies; MX960 AC high-capacity second-generation power supplies; and MX960 high-voltage second-generation universal (HVAC/HVDC) power supplies | Zone 0 | PEM 0 or 2 |
|
MX960 DC (normal-capacity and high-capacity power supplies); MX960 AC (normal and high-capacity power supplies); MX960 AC high-capacity second-generation power supplies; and MX960 high-voltage second-generation universal (HVAC/HVDC) power supplies | Zone 1 | PEM 1 or 3 |
|
The following sample configuration shows an MX960 chassis with:
Four high-capacity AC power supplies (using two feeds for each power supply); two supplies are active, two are redundant
Six 16 port 10 GbE MPC with SFP+ interfaces (slots 0 through 5)
Two SCBs with two (redundant) RE-1800x2 routing engines (SCB slot 0 and SCB slot 1)
SCB (SCB slot 6)
Five 16 port 10 GbE MPC with SFP+ interfaces (slots 7 through 11)
High-capacity cooling system (upper and lower fan trays)
Note:The high-capacity cooling system satisfies cooling requirements of MPCs, and must be used for proper cooling.
Calculate the power requirements (usage) using the values in Power Requirements for an MX960 Router as shown in Table 2.
Table 2: Sample Power Requirements for an MX960 Router Chassis Component
Part Number
Power Requirement
Zone
Base system
MX960BASE-AC-HIGH
50 W1
—
High-capacity cooling system
FANTRAY-MX960-HC
320 W * 2 = 640 W
Zone 0 (lower fan tray) and Zone 1 (upper fan tray)
MPC - slots 0 through 5
MPC-3D-16XGE-SFPP
440 W * 6 = 2640 W
Zone 1
MPC - slots 7 through 11
MPC-3D-16XGE-SFPP
440 W * 5 = 2200 W
Zone 0
SCB 0
SCBE2-MX with
RE-S-1800X2-8G
185 W
90 W
Zone 1
SCB 1
SCBE2-MX with
RE-S-1800X2-8G
185 W
90 W
Zone 0
SCB 2 - slot 6
SCBE2-MX
185 W
Zone 0
MX960 normal-capacity AC (not zoned)
Zone 0 total output power
Zone 1 total output power
6265 W
3005 W
3260 W
1 Divided equally between zone 0 and zone 1.
Evaluate the power budget, including the budget for each zone if applicable. In this step, we check the required power against the maximum output power of available power supply options.
Table 3 lists the power supplies, their maximum output power, and unused power (or a power deficit).
Note:The following power consumption figures are representational and may have round-off errors. Refer the Power Calculator tool for exact power requirements.
Table 3: Calculating Power Budget Power Supply
Maximum Output Power of Power Supply
Maximum Output Power for System
Nonzoned Unused Power
Zone 0 Unused Power1
Zone 1 Unused Power2
MX960 AC normal-capacity
1700 W
5100 W
Power exceeded (non-zoned; 5100 W - 6160 = power exceeded)
–
–
MX960 AC high-capacity
1700 W (one feed)
3400 W (one feed)
–
Power exceeded
Power exceeded
4100 W (two feeds)
8200 W (two feeds)
1165 W
875 W
MX960 DC normal-capacity
2800 W
5600 W
–
Power exceeded
Power exceeded
MX960 AC high-capacity second-generation
2300 W (one feed)
4230 W (one feed)
Power exceeded
Power exceeded
5100 W (two feeds)
10200 W (two feeds)
2165 W
1875 W
MX960 high-voltage second-generation (HVAC or HVDC)
5100 W
10200 W
Power exceeded
MX960 DC high-capacity
1700 W (one feed)
3400 W (one feed)
–
Power exceeded
Power exceeded
4100 W (two feeds)
8200 W (two feeds)
1165 W
875 W
1 For this configuration, output power is 2935 W.
2 For this configuration, output power is 3225 W.
Calculate input power. In this step, the input power requirements for the example configuration are calculated. To do this, divide the total output requirement by the efficiency of the power supply as shown in Table 4.
Note:MX960 AC and MX960 DC normal-capacity power supplies are not included in the following table, because their power budget was exceeded in the sample configuration.
Table 4: Calculating Input Power Power Supply
Power Supply Efficiency1
Input Power Requirement2
MX960 AC high-capacity
~88 %
3335 W3
MX960 DC high-capacity
86 %
3413 W3
MX960 AC high-capacity second-generation
91 %
3225 W
MX960 (HVAC or HVDC) high-voltage second-generation universal
91 %
3225 W
1 These values are at full load and nominal voltage.
2 For this configuration, total power for zone 0 is 2935 W. The calculation method for zone 1 is the same as zone 0.
3 Zone 0 requirement.
Calculate thermal output (BTUs). To calculate this, multiply the input power requirement (in watts) by 3.41 as shown in Table 5.
Table 5: Calculating Thermal Output Power Supply
Thermal Output (BTUs per hour)
MX960 AC high-capacity
3335 * 3.41 = 11,372 BTU/hr1
MX960 DC high-capacity
3413 * 3.41 = 11,638 BTU/hr1
MX960 AC high-capacity second-generation
3225 * 3.41 = 10997 BTU/hr1
MX960 (HVAC or HVDC) high-voltage second-generation universal
3225 * 3.41 = 10997 BTU/hr1
1 Zone 0 output. The calculation method for zone 1 is the same as for zone 0.